Hi, Arnaud

Thank You for Your kind answer.

I attempted to use USB, as You suggested. After connecting the cable, kernel 
detects HP R 5000 as HID like this:

[ 1701.100025] usb 2-1: new full speed USB device using ohci_hcd and address 2
[ 1701.324982] usb 2-1: New USB device found, idVendor=03f0, idProduct=1fe7
[ 1701.324985] usb 2-1: New USB device strings: Mfr=1, Product=2, SerialNumber=4
[ 1701.324989] usb 2-1: Product: HP R5000
[ 1701.324991] usb 2-1: Manufacturer: HP
[ 1701.324992] usb 2-1: SerialNumber: 3C81520083 
[ 1701.325147] usb 2-1: configuration #1 chosen from 1 choice
[ 1701.391326] usbcore: registered new interface driver hiddev
[ 1701.433359] generic-usb: probe of 0003:03F0:1FE7.0001 failed with error -22
[ 1701.433395] usbcore: registered new interface driver usbhid
[ 1701.433460] usbhid: v2.6:USB HID core driver

Although generic-usb fails with error -22, I hope this should not be a problem, 
since next lines, usbcore and usbhid show no no sign of trouble.

I set ups.conf like this:

 protocol = usbhid-ups
 port = auto

However, starting upsdrvctl shows this error:

 Network UPS Tools - UPS driver controller 2.4.3
 Network UPS Tools - Generic HID driver 0.34 (2.4.3)
 USB communication driver 0.31
 No matching HID UPS found
 Driver failed to start (exit status=1)


Should I use some exact vendor specification in ups.conf and if, what should it 
be? Or is there other source of trouble?

cheers,
Peter
 
----------------Pôvodná správa-----------------
Od: "Arnaud Quette" [email protected] 
Komu: "Peter Tuhársky" [email protected] 
Kópia: [email protected] 
Dátum: Thu, 29 Mar 2012 18:38:17 +0200
-------------------------------------------------
 
 
> Hi Peter,
> 
> sorry for the lag in answering... crowded week.
> 
> One thing bothers me. I don't see parameters like "battery.runtime.low"
>> here. How will the UPS notice the NUT that it is running critically low? Or
>> better said, when will it do that?
>>
>> With APC, there is such parameter, default set to 120 seconds. As I
>> understand, when battery goes critically low (2 minutes before getting
>> fully discharged), it sends "battery critical" to the NUT server, and the
>> NUT sends "shutdown" command to clients.
>>
> 
> that's it.
> 
> However with the HP, either R5000 or R5500, there is no such parameter, and
>> I even didn't find it in web interface settings. There is quite opposite
>> setting possible (custom): how many seconds AFTER the UPS goes battery,
>> should it switch off. This is quite illogical, though.
>>
> 
> a fallback option is to use upssched:
> 
> http://www.networkupstools.org/docs/user-manual.chunked/ar01s07.html
> #_the_advanced_approach_using_upssched
> 
> If you, for example, have 10 mn of runtime, and need 2 mn to shutdown the
> system, then you would declare a (max) 8 mn timer when switching on battery.
> 
> So, I'm afraid a bit doing UPS fullscale test because I don't know, whether
>> servers will have enough time to shutdown before UPS switches itself off. I
>> know I will face it in future, however need more info now.
>>
> 
> your remarks are valid!
> I entered the round lately on this driver, following Eaton acquisition of
> MGE OPS.
> The thing is that, since that time, the various redundant Eaton protocols
> coming from Eaton or MGE (Ie serial XCP Vs SHUT, USB XCP Vs USB/HID, ...)
> have seen some decision: XCP has been superseded by SHUT and HID.
> My main focus has so gone to these, though I've also been putting some
> efforts to improve the XCP driver.
> 
> So, mge-shut and usbhid-ups (Eaton and derivative products) provide support
> for lot more data and features.
> battery.runtime.low is for example supported.
> And R5000 is supported by usbhid-ups through the USB port.
> 
> Otherwise, there are still planned improvement for XCP (and a lot around
> configuration).
> The best would be a driver rewrite, but I've currently not enough resources
> to staff one on this.
> But I think I've identified what should be mapped battery.runtime.low.
> So I you really want to go the XCP way, let me know and I'll check what I
> can do.
> One thing that may help is to tell HP that you want a better NUT support...
> 
> I hope this will shed some light on this, and provide you at least a
> suitable solution.
> 
> cheers,
> Arnaud
> -- 
> Linux / Unix Expert R&D - Eaton - http://powerquality.eaton.com
> Network UPS Tools (NUT) Project Leader - http://www.networkupstools.org/