Muhammad,


You are not taking into account shunt elements (Qshunt) and branch charging 
injections (Qbsh):

Tota System Q = Qgen + Qshunt + Qbsh - Qload - Qloss  = 0.0
= 82.4 + 21.2 + 24.4 - 73.5 -54.54 = 0.0


Regards

Uriel


El 01/04/2014, a las 05:02, MUHAMMAD FARAZ SAHITO 
<[email protected]<mailto:[email protected]>> escribió:

Hi Every One,
I am running AC Power flow using Newton Raphson method for IEEE 14 bus system, 
I am using following command:

results = runpf('case14');

When i get the results I see total reactive Power Injection [Q (MVAr) 
Generation = 82.44] and total consumed reactive Power [Q (MVAr) Load = 73.50]. 
If we subtract consumed reactive power from injected reactive power we get the 
Loss.

Total Reactive Power Loss = Total Reactive Power Injection - Total Reactive 
Power Consumption = 82.44 - 73.5 = 8.94 MVAR

where as AC load Flow is giving 54.54 MVAR, Can any one explain why this loss 
is coming wrong.