On Dec 16, 2018, at 6:07 PM, James <[email protected]> wrote:
>> Which driver is this?
>
...
> device.mfr: CPS
> device.model: UPS CP850AVRLCD
> device.type: ups
> driver.name: usbhid-ups
For a USB HID PDC (Power Device Class) UPS like this, "ups.test.result" comes
straight from the spec:
https://github.com/networkupstools/nut/blob/v2.7.4/drivers/usbhid-ups.c#L383-L392
<https://github.com/networkupstools/nut/blob/v2.7.4/drivers/usbhid-ups.c#L383-L392>
https://www.usb.org/document-library/power-device-class-document-10
<https://www.usb.org/document-library/power-device-class-document-10> page 26
It is possible to check around for other status bits, but if they are
non-standard, mapping them back to useful names might be difficult.
I think it would be useful to have a debug dump from before and after replacing
the battery, if you have the time. Basically, you can kill the driver out from
under NUT ("killall usbhid-ups" as root), then restart it with "-DDD". If your
system uses paths similar to Debian/Ubuntu, it will be something like this:
# /lib/nut/usbhid-ups -a desktop_ups -DDD 2>&1 | tee
/tmp/CP850AVRLCD.debug.old-battery.txt
Let it run for a few seconds, and once it starts looping, you can kill it with
Ctrl-C. If the log is larger than a few kB, please gzip it before sending.
You can start the driver again with "/lib/nut/usbhid-ups -a desktop_ups", or by
restarting the whole NUT service if things are not looking right._______________________________________________