You are missing contribution of the shunt elements defined in the GS and BS 
columns of the bus matrix. These also contribute to the overall power balance. 
Have a look at …

case_info(powerflow)

… after running your test_file.

    Ray


> On Nov 27, 2018, at 11:53 AM, José Paulos <[email protected]> wrote:
> 
> Hi,
> We have a network with the following configuration:
> %% system MVA base
> mpc.baseMVA = 100;
> 
> %% system voltage levels (kV)
> mpc.V_levels = [
>       0.4     15.0     30.0     60.0    
> ];
> 
> %% system summary
> % number of buses:             41 (1 REF | 1 PV)
> % number of branches:       41 (8 transformers)
> % number of loads:              21 (including Pd/Qd = 0) 
> % number of generators:    2
> % number of capacitors:     2
> 
> We use get_lossses, in this case:
> 
>     %%% compute the losses
>     losses = get_losses(powerflow);
>     %%% the active losses
>     active_losses = sum(abs(real(losses)));
> 
> The balance between the injected active power and the Loads/Gen's is not 
> equal to the result of the get_lossses procedure described.
> Follows attached the case (run test_file.m with test_network.mat in the same 
> dir)
> 
> Thanks in advance,
> 
> -- 
> 
> 
> José Paulos
> Centro de Sistemas de Energia
> Centre for Power and Energy Systems
> 
> INESC TEC
> Campus da FEUP
> Rua Dr Roberto Frias
> 4200-465 Porto
> Portugal
> 
> T +351 91 424 1519
> F +351 22 209 4050
> [email protected] <mailto:[email protected]>
> www.inesctec.pt <http://www.inesctec.pt/>
> 
> <test_file.m><test_network.mat>