You are right, it would be a monumental task to put together a listing of each and every component item in a typical system and then look up the flame ratings on each (if you could find them). To date this has not been my understanding of what is required. You must have entries for at least 95% of the polymeric load of the system which document how they are acceptable as components under GR-63 4.2.3. The remainder of the system fuel load should be described qualitatively.

So we build a flame database where the line items are the bare boards and then the component assemblies. So instead of tens of thousands of table entries, we have tens. But our database still covers at least 95% of the polymeric load of the system and documents that they comply with the component requirements of Gr-63.

You can prove component acceptability one of three ways:

1.  By flame rating/ O2 index rating.
or
2.  By individual needle flame on each component (x3 samples)
or
3.  By needle flame testing on the component mounted on an assembly in-situ.

There are various application times and performance standards for each of these methods in Gr-63.

The most efficient way to cover a system is to perform needle flame testing on subassemblies. It takes about 2 days of needle flame testing to get the testing done on a typical board system set as you need to direct the needle flame at many/multiple components on each assembly in order to qualify them.

If a more detailed component listing was ever required, it could be constructed by expanding the subassemblies entries in the database by entering their BOMs. For each of the components so entered the comment statement would be "acceptable proved by subassembly needle flame testing per Section 5.2.4".

[email protected] wrote:

Hi Jon,

Can you give me a little detail regarding the database you put together?  It
seems to me to be a huge task.  You have to list all of the plastic
components in the system and either give the CTI or the weight of t he
plastic material for each part.

Am I missing something?  If not, what is your charge to create the database?

Thanks,

Jack

-----Original Message-----
From: Jon Curtis [mailto:[email protected]]
Sent: Friday, February 15, 2002 1:36 PM
To: [email protected]
Subject: Re: Fire Resistance Database Analysis


Hi Dave,

I asked Verizon at the Las Vegas conference if they wanted a report from an independent source to support GR-78 compliance and they indicated at that time that they did not feel that was necessary.

At Curtis-Straus, we routinely put together an assembly level flame database for every complete GR-63 report we produce. The Verizon checklist says that you need to provide it if they ask for it.

Dave Wilson wrote:

Hi,

I'm looking at the Verizon NEBS requirements, which along with GR-63 and
GR-1089 call out the design guidelines in GR-78. Does GR-78 compliance have
to be assessed independently for Verizon compliance, or is manufacturer's
declaration on the NEBS checklist sufficient (section 2.8.1 would suggest
otherwise, but design guidelines are not as readily measurable as say,
environmental or EMC criteria)?

Also, has anyone out there put together a fire resistance database in
accordance with GR-63 4.3.2.1 before? Was it necessary for Verizon
compliance? Or is shelf/frame-level flame testing and needle-flame

component

testing sufficient, provided the split-frame infra-red video requirements
for Verizon are met?

Thanks in advance,

Dave Wilson
Manager, Quality & Compliance
Alidian Networks, Inc.




--
Jon D. Curtis, P.E.

Director of Engineering
Curtis-Straus LLC NRTL TCB

One Stop Laboratory for NEBS, EMC, Product Safety, and Telecom Testing.
527 Great Road
Littleton, MA 01460 USA
Voice 978-486-8880  Fax 978-486-8828
email: [email protected]
WWW.CURTIS-STRAUS.COM


Reply via email to