I'm going to guess that since your test runtime of 305 is very close to the low
limit of 300, that's the warning. Not yet a fail, but very, very close.
On October 31, 2020 11:41:39 AM CDT, Rick Dicaire <[email protected]> wrote:
>Hi folks, new to list...
>nut 2.7.2 on Ubuntu 16.04 with Cyberpowersystems CP1350PFCLCD.
>
>After performing upscmd cp1350@localhost test.battery.start.quick the
>result was "Done and warning". I searched through syslog but could find no
>additional information.
>
>What is the warning?
>
>Battery charge was 100% before test was performed.
>Here's the full output from upsc after test:
>
>battery.charge: 37
>battery.charge.low: 10
>battery.charge.warning: 20
>battery.mfr.date: CPS
>battery.runtime: 305
>battery.runtime.low: 300
>battery.type: PbAcid
>battery.voltage: 16.0
>battery.voltage.nominal: 24
>device.mfr: CP1350PFCLCD
>device.model: CRCA102\#BJ1
>device.serial: CPS
>device.type: ups
>driver.name: usbhid-ups
>driver.parameter.pollfreq: 30
>driver.parameter.pollinterval: 10
>driver.parameter.port: auto
>driver.parameter.vendorid: 0764
>driver.version: 2.7.2
>driver.version.data: CyberPower HID 0.3
>driver.version.internal: 0.38
>input.transfer.high: 139
>input.transfer.low: 88
>input.voltage: 122.0
>input.voltage.nominal: 120
>output.voltage: 138.0
>ups.beeper.status: disabled
>ups.delay.shutdown: 20
>ups.delay.start: 30
>ups.load: 36
>ups.mfr: CP1350PFCLCD
>ups.model: CRCA102#BJ1
>ups.productid: 0501
>ups.realpower.nominal: 810
>ups.serial: CPS
>ups.status: OL CHRG LB
>ups.test.result: Done and warning
>ups.timer.shutdown: -60
>ups.timer.start: -60
>ups.vendorid: 0764
>
>Thanks
--
Sent from my Android device with K-9 Mail. Please excuse my brevity.
_______________________________________________
Nut-upsuser mailing list
[email protected]
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser