The tripplite driver was developed on a machine with a reliable serial
connection, and inherited the assumption that the serial line connection
would not drop, reorder, or fail character read and writes.  This patch
adds significantly improved failure mode handling and also does basic
checks of data validity.

There's also a few minor cleanups/beautification.

I've tested this code on my machine that runs a Smart 700 on a sporadically
unreliable serial interface, and it works for me.  The old code would
sometimes mysteriously segfault in libc or return wildly out of range values.

Patch is against 2.2.2.

Detailed changes:

- Update comment for tripplite documentation URL; appears to be dead now.
- Move #defines to tripplite.h
- Remove a useless static float definition and replace with an inline
  constant; saves .text space, easier to read, and optimizes better.
- Open code hex2d() buffer handling.  strncpy's edge case is ugly.  The
  old code could never overflow, but was harder to read.
- send_cmd() now flushes both input and output buffers on exit or failure.
  This change guards against corrupted serial port i/o between send_cmd()
  calls.
- Squash a harmless unsigned/signed char warning in send_cmd().
- upsdrv_initinfo() now retries W/L/V/X commands on failure.  I've never
  seen these commands fail, but better to be safe.
- upsdrv_shutdown() is significantly more robust.  All serial i/o is checked
  for failure, errors are reported, and where possible, data returned is
  checked for range validity.
- Wait time for ser_get calls is now 1.0s rather than 3.0s.
- Update copyright date.

--- nut-2.2.2/drivers/tripplite.c       2007-05-26 10:24:26.000000000 -0400
+++ nut-2.2.2-nk/drivers/tripplite.c    2008-07-09 16:38:08.000000000 -0400
@@ -6,7 +6,7 @@
 
    Copyright (C) 1999  Russell Kroll <[EMAIL PROTECTED]>
    Copyright (C) 2001  Rickard E. (Rik) Faith <[EMAIL PROTECTED]>
-   Copyright (C) 2004  Nicholas J. Kain <[EMAIL PROTECTED]>
+   Copyright (C) 2004,2008  Nicholas J. Kain <[EMAIL PROTECTED]>
 
    This program is free software; you can redistribute it and/or modify
    it under the terms of the GNU General Public License as published by
@@ -26,8 +26,8 @@
 /* REFERENCE 1
 
    A few magic numbers were derived from the GPL'd file
-   opensrc_server/upscmd.cpp, available from Tripp Lite at
-   http://www.tripplite.com/linux/.
+   opensrc_server/upscmd.cpp, formerly (but not longer) available from
+   Tripp Lite at http://www.tripplite.com/linux/.
 */
 
 /* REFERENCE 2
@@ -111,30 +111,6 @@
 #include <math.h>
 #include <ctype.h>
 
-#define ENDCHAR '\n'           /* replies end with CR LF -- use LF to end */
-#define IGNCHAR '\r'           /* ignore CR */
-#define MAXTRIES 3
-#define SER_WAIT_SEC  3        /* allow 3.0 sec for ser_get calls */
-#define SER_WAIT_USEC 0
-#define DEFAULT_OFFDELAY   64  /* seconds (max 0xFF) */
-#define DEFAULT_STARTDELAY 60  /* seconds (max 0xFFFFFF) */
-#define DEFAULT_BOOTDELAY  64  /* seconds (max 0xFF) */
-#define MAX_VOLT 13.4          /* Max battery voltage (100%) */
-#define MIN_VOLT 11.0          /* Min battery voltage (10%) */
-
-/* We calculate battery charge (q) as a function of voltage (V).
- * It seems that this function probably varies by firmware revision or
- * UPS model - the Windows monitoring software gives different q for a
- * given V than the old open source Tripp Lite monitoring software.
- *
- * The discharge curve should be the same for any given battery chemistry,
- * so it should only be necessary to specify the minimum and maximum
- * voltages likely to be seen in operation.
- */
-
-/* Interval notation for Q% = 10% <= [minV, maxV] <= 100%  */
-static float V_interval[2] = {MIN_VOLT, MAX_VOLT};
-
 /* Time in seconds to delay before shutting down. */
 static unsigned int offdelay = DEFAULT_OFFDELAY;
 static unsigned int startdelay = DEFAULT_STARTDELAY;
@@ -143,9 +119,15 @@ static unsigned int bootdelay = DEFAULT_
 static int hex2d(char *start, unsigned int len)
 {
        char buf[32];
-       buf[31] = '\0';
+       unsigned int i;
+
+       for(i = 0; i < len && i < (sizeof buf - 1); ++i)
+           buf[i] = start[i];
+       if (i < (sizeof buf - 1))
+           buf[i] = '\0';
+       else
+           buf[i-1] = '\0';
 
-       strncpy(buf, start, (len < (sizeof buf) ? len : (sizeof buf - 1)));
        return strtol(buf, NULL, 16);
 }
 
@@ -159,34 +141,36 @@ static int hex2d(char *start, unsigned i
  * return: # of chars in buf, excluding terminating \0 */
 static int send_cmd(const char *str, char *buf, size_t len)
 {
-       char c;
-       int ret;
+       unsigned char c;
+       int ret = 0;
        size_t i = 0;
 
        ser_send(upsfd, str);
 
        if (!len || !buf)
-               return -1;
+               goto out;
 
        for (;;) {
                ret = ser_get_char(upsfd, &c, SER_WAIT_SEC, SER_WAIT_USEC);
                if (ret == -1)
-                       return -1;
+                       goto out;
                if (c == ENDCHAR)
                        break;
        }
        do {
                ret = ser_get_char(upsfd, &c, SER_WAIT_SEC, SER_WAIT_USEC);
                if (ret == -1)
-                       return -1;
+                       goto out;
 
                if (c == IGNCHAR || c == ENDCHAR)
                        continue;
                buf[i++] = c;
        } while (c != ENDCHAR && i < len);
        buf[i] = '\0';
-       ser_flush_in(upsfd, NULL, 0);
-       return i;
+       ret = i;
+out:
+       ser_flush_io(upsfd);
+       return ret;
 }
 
 static void ups_sync(void)
@@ -301,14 +285,17 @@ void upsdrv_initinfo(void)
        int  va;
        long w, l;
 
-
        /* Detect the UPS or die. */
        ups_sync();
 
-       send_cmd(":W\r", w_value, sizeof w_value);
-       send_cmd(":L\r", l_value, sizeof l_value);
-       send_cmd(":V\r", v_value, sizeof v_value);
-       send_cmd(":X\r", x_value, sizeof x_value);
+       while (send_cmd(":W\r", w_value, sizeof w_value) < 1)
+           sleep(1);
+       while (send_cmd(":L\r", l_value, sizeof l_value) < 1)
+           sleep(1);
+       while (send_cmd(":V\r", v_value, sizeof v_value) < 1)
+           sleep(1);
+       while (send_cmd(":X\r", x_value, sizeof x_value) < 1)
+           sleep(1);
 
        dstate_setinfo("ups.mfr", "%s", "Tripp Lite");
 
@@ -365,57 +352,111 @@ void upsdrv_shutdown(void)
 void upsdrv_updateinfo(void)
 {
        char buf[256];
-       int bp;
-       float bv;
+       int bp, volt, temp, load, vmax, vmin, stest, len;
+       int bcond, lstate, tstate, mode;
+       float bv, freq;
+
+       len = send_cmd(":D\r", buf, sizeof buf);
+       if (len != 21) {
+               ser_comm_fail("Data command failed: [%d] bytes != 21 bytes.", 
len);
+                       dstate_datastale();
+               return;
+       }
+
+       volt = hex2d(buf + 2, 2);
+       temp = (int)(hex2d(buf + 6, 2)*0.3636 - 21.0);
+       load = hex2d(buf + 12, 2);
+       freq = hex2d(buf + 18, 3) / 10.0;
+       bcond = buf[0];
+       lstate = buf[1];
+       tstate = buf[4];
+       mode = buf[5];
+       if (volt > INVOLT_MAX || volt < INVOLT_MIN ||
+                       temp > TEMP_MAX || temp < TEMP_MIN ||
+                       load > LOAD_MAX || load < LOAD_MIN ||
+                       freq > FREQ_MAX || freq < FREQ_MIN) {
+               ser_comm_fail("Data out of bounds: [%0d,%3d,%3d,%02.2f]",
+                               volt, temp, load, freq);
+               dstate_datastale();
+               return;
+       }
+
+       send_cmd(":B\r", buf, sizeof buf);
+       bv = (float)hex2d(buf, 2) / 10.0;
+       if (bv > 50.0 || bv < 0.0) {
+               ser_comm_fail("Battery voltage out of bounds: [%02.1f]", bv);
+               dstate_datastale();
+               return;
+       }
 
-       send_cmd(":D\r", buf, sizeof buf);
+       send_cmd(":M\r", buf, sizeof buf);
+       vmax = hex2d(buf, 2);
+       if (vmax > INVOLT_MAX || vmax < INVOLT_MIN) {
+               ser_comm_fail("InVoltMax out of bounds: [%d]", vmax);
+               dstate_datastale();
+               return;
+       }
 
-       if (strlen(buf) < 21) {
-               ser_comm_fail("Failed to get data: short read from UPS");
+       send_cmd(":I\r", buf, sizeof buf);
+       vmin = hex2d(buf, 2);
+       if (vmin > INVOLT_MAX || vmin < INVOLT_MIN) {
+               ser_comm_fail("InVoltMin out of bounds: [%d]", vmin);
                dstate_datastale();
                return;
        }
 
-       if (strlen(buf) > 21) {
-               ser_comm_fail("Failed to get data: oversized read from UPS");
+       send_cmd(":C\r", buf, sizeof buf);
+       errno = 0;
+       stest = strtol(buf, 0, 10);
+       if (errno == ERANGE) {
+               ser_comm_fail("Self test is out of range: [%d]", stest);
+               dstate_datastale();
+               return;
+       }
+       if (errno == EINVAL) {
+               ser_comm_fail("Self test returned non-numeric data.");
+               dstate_datastale();
+               return;
+       }
+       if (stest > 3 || stest < 0) {
+               ser_comm_fail("Self test out of bounds: [%d]", stest);
                dstate_datastale();
                return;
        }
 
-       dstate_setinfo("input.voltage", "%0d", hex2d(buf + 2, 2));
-       dstate_setinfo("ups.temperature", "%3d",
-                       (int)(hex2d(buf + 6, 2)*0.3636 - 21.0));
-       dstate_setinfo("ups.load", "%3d", hex2d(buf + 12, 2));
-       dstate_setinfo("input.frequency", "%02.2f", hex2d(buf + 18, 3) / 10.0);
+       dstate_setinfo("input.voltage", "%0d", volt);
+       dstate_setinfo("ups.temperature", "%3d", temp);
+       dstate_setinfo("ups.load", "%3d", load);
+       dstate_setinfo("input.frequency", "%02.2f", freq);
 
        status_init();
 
        /* Battery Voltage Condition */
-       switch (buf[0]) {
+       switch (bcond) {
                case '0': /* Low Battery */
                        status_set("LB");
                        break;
                case '1': /* Normal */
                        break;
                default: /* Unknown */
-                       upslogx(LOG_ERR, "Unknown battery state: %c", buf[0]);
+                       upslogx(LOG_ERR, "Unknown battery state: %c", bcond);
                        break;
        }
 
        /* Load State */
-       switch (buf[1]) {
+       switch (lstate) {
                case '0': /* Overload */
                        status_set("OVER");
                        break;
                case '1': /* Normal */
                        break;
                default: /* Unknown */
-                       upslogx(LOG_ERR, "Unknown load state: %c", buf[1]);
+                       upslogx(LOG_ERR, "Unknown load state: %c", lstate);
                        break;
        }
 
        /* Tap State */
-       switch (buf[4]) {
+       switch (tstate) {
                case '0': /* Normal */
                        break;
                case '1': /* Reducing */
@@ -426,12 +467,12 @@ void upsdrv_updateinfo(void)
                        status_set("BOOST");
                        break;
                default: /* Unknown */
-                       upslogx(LOG_ERR, "Unknown tap state: %c", buf[4]);
+                       upslogx(LOG_ERR, "Unknown tap state: %c", tstate);
                        break;
        }
 
        /* Mode */
-       switch (buf[5]) {
+       switch (mode) {
                case '0': /* Off */
                        status_set("OFF");
                        break;
@@ -445,36 +486,28 @@ void upsdrv_updateinfo(void)
                        status_set("OB");
                        break;
                default: /* Unknown */
-                       upslogx(LOG_ERR, "Unknown mode state: %c", buf[4]);
+                       upslogx(LOG_ERR, "Unknown mode state: %c", mode);
                        break;
        }
 
        status_commit();
-       send_cmd(":B\r", buf, sizeof buf);
-       bv = (float)hex2d(buf, 2) / 10.0;
 
        /* dq ~= sqrt(dV) is a reasonable approximation
         * Results fit well against the discrete function used in the Tripp Lite
         * source, but give a continuous result. */
-       if (bv >= V_interval[1])
+       if (bv >= MAX_VOLT)
                bp = 100;
-       else if (bv <= V_interval[0])
+       else if (bv <= MIN_VOLT)
                bp = 10;
        else
-               bp = (int)(100*sqrt((bv - V_interval[0])
-                                                       / (V_interval[1] - 
V_interval[0])));
+               bp = (int)(100*sqrt((bv - MIN_VOLT) / (MAX_VOLT - MIN_VOLT)));
 
        dstate_setinfo("battery.voltage", "%.1f", bv);
        dstate_setinfo("battery.charge",  "%3d", bp);
+       dstate_setinfo("input.voltage.maximum", "%d", vmax);
+       dstate_setinfo("input.voltage.minimum", "%d", vmin);
 
-       send_cmd(":M\r", buf, sizeof buf);
-       dstate_setinfo("input.voltage.maximum", "%d", hex2d(buf, 2));
-
-       send_cmd(":I\r", buf, sizeof buf);
-       dstate_setinfo("input.voltage.minimum", "%d", hex2d(buf, 2));
-
-       send_cmd(":C\r", buf, sizeof buf);
-       switch (atoi(buf)) {
+       switch (stest) {
                case 0:
                        dstate_setinfo("ups.test.result", "%s", "OK");
                        break;
--- nut-2.2.2/drivers/tripplite.h       2005-09-12 08:38:36.000000000 -0400
+++ nut-2.2.2-nk/drivers/tripplite.h    2008-07-09 14:53:00.000000000 -0400
@@ -6,7 +6,7 @@
 
    Copyright (C) 1999  Russell Kroll <[EMAIL PROTECTED]>
    Copyright (C) 2001  Rickard E. (Rik) Faith <[EMAIL PROTECTED]>
-   Copyright (C) 2004  Nicholas J. Kain <[EMAIL PROTECTED]>
+   Copyright (C) 2004,2008  Nicholas J. Kain <[EMAIL PROTECTED]>
 
    This program is free software; you can redistribute it and/or modify
    it under the terms of the GNU General Public License as published by
@@ -23,4 +23,38 @@
    Foundation, Inc., 59 Temple Place, Suite 330, Boston, MA 02111-1307 USA
 */
 
-#define DRV_VERSION "0.8"
+#define DRV_VERSION "0.9"
+
+#define ENDCHAR '\n'           /* replies end with CR LF -- use LF to end */
+#define IGNCHAR '\r'           /* ignore CR */
+#define MAXTRIES 3             /* max number of times we try to detect ups */
+#define SER_WAIT_SEC  1        /* allow 1.0 sec for ser_get calls */
+#define SER_WAIT_USEC 0
+#define DEFAULT_OFFDELAY   64  /* seconds (max 0xFF) */
+#define DEFAULT_STARTDELAY 60  /* seconds (max 0xFFFFFF) */
+#define DEFAULT_BOOTDELAY  64  /* seconds (max 0xFF) */
+
+/* Sometimes the UPS seems to return bad data, so we range check it. */
+#define INVOLT_MAX 270
+#define INVOLT_MIN 0
+#define FREQ_MAX 80.0
+#define FREQ_MIN 30.0
+#define TEMP_MAX 100
+#define TEMP_MIN 0
+#define LOAD_MAX 100
+#define LOAD_MIN 0
+
+/* We calculate battery charge (q) as a function of voltage (V).
+ * It seems that this function probably varies by firmware revision or
+ * UPS model - the Windows monitoring software gives different q for a
+ * given V than the old open source Tripp Lite monitoring software.
+ *
+ * The discharge curve should be the same for any given battery chemistry,
+ * so it should only be necessary to specify the minimum and maximum
+ * voltages likely to be seen in operation.
+ */
+
+/* Interval notation for Q% = 10% <= [minV, maxV] <= 100%  */
+#define MAX_VOLT 13.4          /* Max battery voltage (100%) */
+#define MIN_VOLT 11.0          /* Min battery voltage (10%) */
+

-- 
Nicholas J. Kain <nicholas at kain dot us>