On Dec 15, 2018, at 10:32 PM, James <[email protected]> wrote:
> 
> My UPS has an LCD that says the battery is 100% and the estimated run time is 
> 12min.
> The uspc has similar results.
> The problem is when line power is lost the UPS batter goes to 0% very quickly 
> (seconds).
> 
> It charged to 85% when power was restored.
> 86-100% is slower.

It is common for an UPS to have different phases of charging, with the charging 
current tapering off at the end.

> 
> I did:
> $ upscmd desktop_ups test.battery.start.deep
> Username (admin):
> Password:
> OK
> 
> Now the ups.test.result says there is a warning.
> I suspect this will tell me the error.
> 
> $ upsc desktop_ups ups.test.result
> Done and warning
> 
> How do I get more details about the result?
> Surely there must be more.

Which driver is this?

It is possible that there is more information that hasn't been mapped to a NUT 
variable in upsc, but there really isn't a lot of other standard information to 
convey. Some UPSes will report a status that we map to the "RB" (replace 
battery) flag in ups.status.

> Are the symptoms consistent with a failed battery?
> It is old.

Lead-acid batteries are good for about 2-5 years in an UPS.
> 
> _______________________________________________
> Nut-upsuser mailing list
> [email protected]
> https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser


_______________________________________________
Nut-upsuser mailing list
[email protected]
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser