Citeren Marco Chiappero <[email protected]>:

When you read the corresponding values from the summary page, the values are reversed however. If we would parse the summary page between these alarms (be it right after parsing an alarm or just before receiving the next), with every new incoming alarm, the previous status would be reset again. So if we want to keep the alarms as they are, we should disregard the values set by the summary page. However, since the above alarm bits are never cleared by an alarm message after the test, this would mean that pressing this test button once would effectively permanently disable the outlet.
Well, the test is supposed to perform a shutdown, so it's assumed that NUT is restarted. I see no problem in this behaviour.

There is no guarantee that the machine where the driver is running on is also powered by the UPS. Most systems administrators like NUT because it allows you to centralize UPS monitoring from a single machine. Allowing the above would mean that each NMC would require a dedicated machine to run the driver on. This pretty much defeats the whole purpose of NUT.

I compiled your code yesterday evening, everything looks fine but I noticed that every 180 secs a new subscription is made: is there a reason for this?

The only reason could be that the driver is not getting alarm messages. The driver should periodically receive empty alarm messages from the NMC. If it doesn't, it assumes the connection is somehow lost and subscribes again. Do you see the empty alarm messages if you run the driver with -DD enabled?

And I see that +20-25% more traffic generated.

This could be the case since we poll both the summary and get_object pages for each pollinterval. If this interval is short, you may notice an increase compared to the previous code non-subscribed mode. The only reason for adding the NSM subscribed mode, is to allow increasing the pollinterval. If you keep it at something like 5 seconds, there is no point in NSM subscriptions.

Thinking a little bit, I would just read alarm messages and the get_object page: when everything is fine extended data is updated once every pollinterval and the relevant one immediately by the alarm messages, when the UPS goes on battery we can scan the summary page too, frequently.

We're only reading the summary page because for some NMC models it contains info the get_object page doesn't (environmental info mostly, but some other things as well). Previously we would poll the summary page only one out of ten calls. This is sufficient if the pollinterval is short, but now that we poll much less frequently (pollinterval = 64), we should poll both at the same time.

Best regards, Arjen
--
Please keep list traffic on the list


_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsdev