As in Case 9, all bus voltage is specified to be 345 kV. If the transformer
defaults ratio is 1:1, does it mean that the generator is connected in 345
kV as well? Thank you.

Best regards,

Ahmad

On Thu, 7 Jul 2022 at 08:55, Carlos E Murillo-Sanchez <
[email protected]> wrote:

> Ahmad Bariq Al Fahri wrote:
>
> I would like to ask about case9.m (9 bus, 3 generators case) system
> configuration. As I know that the parameters of 'TAP' (column 9) in the
> branch data are set to zero, does it mean that the system does not consider
> transformer modelling? Is the generator directly connected to the 345 kV
> bus? I am looking forward to your reply. Thank you in advance.
>
> Best regards,
>
> Ahmad
>
> Dear Ahmad:
>
> In MATPOWER, if the TAP column has a zero, then the ratio defaults to 1:1,
> in the sense that 1 pu at the "FROM" end produces 1 pu at the "TO" end of
> the ideal transformer in the generalized branch model.  Indeed, if you
> assign 1.0 to the TAP column you will get the same results.
>
> Carlos.
>
>