This apparently implies that, unlike some docs say, the snmp-ups driver can 
send the shutdown signals (is not crippled by design)? ;)

Also, are those oids apc-private or commonly used/standard among snmp upses?

Thanks,
//Jim


Typos courtesy of my Samsung Mobile

-------- Исходное сообщение --------
От: Charles Lepple <[email protected]> 
Дата: 2014.02.25  13:08  (GMT+01:00) 
Кому: [email protected] 
Тема: Re: [Nut-upsdev] snmp-ups shutdowns 
 
On Feb 19, 2014, at 11:18 AM, Tim Rice wrote:

> On Wed, 19 Feb 2014, Jim Klimov wrote:
> 
>> On 2014-02-19 03:04, Tim Rice wrote:
>>> Now here are the OIDs (pick one) to actually turn the UPS off
>>> after the shutdown delay.
>>> 
>>> # reboot gracefully (APC) (stays off until utility power is restored)
>>> UPS_OID=".1.3.6.1.4.1.318.1.1.1.6.2.2.0 integer 3"

This OID is curiously commented out in drivers/apc-mib.c, and has been since 
the beginning of our revision control history. I don't see why we couldn't add 
it back in as an instant command.

I wonder if there was some confusion with .1.3.6.1.4.1.318.1.1.1.6.1.1.0 
(upsBasicControlConserveBattery), which is currently mapped to "shutdown.return"

>>> # turn off UP gracefully (APC) (stays off even if power is restored)
>>> #UPS_OID=".1.3.6.1.4.1.318.1.1.1.6.2.1.0 integer 3"

This should map to the "shutdown.stayoff" instant command.

-- 
Charles Lepple
clepple@gmail




_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsdev
_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsdev

Reply via email to