On Dec 1, 2018, at 3:45 PM, raul <[email protected]> wrote:
>
> The UPS is connected to the following environment:
> OS: Debian GNU/Linux 9.6 (stretch)
> NUT version: 2.7.4-5
> Device output from lsusb: 0463:ffff MGE UPS Systems UPS
> Model name: MGE EllipseMAX 1500
> URLs:
> http://powerquality.eaton.com/Products-services/Backup-Power-UPS/Ellipse-MAX-eol.aspx?cx=97&GUID=7BB6CD53-9F6D-4D62-B326-1099F137BF8D
> http://powerquality.eaton.com/68558.aspx?cx=97
>
> The problem is that at some point, after being online for a while, the UPS
> shuts down, cutting the power of all devices without sending any command. The
> log of the master monitor registers a USB error before the events of the OS
> booting process after turning on again the UPS. I have attached the output
>
> Dec 1 21:35:18 openmediavault kernel: [19503.643123] usb 3-2: usbfs:
> USBDEVFS_CONTROL failed cmd usbhid-ups rqt 161 rq 1 len 6 ret -110
> Dec 1 21:35:26 openmediavault kernel: [19511.835644] usb 3-2: usbfs:
> USBDEVFS_CONTROL failed cmd usbhid-ups rqt 161 rq 1 len 5 ret -110
"ret -110" is a timeout, and on other MGE models, I see those sporadically
throughout the day. Those might even correspond to the "libusb_get_interrupt:
Connection timed out" lines in the debug log.
If there is no message to NUT, I would consider opening a trouble ticket with
Eaton. It is possible that there is a known issue and/or a firmware upgrade.
Also, given that the load is only 12%, double-check that the UPS is not
configured for any power saving features that might cause the shutdown ("ECO
mode" or similar). NUT does not get a notification for that event the way that
it gets a normal LB shutdown notification.
--
Charles Lepple
clepple@gmail
_______________________________________________
Nut-upsuser mailing list
[email protected]
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser