Set with upsrw: ups.delay.shutdown=60 is the same as offdelay = 30. 
This time was done correctly by UPS.

Set with upsrw: ups.delay.start=90 is the same as ondelay = 40.
The UPS shut down and reset and forget about the settings.

If I use the program in Win 10 settings in the program from Eaton are stable!?

Jan.
> -----Original Message-----
> From: Nut-upsuser <nut-upsuser-bounces+icingaj=gmail.com@alioth-
> lists.debian.net> On Behalf Of Roger Price
> Sent: Tuesday, July 3, 2018 4:05 PM
> To: nut-upsuser Mailing List <[email protected]>
> Subject: Re: [Nut-upsuser] No run cmd /usbhid-ups -k !
> 
> On Tue, 3 Jul 2018, [email protected] wrote:
> 
> > UPS is Eaton 5SC 500i.
> > Please do not know how to write some parameters permanently to UPS?
> 
> Read man ups.conf and man usbhid-ups and try setting the required values
> in ups.conf.  For example
> 
> [Eaton]
>          driver = usbhid-ups
>          port = auto
>          desc = "Eaton 5sc 500i"
>          offdelay = 30
>          ondelay = 40
>          lowbatt = 37
> 
> Roger
> 
> _______________________________________________
> Nut-upsuser mailing list
> [email protected]
> https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser