On Wed, 19 Feb 2014, Jim Klimov wrote: > On 2014-02-19 03:04, Tim Rice wrote: > > Now here are the OIDs (pick one) to actually turn the UPS off > > after the shutdown delay. > > > > # reboot gracefully (APC) (stays off until utility power is restored) > > UPS_OID=".1.3.6.1.4.1.318.1.1.1.6.2.2.0 integer 3" > > # turn off UP gracefully (APC) (stays off even if power is restored) > > #UPS_OID=".1.3.6.1.4.1.318.1.1.1.6.2.1.0 integer 3" > > These seem like config file entries... where do they go? > I don't see UPS_OID in /etc/nut/* (for that 2.6.3 installation)
They go in a custom shutdown script the runs a snmpset command. > Also, just to make sure, the "reboot gracefully" part does indeed > reboot the UPS and its load "instantly" (after the timeout) if the > wall power is already back by the time the UPS goes down due to > this command, right? Correct. > Thanks, > //Jim Klimov -- Tim Rice Multitalents (707) 456-1146 [email protected] _______________________________________________ Nut-upsdev mailing list [email protected] http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsdev