Ray,
I think the version you sent should work. It is okay to do the updating before calling pfsoln().

Regarding Niccolò’s second question about results being affected by changing load which itself is not a meaurement, the answer is it depends. If you change the load amount at non-generator bus, it should not affect the state estimation results. However, if you change the load amount at generator bus whose generation (Pg) is measured, the state estimation results will change. It is because it will change the estimation error for this Pg and therefore the total square of errors (Note that the state estimator uses weighted lease square estimation method).

To give a simple example, if Pg measurement is 100MW and at the same bus there is a 20MW load. Assume state estimation solution gives 98MW as estimated Pg. Then, the net injection at this bus is 98-20=78MW. When you change the load to 30MW and let's first assume the state estimation solution doesn't change, the net injection will then remain the same as 78MW. Now, the estimated Pg becomes 78MW+30MW=108MW. The Pg estimation error suddenly increases from the original 2MW (=100-98) to 8MW (=100-108). State estimator will be able to adjust the solution to further reduce the total square of errors, resulting in a different SE solution.

Hope it helps.

Thanks,
Rui

Rui Bo
Ph.D, Principal Engineer, Senior Member IEEE
Regulatory and Economic Studies Department
Midcontinent Independent Transmission System Operator (MISO)
2985 Ames Crossing Rd
Eagan, MN 55121, USA
Cell: (865) 951-6639
Email: [email protected], [email protected]
Personal URL: https://sites.google.com/site/eeruibo/

-----Original Message----- From: Ray Zimmerman
Sent: Tuesday, December 6, 2016 8:55 AM
To: MATPOWER discussion forum
Cc: [email protected]
Subject: Re: state estimation: active power not balanced in test cases

Thanks Rui.

Quick question … is there a reason to do the updating of the Pg and Qg values after, rather than before calling pfsoln()? I’ve attached the updated version I propose to include in v6.0.

And what about Niccolò’s second question regarding the results being affected by system load rather than simply the measurements?

Thanks,
  Ray









On Dec 6, 2016, at 2:35 AM, Ray Bo <[email protected]> wrote:

Hi Ray,
Sure I will take care of it.

Niccolò,
As I don't have 6.02b2 right now, I did a quick check on v5.1, and did see the issue you brought up. The state estimation results are actually correctly presented in the last section of the screen output, where you can see the Pg2=0.3034 pu, Pg3=0.1336 pu. So the gen, load and losses are balanced. The Pg2 and Pg3 values you see in the 'Generator Data' output section are actually the default values from the 3-bus case, and appear to be inbalanced with load. The reason Pg2 and Pg3 values do not get updated in the 'Generator Data' output section is that, to output the power flow solution in a nice format, I simply took advantage of the MATPOWER function 'pfsoln' to update bus, gen, branch data structures to match power flow solution. This function however only updates Pg for the slack bus generator and not for the rest of the generators (because those are PQ and PV buses and there is no need to do it).

To clean up the output to avoid such confusion, I have implemented a quick fix for the issue by updating the Pg and Qg using state estimation results. The code with the quick fix is attached. I haven't tested it extensively. Please use it and let me know if you find it useful or if you have additional questions. I can be reached at [email protected].

Thanks,
Rui

-----Original Message----- From: Ray Zimmerman
Sent: Monday, December 5, 2016 9:27 AM
To: Rui Bo
Cc: MATPOWER discussion forum
Subject: Re: state estimation: active power not balanced in test cases

Hi Rui and Niccolò,

The state estimation code was contributed by Rui Bo, so I’m not that familiar with it. Rui, I was wondering if you might be able to address Niccolò's questions.

Thanks,

 Ray



On Dec 1, 2016, at 6:20 PM, Niccolò Citroni <[email protected]> wrote:

Hallo, I'm new to matpower, using it for my master thesis.
I'm trying to figure out how the se program works, and running the included test cases I noticed the following: there is a big unbalance in active power in the network, for example in the 3 bus case there are more than 380 MW of active power in excess, considering generation, load, and losses. How is that possible? Another thing: modifing the load i get different results runnning the se. Why is that? shouldn't the state estimation be based only on the input mesurements and the topology of the network? How has the load and generator power anything to do with the se, when not included in the mesurements? From what I know the power balance at each node should be a result of the se, not part of the input data (when not as mesurements of course).
I hope I've been clear enough.
I'm using version 6.0b2
Thankyou for the help and the program.
Niccolò Citroni

<run_se.m>