>> Can you post a full listing of the driver running in debug level 2? > I think that's here... should I do something different than what was > in the 2nd attachment in the message below?
Ooops. I forgot that you already did. Never mind. From the HID paths that indicate a voltage, only the following two are candidates for the battery voltage: > Path: UPS.PowerSummary.ConfigVoltage, Type: Feature, ReportID: 0x27, Offset: 0, Size: 16, Value: 120.000000 > Path: UPS.PowerSummary.Voltage, Type: Feature, ReportID: 0x2b, Offset: 16, Size: 16, Value: 119.000000 The other four are clearly *not* indicating a battery voltage: > Path: UPS.Flow.[1].ConfigVoltage, Type: Feature, ReportID: 0x13, Offset: 16, Size: 16, Value: 120.000000 > Path: UPS.Flow.[4].ConfigVoltage, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 120.000000 > Path: UPS.PowerConverter.Input.[1].Voltage, Type: Feature, ReportID: 0x19, Offset: 24, Size: 16, Value: 0.000000 > Path: UPS.PowerConverter.Output.Voltage, Type: Feature, ReportID: 0x1c, Offset: 48, Size: 16, Value: 120.000000 The first two (Flow.[1] and Flow.[4]) are the input- and output respectively and the last two specifically mention that they are *.Input.Voltage and *.Output.Voltage. Since we also know that the UPS was without input power at the time you ran this report, there is no ambiguity. These are not the battery voltage. This leaves the two possibilities for "UPS.PowerSummary.ConfigVoltage" and "UPS.PowerSummary.Voltage": 1) They have indeed nothing to do with the battery on your UPS, which means that yours probably has no means of indicating the battery voltage. In this case, we should override these values (in a similar way as we already do for the Evolution 650) or mask them out completely. 2) They actually *do* report the (nominal) battery voltage, just the multiplier is off by a factor of 10. In that case, we need a conversion function that modifies these values. For reasons I already mentioned in an earlier post, changing the meaning of these HID paths (as Arnaud suggested) is not an option, we'll have to deal with this on a model specific basis. Best regards, Arjen _______________________________________________ Nut-upsdev mailing list [email protected] http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev