On 2018-12-16 8:04 a.m., Charles Lepple wrote:
On Dec 15, 2018, at 10:32 PM, James <[email protected]> wrote:
My UPS has an LCD that says the battery is 100% and the estimated run time is
12min.
The uspc has similar results.
The problem is when line power is lost the UPS batter goes to 0% very quickly
(seconds).
It charged to 85% when power was restored.
86-100% is slower.
It is common for an UPS to have different phases of charging, with the charging
current tapering off at the end.
I did:
$ upscmd desktop_ups test.battery.start.deep
Username (admin):
Password:
OK
Now the ups.test.result says there is a warning.
I suspect this will tell me the error.
$ upsc desktop_ups ups.test.result
Done and warning
How do I get more details about the result?
Surely there must be more.
Which driver is this?
$ upsc desktop_ups
Init SSL without certificate database
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 20
battery.mfr.date: CPS
battery.runtime: 1230
battery.runtime.low: 300
battery.type: PbAcid
battery.voltage: 13.5
battery.voltage.nominal: 12
device.mfr: CPS
device.model: UPS CP850AVRLCD
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.synchronous: no
driver.version: 2.7.4
driver.version.data: CyberPower HID 0.4
driver.version.internal: 0.41
input.transfer.high: 140
input.transfer.low: 90
input.voltage: 119.0
input.voltage.nominal: 120
output.voltage: 119.0
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 27
ups.mfr: CPS
ups.model: UPS CP850AVRLCD
ups.productid: 0501
ups.realpower.nominal: 510
ups.status: OL
ups.test.result: Done and warning
ups.timer.shutdown: -60
ups.timer.start: 0
ups.vendorid: 0764