Yes, I am using dispatchable loads and as far as the costs, grid infeed is of 
free cost, distributed generation is more expensive and the energy not supplied 
generators are of the highest cost. When there is energy not supplied the 
voltage in that nodes reaches the maximum upper limit (1.06) . When I change 
the voltage limit, the dispatch is again the same and the problematic nodes 
reach the new maximum upper limit. I think that the problem is the initial 
voltage of the gens in mpc.gen(:,6). What values should I put? The system 
originally had only load buses( with voltage less than 1 ). Now that I have 
transformed those buses to gen buses I should predetermined the voltages of the 
gens. I tried to put the same voltage as the mpc.bus (:, 8). But these values 
seem to be not so accurate in the end. How should I evaluate what values to put 
in the mpc.gen(:,6)?

From: [email protected]
Subject: Re: reluctant energy not supplied in a distribution system with opf
Date: Tue, 11 Feb 2014 11:14:31 -0500
To: [email protected]

I also suspect it is a reactive power or voltage problem. Is there a voltage 
limit binding at the buses where energy is not supplied (I assume you are using 
dispatchable loads)? If so, you might get some insight from doing some 
perturbation analysis. Simply change that voltage limit by a very small amount 
and see how the dispatch changes. My guess is that the only way to maintain the 
voltage is by using the expensive distributed generators. Shifting generation 
to the grid infeed would likely result in more load shedding to keep voltages 
in line. Presumably load shedding is even more costly than the distributed 
generation?Kind Regards,Angelina

-- 
Ray ZimmermanSenior Research AssociateB30 Warren Hall, Cornell University, 
Ithaca, NY 14853phone: (607) 255-9645



On Feb 11, 2014, at 5:48 AM, angelina sirri <[email protected]> wrote:Dear Dr 
Zimmerman,I am using an 11kV distribution system, which is consisted of two 
radial circuits connected by a normally open point. The network has one grid 
infeed (Vg=1) whereas all the other nodes where occupied only by loads (with 
Vm<1). Now I increase the loading of the circuits and  have added distributed 
generators in all the load buses, which will only operate in case there is a 
line fault in the system(otherwise there is no need for them to operate because 
the grid infeed can give really high power, comparing to the load and the lines 
rating is also really big) .  For the voltage problems, I have added reactive 
power in each node. The thing that confuses me is , that when there is a line 
fault (the worst case scenario line loss), there is always energy not supplied 
, although a path  from the main supply exists and also the rating of the lines 
allows that power to pass through the line. This happens mainly for the most 
distant nodes. In that case, all the available distributed generators generate 
at their Pmax , but the grid infeed value is really small.  Why the opf  
prefers to use the really expensive generators of the distant nodes (used for 
the energy not supplied) instead of absorbing that power from the free of cost 
grid infeed? I can guess that is a reactive problem or a voltage problem but I 
cannot find a suitable solution. Any help would be of high importance,King 
Regards,Angelina
                                          