On Saturday 31 October 2020 20:13:48 Rick Dicaire wrote:

> On Sat, Oct 31, 2020 at 2:42 PM Tim Dawson <[email protected]> wrote:
> > I'm going to guess that since your test runtime of 305 is very close
> > to the low limit of 300, that's the warning. Not yet a fail, but
> > very, very close.
>
> I tried setting
> override.battery.runtime.low = 60
> in ups.conf, and waited for the UPS to reach 100% charge, and
> ups.status to report only OL.
>
> I initiated another test.battery.start.quick.
> Same kind of result:
>
> battery.charge: 31
> battery.charge.low: 10
> battery.charge.warning: 20
> battery.mfr.date: CPS
> battery.runtime: 255
> battery.runtime.low: 60
> battery.type: PbAcid
> battery.voltage: 16.0
At that voltage, 5 of the 12 cells are shorted
> battery.voltage.nominal: 24
> device.mfr: CP1350PFCLCD
> device.model: CRCA102\#BJ1
> device.serial: CPS
> device.type: ups
> driver.name: usbhid-ups
> driver.parameter.pollfreq: 30
> driver.parameter.pollinterval: 5
> driver.parameter.port: auto
> driver.parameter.vendorid: 0764
> driver.version: 2.7.2
> driver.version.data: CyberPower HID 0.3
> driver.version.internal: 0.38
> input.transfer.high: 139
> input.transfer.low: 88
> input.voltage: 122.0
> input.voltage.nominal: 120
> output.voltage: 138.0
too high by about 15 volts
> ups.beeper.status: disabled
> ups.delay.shutdown: 20
> ups.delay.start: 30
> ups.load: 36
> ups.mfr: CP1350PFCLCD
> ups.model: CRCA102#BJ1
> ups.productid: 0501
> ups.realpower.nominal: 810
> ups.serial: CPS
> ups.status: OL CHRG LB
> ups.test.result: Done and warning
> ups.timer.shutdown: -60
> ups.timer.start: -60
> ups.vendorid: 0764
>
> I'm trying to determine if I need to replace the batteries/device, its
> out of warranty at this rate anyway.
> Any more ideas?

Wow!  That battery is beyond toasted, shoulda been replaced months ago. 
And the output voltage is a bit much if its truthfull.

Cheers, Gene Heskett
-- 
"There are four boxes to be used in defense of liberty:
 soap, ballot, jury, and ammo. Please use in that order."
-Ed Howdershelt (Author)