> there are definitely wrong (at least fallback) declarations in mge-hid.c
> as an example, we should try to map the below 2nd one as a fallback
> since it's really the nominal *output* voltage, not the battery one:
> { "battery.voltage.nominal", 0, 0, "UPS.BatterySystem.ConfigVoltage",
> NULL, "%.0f", HU_FLAG_STATIC, NULL },
> { "battery.voltage.nominal", 0, 0, "UPS.PowerSummary.ConfigVoltage",
> NULL, "%s", HU_FLAG_STATIC, mge_battery_voltage_nominal },
>
> gotta fix this.
That's a pretty bold statement you make here. On at least two different
MGE units (Evolution 650 (broken) and Pulsar M 2200 (good)) it actually
*is* reporting 'battery.voltage.nominal' and not 'output.voltage.nominal'
(below a summary for the Pulsar M 2200 I found in the archives):
Path: UPS.PowerSummary.ConfigVoltage, Type: Feature, Value: 72.000000
Path: UPS.PowerSummary.Voltage, Type: Feature, Value: 81.000000
Can't find object UPS.BatterySystem.ConfigVoltage
>From looking at the reported values, I'm fairly sure that these deal with
the *battery* voltage and not the *output* voltage (at least for this UPS
and possibly others too, I recall having seen reports where people
actually complained that NUT was reporting impossibly low
'output.voltage.nominal'). So I don't think there is something *broken*
here. What is probably *missing* is the HID path that is reporting the
battery on Charles' UPS, so that the driver won't have to fallback to
"UPS.PowerSummary.ConfigVoltage". Alternatively, if this UPS doesn't
report nominal or actual battery voltage, we may need to ignore these
values.
We may also wish to add "UPS.PowerSummary.ConfigVoltage" as a fallback
when "UPS.Flow.[4].ConfigVoltage" can't be found. But since it can have
two meanings, we can only use it as a fallback if the other paths that
deal with these ("UPS.BatterySystem.ConfigVoltage" and
"UPS.Flow.[4].ConfigVoltage" respectively) can't be found.
I therefor propose to add the following to 'mge-hid.c':
/* Output page */
{ "output.voltage", 0, 0, "UPS.PowerConverter.Output.Voltage", NULL,
"%.1f", 0, NULL },
{ "output.voltage.nominal", ST_FLAG_RW | ST_FLAG_STRING, 5,
"UPS.Flow.[4].ConfigVoltage", NULL, "%.0f", HU_FLAG_SEMI_STATIC, NULL },
+ { "output.voltage.nominal", 0, 0, "UPS.PowerSummary.ConfigVoltage",
NULL, "%.0f", HU_FLAG_STATIC, NULL },
{ "output.current", 0, 0, "UPS.PowerConverter.Output.Current", NULL,
"%.2f", 0, NULL },
{ "output.powerfactor", 0, 0, "UPS.PowerConverter.Output.PowerFactor",
NULL, "%s", 0, mge_powerfactor_conversion },
Best regards, Arjen