I’m afraid I do not know exactly what characteristic of your system results in 
this issue for larger loads. Attempting with a different solver is certainly 
worth a try. It is possible that the problem becomes infeasible (e.g. due to 
voltage and reactive power limits being exceeded) when the load increases.


-- 
Ray Zimmerman
Senior Research Associate
B30 Warren Hall, Cornell University, Ithaca, NY 14853
phone: (607) 255-9645



On Dec 1, 2013, at 3:08 PM, Spyridon Gian <[email protected]> wrote:

> 
> I have created a 10 bus radial network, with line resistance = 0.06 pu, and 
> Line reactance = 0.02 pu , for each line. 
> The load is 13.6 kW , for each of 6 buses. The remaining 4 buses have no 
> load. 
> There is only 1 generator and is connected to bus 1. 
> I run the OPF, and the result is the following: 
> 
> MATPOWER Version 4.1, 14-Dec-2011 -- AC Optimal Power Flow
> MATLAB Interior Point Solver -- MIPS, Version 1.0, 07-Feb-2011Warning: Matrix 
> is close to singular or badly scaled. Results may be inaccurate. RCOND =  
> 9.951817e-19. 
> > In mips at 422
>   In mipsopf_solver at 145
>   In opf_execute at 106
>   In opf at 225
>   In runopf at 96 
> 
> Numerically Failed
> 
> Did not converge in 7 iterations.
> 
> Did not converge (0.10 seconds)
> 
> The interesting thing is that the OPF converges at the exact same network, 
> after one and only one change: 
> If the load becomes less than 13.5 kW ! Eg. If I run the OPF using a load of 
> 2.9kW , it converges! 
> 
> 1. Can you give me an explanation of the reason why this occurs?  
> 2. Is there a way to avoid it ? Eg by choosing another solver perhaps?
> 
> Thank you

Reply via email to