If you are running an OPF, and it is converging successfully, then the initial 
values of mpc.gen(:, VG) or mpc.bus(:, VM) are not critical. The important 
thing is which constraints are binding at the solution. Are there binding 
reactive power limits?

-- 
Ray Zimmerman
Senior Research Associate
B30 Warren Hall, Cornell University, Ithaca, NY 14853
phone: (607) 255-9645



On Feb 11, 2014, at 11:38 AM, angelina sirri <[email protected]> wrote:

> Yes, I am using dispatchable loads and as far as the costs, grid infeed is of 
> free cost, distributed generation is more expensive and the energy not 
> supplied generators are of the highest cost. When there is energy not 
> supplied the voltage in that nodes reaches the maximum upper limit (1.06) . 
> When I change the voltage limit, the dispatch is again the same and the 
> problematic nodes reach the new maximum upper limit. I think that the problem 
> is the initial voltage of the gens in mpc.gen(:,6). What values should I put? 
> The system originally had only load buses( with voltage less than 1 ). Now 
> that I have transformed those buses to gen buses I should predetermined the 
> voltages of the gens. I tried to put the same voltage as the mpc.bus (:, 8). 
> But these values seem to be not so accurate in the end. How should I evaluate 
> what values to put in the mpc.gen(:,6)?
> 
> From: [email protected]
> Subject: Re: reluctant energy not supplied in a distribution system with opf
> Date: Tue, 11 Feb 2014 11:14:31 -0500
> To: [email protected]
> 
> I also suspect it is a reactive power or voltage problem. Is there a voltage 
> limit binding at the buses where energy is not supplied (I assume you are 
> using dispatchable loads)? If so, you might get some insight from doing some 
> perturbation analysis. Simply change that voltage limit by a very small 
> amount and see how the dispatch changes. My guess is that the only way to 
> maintain the voltage is by using the expensive distributed generators. 
> Shifting generation to the grid infeed would likely result in more load 
> shedding to keep voltages in line. Presumably load shedding is even more 
> costly than the distributed generation?
> Kind Regards,
> Angelina
> 
> -- 
> Ray Zimmerman
> Senior Research Associate
> B30 Warren Hall, Cornell University, Ithaca, NY 14853
> phone: (607) 255-9645
> 
> 
> 
> On Feb 11, 2014, at 5:48 AM, angelina sirri <[email protected]> wrote:
> 
> Dear Dr Zimmerman,
> I am using an 11kV distribution system, which is consisted of two radial 
> circuits connected by a normally open point. The network has one grid infeed 
> (Vg=1) whereas all the other nodes where occupied only by loads (with Vm<1). 
> Now I increase the loading of the circuits and  have added distributed 
> generators in all the load buses, which will only operate in case there is a 
> line fault in the system(otherwise there is no need for them to operate 
> because the grid infeed can give really high power, comparing to the load and 
> the lines rating is also really big) .  For the voltage problems, I have 
> added reactive power in each node.
>  The thing that confuses me is , that when there is a line fault (the worst 
> case scenario line loss), there is always energy not supplied , although a 
> path  from the main supply exists and also the rating of the lines allows 
> that power to pass through the line. This happens mainly for the most distant 
> nodes. In that case, all the available distributed generators generate at 
> their Pmax , but the grid infeed value is really small.
>   Why the opf  prefers to use the really expensive generators of the distant 
> nodes (used for the energy not supplied) instead of absorbing that power from 
> the free of cost grid infeed? I can guess that is a reactive problem or a 
> voltage problem but I cannot find a suitable solution. 
> Any help would be of high importance,
> King Regards,
> Angelina