Arjen de Korte ha scritto:
Citeren Marco Chiappero <[email protected]>:

Maybe there is something I'm missing, but if that particular machine don't need to go down just do not let it shutdown, it will simply see the low battery flag and notice it.

The problem is, that this flag will never be cleared by an alarm message.

I can't see the problem, it's just for testing purpose, while setting things up. Once done NUT must be restarted, if that schema is used. Need only to be mentioned in the man page.
Alarm messages can't get lost on TCP (unless explicitly dropped).

Could it be that the card is rebooting? If you're running multiple clients in parallel, this might trigger an NMC reset.

Ok, I didn't noticed it at first: the NMC keeps resetting all the subscription connections when using other clients along with NUT. However it started working like this after the netxml-ups upgrade. Had to stop NUT. I never experienced such issue before. Ok, found... the netxml-ups driver keeps asking the get_object page really often.

How do you know the subscription is successful without running the driver in debug mode? Currently, the driver won't inform you about that.

Network traffic sniffing (tcpdump in particular).