I also suspect it is a reactive power or voltage problem. Is there a voltage 
limit binding at the buses where energy is not supplied (I assume you are using 
dispatchable loads)? If so, you might get some insight from doing some 
perturbation analysis. Simply change that voltage limit by a very small amount 
and see how the dispatch changes. My guess is that the only way to maintain the 
voltage is by using the expensive distributed generators. Shifting generation 
to the grid infeed would likely result in more load shedding to keep voltages 
in line. Presumably load shedding is even more costly than the distributed 
generation?

-- 
Ray Zimmerman
Senior Research Associate
B30 Warren Hall, Cornell University, Ithaca, NY 14853
phone: (607) 255-9645



On Feb 11, 2014, at 5:48 AM, angelina sirri <[email protected]> wrote:

> Dear Dr Zimmerman,
> I am using an 11kV distribution system, which is consisted of two radial 
> circuits connected by a normally open point. The network has one grid infeed 
> (Vg=1) whereas all the other nodes where occupied only by loads (with Vm<1). 
> Now I increase the loading of the circuits and  have added distributed 
> generators in all the load buses, which will only operate in case there is a 
> line fault in the system(otherwise there is no need for them to operate 
> because the grid infeed can give really high power, comparing to the load and 
> the lines rating is also really big) .  For the voltage problems, I have 
> added reactive power in each node.
>  The thing that confuses me is , that when there is a line fault (the worst 
> case scenario line loss), there is always energy not supplied , although a 
> path  from the main supply exists and also the rating of the lines allows 
> that power to pass through the line. This happens mainly for the most distant 
> nodes. In that case, all the available distributed generators generate at 
> their Pmax , but the grid infeed value is really small.
>   Why the opf  prefers to use the really expensive generators of the distant 
> nodes (used for the energy not supplied) instead of absorbing that power from 
> the free of cost grid infeed? I can guess that is a reactive problem or a 
> voltage problem but I cannot find a suitable solution. 
> Any help would be of high importance,
> King Regards,
> Angelina