On Fri, Sep 11, 2020, at 4:05 PM, Bartosz wrote:
> Dear All,
> 
> Could you please recommend me a UPS with 100% support of the ondelay 
> parameter and NUT compatibility?
> 
> 850 or 1000 VA
> 
> I have the EATON 5E850iUSBDIN UPS and it does not support this parameter so I 
> would like to buy another UPS that for sure will support it.
> 
> Thank you, 
> Bart

Can you tell from this output? If not, what should I be looking for to answer 
your question?

[dan@slocum:~] $ upsc ups02
battery.capacity: 9.00
battery.charge: 100
battery.charge.low: 20
battery.charge.restart: 0
battery.charger.status: resting
battery.energysave: no
battery.protection: yes
battery.runtime: 1941
battery.type: PbAc
device.mfr: EATON
device.model: Eaton 5PX 2200
device.serial: G091C30079
device.type: ups
driver.name: dummy-ups
driver.parameter.mode: repeater
driver.parameter.pollinterval: 2
driver.parameter.port: [email protected]
driver.parameter.synchronous: no
driver.version: 2.7.4
driver.version.internal: 0.14
input.current: 0.00
input.frequency: 59.9
input.frequency.extended: no
input.frequency.nominal: 60
input.sensitivity: normal
input.transfer.boost.low: 102
input.transfer.high: 151
input.transfer.low: 89
input.transfer.trim.high: 132
input.voltage: 116.7
input.voltage.extended: no
input.voltage.nominal: 120
outlet.1.autoswitch.charge.low: 0
outlet.1.current: 3.70
outlet.1.delay.shutdown: 65535
outlet.1.delay.start: 3
outlet.1.desc: PowerShare Outlet 1
outlet.1.id: 1
outlet.1.power: 432
outlet.1.powerfactor: 94.00
outlet.1.realpower: 410
outlet.1.status: on
outlet.1.switchable: yes
outlet.2.autoswitch.charge.low: 0
outlet.2.current: 5.50
outlet.2.delay.shutdown: 65535
outlet.2.delay.start: 6
outlet.2.desc: PowerShare Outlet 2
outlet.2.id: 2
outlet.2.power: 630
outlet.2.powerfactor: 97.00
outlet.2.realpower: 616
outlet.2.status: on
outlet.2.switchable: yes
outlet.current: 0.00
outlet.desc: Main Outlet
outlet.id: 0
outlet.power: 0
outlet.powerfactor: 0.00
outlet.realpower: 0
outlet.switchable: no
output.current: 9.10
output.frequency: 59.9
output.frequency.nominal: 60
output.powerfactor: 0.96
output.voltage: 116.7
output.voltage.nominal: 120
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.efficiency: 97
ups.firmware: 06
ups.load: 52
ups.load.high: 105
ups.mfr: EATON
ups.model: Eaton 5PX 2200
ups.power: 1062
ups.power.nominal: 2200
ups.productid: ffff
ups.realpower: 1030
ups.realpower.nominal: 1980
ups.serial: G091C30079
ups.shutdown: enabled
ups.start.auto: yes
ups.start.battery: yes
ups.start.reboot: yes
ups.status: OL
ups.test.interval: 604800
ups.test.result: Done and passed
ups.timer.shutdown: 0
ups.timer.start: 0
ups.type: offline / line interactive
ups.vendorid: 0463

--
  Dan Langille
  [email protected]

_______________________________________________
Nut-upsuser mailing list
[email protected]
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to