On Sat, Oct 31, 2020 at 2:42 PM Tim Dawson <[email protected]> wrote:
> I'm going to guess that since your test runtime of 305 is very close to > the low limit of 300, that's the warning. Not yet a fail, but very, very > close. > I tried setting override.battery.runtime.low = 60 in ups.conf, and waited for the UPS to reach 100% charge, and ups.status to report only OL. I initiated another test.battery.start.quick. Same kind of result: battery.charge: 31 battery.charge.low: 10 battery.charge.warning: 20 battery.mfr.date: CPS battery.runtime: 255 battery.runtime.low: 60 battery.type: PbAcid battery.voltage: 16.0 battery.voltage.nominal: 24 device.mfr: CP1350PFCLCD device.model: CRCA102\#BJ1 device.serial: CPS device.type: ups driver.name: usbhid-ups driver.parameter.pollfreq: 30 driver.parameter.pollinterval: 5 driver.parameter.port: auto driver.parameter.vendorid: 0764 driver.version: 2.7.2 driver.version.data: CyberPower HID 0.3 driver.version.internal: 0.38 input.transfer.high: 139 input.transfer.low: 88 input.voltage: 122.0 input.voltage.nominal: 120 output.voltage: 138.0 ups.beeper.status: disabled ups.delay.shutdown: 20 ups.delay.start: 30 ups.load: 36 ups.mfr: CP1350PFCLCD ups.model: CRCA102#BJ1 ups.productid: 0501 ups.realpower.nominal: 810 ups.serial: CPS ups.status: OL CHRG LB ups.test.result: Done and warning ups.timer.shutdown: -60 ups.timer.start: -60 ups.vendorid: 0764 I'm trying to determine if I need to replace the batteries/device, its out of warranty at this rate anyway. Any more ideas?