It works for me if I explicitly set bus 2 to be type REF. MATPOWER does not 
automatically detect islands and convert the first PV bus to REF.

-- 
Ray Zimmerman
Senior Research Associate
419A Warren Hall, Cornell University, Ithaca, NY 14853
phone: (607) 255-9645




On Apr 17, 2013, at 12:46 PM, Tao HUANG <[email protected]> wrote:

> I quickly tried on a very simple 3 buses system (pls check the attached 
> figure) modified based on the t_case9_dcline system to test the islands.
> Firstly I set the status of line 1-2 equal to 1, then both PF and OPF works 
> fine. In this case, with the replacement of dummy generators for the DC 
> lines, the whole system is still connected.
> Then, I set the status of line 1-2 equal to 0, then both PF and OPF do not 
> converge. In this case, by using the dummy generators to model the DC line, 
> the network was split into to 2 islands. By the way, I put a generator at bus 
> 2 so each island should have a reference bus (suppose Matpower would use the 
> first PV bus as the reference bus)
> Dr. TAO HUANG
> Senior Assistant Researcher
> SESAME –Executive vice coordinator
> Politecnico di Torino
> Dipartimento Energia
> Corso Duca degli Abruzzi, 24
> 10129 Torino – Italy
> tel. +39 011 090 7117
> fax +39 011 090 7199
> e-mail  [email protected]
>  
>  
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Ray Zimmerman
> Sent: Wednesday, April 17, 2013 5:52 PM
> To: MATPOWER discussion forum
> Subject: Re: Modelling transformer and phase shifter
>  
> But as long as the dummy generators are dispatchable and appropriately 
> coupled I don't see why you wouldn't get an optimal solution for the whole 
> system (as with our DC line implementation described in Section 6.5.3 of the 
> User's Manual.
>  
>  
> -- 
> Ray Zimmerman
> Senior Research Associate
> 419A Warren Hall, Cornell University, Ithaca, NY 14853
> phone: (607) 255-9645
> 
> 
> 
> 
>  
> On Apr 17, 2013, at 10:35 AM, Tao HUANG <[email protected]> wrote:
> 
> 
> For power flow maybe yes (neglecting the angle differences and overall system 
> losses), but for OPF, the optimal result for each island may not be the 
> optimal solution for the whole system, as the islands are formed purely due 
> to the replacement of a transformer (or a DC line) by two dummy generators.
>  
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Ray Zimmerman
> Sent: Wednesday, April 17, 2013 4:30 PM
> To: MATPOWER discussion forum
> Subject: Re: Modelling transformer and phase shifter
>  
> As long as each island has a voltage angle reference I don't think the 
> islands should present a problem.
>  
> -- 
> Ray Zimmerman
> Senior Research Associate
> 419A Warren Hall, Cornell University, Ithaca, NY 14853
> phone: (607) 255-9645
> 
> 
> 
> 
> 
> 
>  
> On Apr 17, 2013, at 5:05 AM, Tao HUANG <[email protected]> wrote:
> 
> 
> 
> Dear Ray and Kartik,
>  
> Thanks for your reply. I guess the easiest way to utilize the current version 
> of matpower is to use dummy generators as Ray indicated. But what I concerned 
> of using this method is the problem of split the network into many islands 
> when replacing the transformer/phase shifter with 2 generators. If this 
> happens, we cannot get the OPF/PF results.
>  
> I would also skip using heuristic algorithms as I think they cannot give a 
> “stable” and “coherent” solution.
>  
> Thanks again for your suggestions.
>  
> Tao
>  
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Kartik Pandya
> Sent: Wednesday, April 17, 2013 6:35 AM
> To: MATPOWER discussion forum
> Subject: Re: Modelling transformer and phase shifter
>  
> You may use AI method like PSO to consider TAPS as control variables. 
> please refer "Optimal reactive power dispatch using Particle swarm 
> optimization" file at matlab file exchange for more details.
> in that file i had optimized TAPS of transformers connected in line no. 
> 11,12,15, and 36 for IEEE 30 bus test system.
>  
> From: Ray Zimmerman <[email protected]>
> To: MATPOWER discussion forum <[email protected]> 
> Sent: Wednesday, 17 April 2013 12:49 AM
> Subject: Re: Modelling transformer and phase shifter
>  
> 
> It is correct that in the current MATPOWER OPF, the TAP and SHIFT parameters 
> are fixed input parameters, not variables. I don't think there is a way to 
> fake it with the AC OPF. That is, I think you really need to include them as 
> variables in the flow equations and corresponding derivatives. There may be a 
> way to fake it with dummy injections in the DC OPF, but I haven't really 
> thought about it carefully.
>  
> Please let us know if you come up with something that works. And of course, 
> others can feel free to suggest ideas.
>  
> -- 
> Ray Zimmerman
> Senior Research Associate
> 419A Warren Hall, Cornell University, Ithaca, NY 14853
> phone: (607) 255-9645
>  
> 
>  
> 
>  
> On Apr 16, 2013, at 9:04 AM, Tao HUANG <[email protected]> wrote:
>  
> 
> Dear Dr. Ray,
>  
> Speaking of the modeling transformer and phase shifter, I would like to see 
> if the adjustment of the two parameters (tap ratios and shift angles) along 
> with the generators and loads could get better results of OPF in terms of 
> cost and convergence (due to the line limits in some cases). do you have any 
> suggestions as to how to make the tap ratios and shift angles as variables in 
> the OPF without using iterative calculation (like blindly or using some 
> heuristic algorithms to modify them and redo the OPF)? If I understand it 
> correctly, these two values are fixed before the PF & OPF calculation in 
> terms of Y matrix at present in Matpower.
>  
> I was considering to model the transformer/ phase shifter as two generators 
> in respect to the flow limits, but it may split the network into two islands 
> in some cases. So, do you have any suggestion on this as well? I guess it 
> also applies to the DC line when it is the only connection between two parts 
> of the network.
>  
> Thanks a lot
>  
> Best wishes,
>  
> Tao
>  
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Ray Zimmerman
> Sent: Tuesday, April 16, 2013 2:31 PM
> To: MATPOWER discussion forum
> Subject: Re: Modelling transformer and phase shifter
>  
> Yes, for a transformer you will typically have an off-nominal taps ratio, 
> i.e. branch(b, TAP) ~= 1 (or 0, which signifies a normal transmission line). 
> Similarly, if you have a phase shift, you will have branch(b, SHIFT) ~= 0.
>  
> How the transformer TAP and SHIFT parameters affect the amount of load able 
> to be dispatched depends on the network, so it could go either way.
>  
> -- 
> Ray Zimmerman
> Senior Research Associate
> 419A Warren Hall, Cornell University, Ithaca, NY 14853
> phone: (607) 255-9645
>  
> 
>  
> 
>  
> On Apr 16, 2013, at 8:18 AM, Jiashen Teh <[email protected]> 
> wrote:
>  
> 
> Dear Dr Ray,
> 
> According to your manual , in section '3.2 Branches'
> it is mentioned that:
>  
> 'All transmission lines, transformers and phase shifters are modeled with a 
> common branch model......'
> 
> Does this mean, if I want to include modelling of transformer at a branch, I 
> would set the column 9 and 10 of mpc.branch which govern the transformer turn 
> ratio, N ?
> 
> I notice that for values other than zero for both columns (in a manner to 
> increase N or reduce N), the network (6 bus) will encounter increase of load 
> not able to be dispatched. Isn't is load dispatch-able should increase?
>                 
> Yours sincerely,
> 
> Jiashen Teh
>  
>  
>  
> 
>  
>  
> <t_case3_dcline.m><DCline.png>