Okay, thanks again for the answer.

On Thu, Jul 7, 2022, 10:08 PM Carlos E Murillo-Sanchez <
[email protected]> wrote:

> Ahmad Bariq Al Fahri wrote:
>
> Thank you Carlos for the information.
> As in Case 9, all bus voltage is specified to be 345 kV. If the
> transformer defaults ratio is 1:1, does it mean that the generator is
> connected in 345 kV as well? Thank you.
>
> Best regards,
>
> Ahmad
>
> Dear Ahmad:
>
> No, it just means that the winding ratio corresponds exactly to the ratio
> of the nominal voltages on both sides of the transformer.  The TAP setting
> corresponds to off-nominal deviations, not to the physical winding ratio.
> In fact, the nominal voltages at the generator buses for case9.m are
> really  16.5, 18, and 13.8 KV, while the nominal transmission voltage is
> 230 KV if I recall correctly.  MATPOWER only uses the (already converted to
> pu) branch impedances, the system MVA base, and the off-nominal TAP ratio;
> the BASE_KV column in the bus matrix is not used for power flows.
>
> Carlos.
>
>