I did some research on UL/CSA approved transformers, and there is a 
requirement that all windings withstand a minimum breakdown voltage, even 
if they are intended to be connected together, such as dual-primaries. 
Depending upon the VA rating and the voltage, the breakdown must be between 
1050 and 4000 V RMS according to how I read the spec (UL5058-2 / CSA C22.2 
#66). The test is conducted between 1 winding, and all other windings and 
the core combined and at elevated temperature. There are copies of the spec 
online.

I knew there had to be some amount of isolation, but I did not realize it 
was *that* high. While I would never expose or touch anything that is 
supposedly "isolated", it does reassure me there is decent insulation.


-- 