> On Jul 2, 2018, at 9:02 AM, [email protected] wrote: > > > > ioctl(12, USBDEVFS_CLAIMINTERFACE, 0xbecf910c) = -1 EBUSY (Resource > > busy) ioctl(12, USBDEVFS_GETDRIVER, 0xbecf9024) = 0 writev(2, [{"Can't > > claim USB device [0463:fff"..., 62}, {NULL, 0}], 2Can't claim USB > > device [0463:ffff]: No such file or directory > > ) = 62 > > exit_group(1) = ? > > +++ exited with 1 +++ > > > > Why? > > did you see this reply? > > https://alioth-lists.debian.net/pipermail/nut-upsuser/2018-July/011147.html > > if that does not change the strace output, how is your OS launching the NUT > driver? Are the startup scripts in a repository somewhere? > > (if you aren't getting replies, you can check if you are subscribed here: > https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser )
I have UPS Eaton 5SC 500. I tested three solutions: 1. swap usbhid-ups -a qnapups with usbhid-ups -a qnapups -k Result: server shutdown UPS not. 2. run upsmon -c fsd Result: server shutdown UPS not. 3. run upscmd -u admin -p 123456 qnapups shutdown.return and next shutdown Result: server shutdown UPS shutdown. After starting the UPS, immediately the UPS is switched on. The UPS was supposed to wait ups.delay.start time and then turned on. I set in rc.local this parameters for UPS: Set with upsrw: ups.delay.shutdown=60 Set with upsrw: ups.delay.start=90 Set with upsrw: ups.start.auto=no Set with upsrw: ups.start.auto=no Set with upsrw: ups.start.battery=no Set with upsrw: ups.start.reboot=no Please do not know how to write some parameters permanently to UPS? Sorry but I'm not working with Mailing lists! Thx Jan. _______________________________________________ Nut-upsuser mailing list [email protected] https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser