On Dec 1, 2018, at 10:08 PM, raul <[email protected]> wrote:
> 
>> Also, given that the load is only 12%, double-check that the UPS is not 
>> configured for any power saving features that might cause the shutdown ("ECO 
>> mode" or similar). NUT does not get a notification for that event the way 
>> that it gets a normal LB shutdown notification.
> 
> Are you referring to NUT (ups.conf) or to the UPS itself? I have checked the 
> instruction manual and it says nothing about ECO modes. It talks only about 
> disabling alarms or changing sensitivity to source voltage variations.
> 
I was referring to a setting on the UPS (which NUT can change). It would look 
like this in the upsc output, so I don't think you have it:

outlet.1.autoswitch.charge.low: 0