The shunts are not included in the loss numbers, so everything does add up.

Generation = 5.4 MW
Loads = 4.9 MW
Losses = 0.4 MW
Shunt Inj = –0.1 MW

Generation + Shunt Inj  = Loads + Losses
5.4 – 0.1 = 4.9 + 0.4

    Ray


> On Nov 29, 2018, at 10:06 AM, José Paulos <[email protected]> wrote:
> 
> Hi Ray, thanks for your input.
> 
> In fact, we weren't considering that. However:
> 
> When analyzing the case_info we get:
> 
> Shunt Injections    
>     active (MW)            -0.1 
>     reactive (MVAr)         3.6 
> 
> I'm assuming that those are simplified values, but in our network, we have:
> 
> Sum of the GS Shunt Conductances = 0.0865 MW
> Difference between calculated losses vs. get_losses = 0.095 MW (that were 
> supposedly due to the missing GS values)
> Resulting a difference of 0.0085 MW (even this is different from the -0.1 MW 
> active shunt injections).
> 
> 
> 
> 
> 
> José Paulos
> Centro de Sistemas de Energia
> Centre for Power and Energy Systems
> 
> INESC TEC
> Campus da FEUP
> Rua Dr Roberto Frias
> 4200-465 Porto
> Portugal
> 
> T +351 91 424 1519
> F +351 22 209 4050
> [email protected] <mailto:[email protected]>
> www.inesctec.pt <http://www.inesctec.pt/>
> 
> On 27-Nov-18 20:03, Ray Zimmerman wrote:
>> You are missing contribution of the shunt elements defined in the GS and BS 
>> columns of the bus matrix. These also contribute to the overall power 
>> balance. Have a look at …
>> 
>> case_info(powerflow)
>> 
>> … after running your test_file.
>> 
>>     Ray
>> 
>> 
>>> On Nov 27, 2018, at 11:53 AM, José Paulos <[email protected] 
>>> <mailto:[email protected]>> wrote:
>>> 
>>> Hi,
>>> We have a network with the following configuration:
>>> %% system MVA base
>>> mpc.baseMVA = 100;
>>> 
>>> %% system voltage levels (kV)
>>> mpc.V_levels = [
>>>       0.4     15.0     30.0     60.0    
>>> ];
>>> 
>>> %% system summary
>>> % number of buses:             41 (1 REF | 1 PV)
>>> % number of branches:       41 (8 transformers)
>>> % number of loads:              21 (including Pd/Qd = 0) 
>>> % number of generators:    2
>>> % number of capacitors:     2
>>> 
>>> We use get_lossses, in this case:
>>> 
>>>     %%% compute the losses
>>>     losses = get_losses(powerflow);
>>>     %%% the active losses
>>>     active_losses = sum(abs(real(losses)));
>>> 
>>> The balance between the injected active power and the Loads/Gen's is not 
>>> equal to the result of the get_lossses procedure described.
>>> Follows attached the case (run test_file.m with test_network.mat in the 
>>> same dir)
>>> 
>>> Thanks in advance,
>>> 
>>> -- 
>>> 
>>> 
>>> José Paulos
>>> Centro de Sistemas de Energia
>>> Centre for Power and Energy Systems
>>> 
>>> INESC TEC
>>> Campus da FEUP
>>> Rua Dr Roberto Frias
>>> 4200-465 Porto
>>> Portugal
>>> 
>>> T +351 91 424 1519
>>> F +351 22 209 4050
>>> [email protected] <mailto:[email protected]>
>>> www.inesctec.pt <http://www.inesctec.pt/>
>>> 
>>> <test_file.m><test_network.mat>
>> 
> 

Reply via email to