Muhammad,

You are not taking into account shunt elements (Qshunt) and branch charging 
injections (Qbsh):

Tota System Q = Qgen + Qshunt + Qbsh - Qload - Qloss  = 0.0 
                        = 82.4 + 21.2 + 24.4 - 73.5 -54.54 = 0.0 


Regards

Uriel


El 01/04/2014, a las 05:02, MUHAMMAD FARAZ SAHITO <[email protected]> 
escribió:

> Hi Every One,
> I am running AC Power flow using Newton Raphson method for IEEE 14 bus 
> system, I am using following command:
> 
> results = runpf('case14');
> 
> When i get the results I see total reactive Power Injection [Q (MVAr) 
> Generation = 82.44] and total consumed reactive Power [Q (MVAr) Load = 
> 73.50]. If we subtract consumed reactive power from injected reactive power 
> we get the Loss.
> 
> Total Reactive Power Loss = Total Reactive Power Injection - Total Reactive 
> Power Consumption = 82.44 - 73.5 = 8.94 MVAR
> 
> where as AC load Flow is giving 54.54 MVAR, Can any one explain why this loss 
> is coming wrong.
> 
> Best Regards,
> Muhammad Faraz Sahito
> Graduate Student | Electrical Department
> 
>  
> 
>  
> 
>  
> 