On Tue, 25 Feb 2014, Charles Lepple wrote: | On Feb 19, 2014, at 11:18 AM, Tim Rice wrote: | | > On Wed, 19 Feb 2014, Jim Klimov wrote: | > | >> On 2014-02-19 03:04, Tim Rice wrote: | >>> Now here are the OIDs (pick one) to actually turn the UPS off | >>> after the shutdown delay. | >>> | >>> # reboot gracefully (APC) (stays off until utility power is restored) | >>> UPS_OID=".1.3.6.1.4.1.318.1.1.1.6.2.2.0 integer 3" | | This OID is curiously commented out in drivers/apc-mib.c, and has been | since the beginning of our revision control history. I don't see why we | couldn't add it back in as an instant command. | | I wonder if there was some confusion with .1.3.6.1.4.1.318.1.1.1.6.1.1.0 | (upsBasicControlConserveBattery), which is currently mapped to | "shutdown.return"
Looking at the description in powernet409.mib it seems that upsBasicControlConserveBattery should only be sent by a device not powered by the UPS. (no mention of grace time) The above upsAdvControlRebootShutdownUps seems a better choice. | | >>> # turn off UPS gracefully (APC) (stays off even if power is restored) | >>> #UPS_OID=".1.3.6.1.4.1.318.1.1.1.6.2.1.0 integer 3" | | This should map to the "shutdown.stayoff" instant command. Agreed. -- Tim Rice Multitalents [email protected] _______________________________________________ Nut-upsdev mailing list [email protected] http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsdev