Arjen de Korte ha scritto:
Citeren Marco Chiappero <[email protected]>:
When you read the corresponding values from the summary page, the values
are reversed however. If we would parse the summary page between these
alarms (be it right after parsing an alarm or just before receiving the
next), with every new incoming alarm, the previous status would be reset
again. So if we want to keep the alarms as they are, we should disregard
the values set by the summary page. However, since the above alarm bits
are never cleared by an alarm message after the test, this would mean
that pressing this test button once would effectively permanently
disable the outlet.
Well, the test is supposed to perform a shutdown, so it's assumed that
NUT is restarted. I see no problem in this behaviour.
I compiled your code yesterday evening, everything looks fine but I
noticed that every 180 secs a new subscription is made: is there a
reason for this? And I see that +20-25% more traffic generated.
Thinking a little bit, I would just read alarm messages and the
get_object page: when everything is fine extended data is updated once
every pollinterval and the relevant one immediately by the alarm
messages, when the UPS goes on battery we can scan the summary page too,
frequently.
Regards,
Marco
_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev