Those are the VAr flows in the branches (corresponding to the circulating 
current) from bus 1 to bus 2 in branch 1, and vice versa in branch 2. And you 
are correct that the current version of MATPOWER does not include a unique 
branch identifier to distinguish parallel branches, so they are only 
distinguished by their order of appearance in the branch matrix.

    Ray


On Dec 11, 2020, at 4:53 PM, Russ Patterson 
<[email protected]<mailto:[email protected]>> wrote:

Hi friends,

I have a simple power flow case with an infinite bus and 2 transformers (no 
load).  The transformers have different turns ratios so I’ll get circulating 
current and VAr drop in the banks.

#1 Transformer (100MVA)
161:13.8kV, X=0.1pu

#2 Transformer (100MVA)
161:13.14kV, X=0.1pu

<image001.png>

The voltage difference is (13.8kV – 13.14kV)/13.8kV = 0.0478 pu which is the 
driving voltage for the circulating current.  The circulating current will be 
0.0478/0.2pu = 0.239pu A.  This circulating current will produce a var drop of 
Q = (0.239)(0.239) x (0.2) = 0.01144 pu.  This is 1.14MVAr.

I ran the attached power flow case and got 1.13MVAR (nice).  But, I don’t 
understand the big MVAr drops being reported in the branch report (see below).  
What is causing those big values?

================================================================================
|     Branch Data                                                              |
================================================================================
Brnch   From   To    From Bus Injection   To Bus Injection     Loss (I^2 * Z)
  #     Bus    Bus    P (MW)   Q (MVAr)   P (MW)   Q (MVAr)   P (MW)   Q (MVAr)
-----  -----  -----  --------  --------  --------  --------  --------  --------
   1      1      2      0.00     23.81      0.00    -23.24    -0.000      0.57
   2      1      2      0.00    -22.68      0.00     23.24    -0.000      0.57
                                                             --------  --------
                                                    Total:     0.000      1.13

I have a second minor question, how do you specify “branch 1” or “branch 2” 
when you have 2 branches between 2 buses?  Does MATPOWER just take them in 
order they show up in the mpc.branch structure (e.g. the 1st occurrence as 
“branch 1”)?  I did “help idx_brch” but didn’t see anything specifying.

Thank you,
Russ

<circulating_current_no_load.m>