Hi Ray, thanks for your input.

In fact, we weren't considering that. However:

When analyzing the case_info we get:

   Shunt Injections
        active (MW)            -0.1
        reactive (MVAr)         3.6

I'm assuming that those are simplified values, but in our network, we have:

Sum of the GS Shunt Conductances = *0.0865 MW*
Difference between calculated losses vs. get_losses = *0.095 MW *(that were supposedly due to the missing GS values) Resulting a difference of *0.0085 MW *(even this is different from the *-0.1 MW* active shunt injections).



INESC TEC

*José Paulos*
Centro de Sistemas de Energia
Centre for Power and Energy Systems

*INESC TEC*
Campus da FEUP
Rua Dr Roberto Frias
4200-465 Porto
Portugal

T +351 91 424 1519
F +351 22 209 4050
[email protected] <mailto:[email protected]>
www.inesctec.pt <http://www.inesctec.pt>

On 27-Nov-18 20:03, Ray Zimmerman wrote:
You are missing contribution of the shunt elements defined in the GS and BS columns of the bus matrix. These also contribute to the overall power balance. Have a look at …

case_info(powerflow)

… after running your test_file.

    Ray


On Nov 27, 2018, at 11:53 AM, José Paulos <[email protected] <mailto:[email protected]>> wrote:

Hi,

We have a network with the following configuration:

    *%% system MVA base*
    mpc.baseMVA = 100;

    *%% system voltage levels (kV)*
    mpc.V_levels = [
          0.4     15.0     30.0     60.0
    ];

    *%% system summary*
    % number of buses:             41 (1 REF | 1 PV)
    % number of branches:       41 (8 transformers)
    % number of loads:              21 (including Pd/Qd = 0)
    % number of generators:    2
    % number of capacitors:     2

We use get_lossses, in this case:

    %%% *compute the losses*
    losses = get_losses(powerflow);
    %%% *the active losses*
    active_losses = sum(abs(real(losses)));

The balance between the injected active power and the Loads/Gen's is not equal to the result of the get_lossses procedure described.

Follows attached the case (run test_file.m with test_network.mat in the same dir)

Thanks in advance,

--

INESC TEC

*José Paulos*
Centro de Sistemas de Energia
Centre for Power and Energy Systems

*INESC TEC*
Campus da FEUP
Rua Dr Roberto Frias
4200-465 Porto
Portugal

T +351 91 424 1519
F +351 22 209 4050
[email protected] <mailto:[email protected]>
www.inesctec.pt <http://www.inesctec.pt/>

<test_file.m><test_network.mat>