Hi! Thank You!
The UPS behavior are chages with NUT v.2.8.2 but more strange
After this command (if power cord unpluged)
/usr/local/ups/bin/usbhid-ups -DDDD -a UPS -k
....
0.188173 [D4] string_to_path: depth = 3
0.188187 [D4] string_to_path: depth = 3
0.188199 [D4] string_to_path: depth = 3
0.188211 [D4] string_to_path: depth = 3
0.188246 [D2] find_nut_info: unknown info type: load.off.delay
0.188267 [D2] find_nut_info: unknown info type: load.off.delay
0.188280 Initiating UPS shutdown
0.188290 [D1] upsdrv_shutdown...
0.188298 [D1] instcmd(shutdown.return, [NULL])
0.188316 [D3] instcmd: using Path
'UPS.PowerSummary.DelayBeforeShutdown'
0.188332 [D3] powercom_shutdown_nuf: value = (null), command = 5E00
0.224970 [D3] Report[set]: (3 bytes) => 0f 00 5e
0.225003 [D4] Set report succeeded
0.225012 [D3] instcmd: SUCCEED
The UPS are start double beeping every 2 seconds, but didn't turn off
himself ( 2 minutes wait )
UPS are still beeping if power are restored
Status are:
# upsc ups@localhost
battery.charge: 100
battery.charge.low: 70
battery.charge.warning: 30
battery.mfr.date: 2014/01/15
battery.runtime: 800
battery.type: PbAc
device.mfr: POWERCOM Co.,LTD
device.model: HID UPS Battery
device.serial: 004-0D9F-000
device.type: ups
driver.debug: 0
driver.flag.allow_killpower: 0
driver.flag.ignorelb: enabled
driver.name: usbhid-ups
driver.parameter.offdelay: 30
driver.parameter.ondelay: 60
driver.parameter.override.battery.charge.low: 70
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.productid: 0004
driver.parameter.synchronous: auto
driver.parameter.vendorid: 0d9f
driver.state: quiet
driver.version: 2.8.2
driver.version.data: PowerCOM HID 0.7
driver.version.internal: 0.53
driver.version.usb: libusb-1.0.26 (API: 0x1000109)
input.frequency: 50.0
input.voltage: 224.0
input.voltage.nominal: 220
output.frequency: 50.0
output.voltage: 224.0
output.voltage.nominal: 220
ups.beeper.status: enabled
ups.date: 2014/01/15
ups.delay.shutdown: 30
ups.delay.start: 60
ups.load: 1
ups.mfr: POWERCOM Co.,LTD
ups.model: HID UPS Battery
ups.productid: 0004
ups.serial: 004-0D9F-000
ups.status: OL
ups.test.result: Done and passed
ups.timer.shutdown: 269
ups.timer.start: 0
ups.vendorid: 0d9f
root@vTEMPLATE8:/var/log# upsc ups@localhost
battery.charge: 100
battery.charge.low: 70
battery.charge.warning: 30
battery.mfr.date: 2014/01/15
battery.runtime: 800
battery.type: PbAc
device.mfr: POWERCOM Co.,LTD
device.model: HID UPS Battery
device.serial: 004-0D9F-000
device.type: ups
driver.debug: 0
driver.flag.allow_killpower: 0
driver.flag.ignorelb: enabled
driver.name: usbhid-ups
driver.parameter.offdelay: 30
driver.parameter.ondelay: 60
driver.parameter.override.battery.charge.low: 70
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.productid: 0004
driver.parameter.synchronous: auto
driver.parameter.vendorid: 0d9f
driver.state: quiet
driver.version: 2.8.2
driver.version.data: PowerCOM HID 0.7
driver.version.internal: 0.53
driver.version.usb: libusb-1.0.26 (API: 0x1000109)
input.frequency: 50.0
input.voltage: 224.0
input.voltage.nominal: 220
output.frequency: 50.0
output.voltage: 224.0
output.voltage.nominal: 220
ups.beeper.status: enabled
ups.date: 2014/01/15
ups.delay.shutdown: 30
ups.delay.start: 60
ups.load: 1
ups.mfr: POWERCOM Co.,LTD
ups.model: HID UPS Battery
ups.productid: 0004
ups.serial: 004-0D9F-000
ups.status: OL
ups.test.result: Done and passed
ups.timer.shutdown: 89
ups.timer.start: 0
ups.vendorid: 0d9f
root@vTEMPLATE8:/var/log# upsc ups@localhost
battery.charge: 100
battery.charge.low: 70
battery.charge.warning: 30
battery.mfr.date: 2014/01/15
battery.runtime: 800
battery.type: PbAc
device.mfr: POWERCOM Co.,LTD
device.model: HID UPS Battery
device.serial: 004-0D9F-000
device.type: ups
driver.debug: 0
driver.flag.allow_killpower: 0
driver.flag.ignorelb: enabled
driver.name: usbhid-ups
driver.parameter.offdelay: 30
driver.parameter.ondelay: 60
driver.parameter.override.battery.charge.low: 70
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.productid: 0004
driver.parameter.synchronous: auto
driver.parameter.vendorid: 0d9f
driver.state: quiet
driver.version: 2.8.2
driver.version.data: PowerCOM HID 0.7
driver.version.internal: 0.53
driver.version.usb: libusb-1.0.26 (API: 0x1000109)
input.frequency: 50.0
input.voltage: 226.0
input.voltage.nominal: 220
output.frequency: 50.0
output.voltage: 226.0
output.voltage.nominal: 220
ups.beeper.status: enabled
ups.date: 2014/01/15
ups.delay.shutdown: 30
ups.delay.start: 60
ups.load: 1
ups.mfr: POWERCOM Co.,LTD
ups.model: HID UPS Battery
ups.productid: 0004
ups.serial: 004-0D9F-000
ups.status: OL
ups.test.result: Done and passed
ups.timer.shutdown: 3148
ups.timer.start: 0
ups.vendorid: 0d9f
And strange with timer parametr that are changes cycling:
ups.timer.shutdown: 3570
ups.timer.shutdown: 2430
ups.timer.shutdown: 1710
...
ups.timer.shutdown: 870
ups.timer.shutdown: 3629
ups.timer.shutdown: 2729
ups.timer.shutdown: 1829
...
ups.timer.shutdown: 89
ups.timer.shutdown: 3148
...
the ups.conf are:
[UPS]
driver = usbhid-ups
vendorid = 0d9f
productid = 0004
# powercom_sdcmd_byte_order_fallback
port = auto
# pollonly = enabled
pollinterval = 2
pollfreq = 30
offdelay = 30
ondelay = 60
allow_killpower
ignorelb
override.battery.charge.low = 70
# override.battery.runtime.low = 600
06.05.2025 01:49, Jim Klimov:
At least the "shutdown.return requires a parameter" part *may* be a
regression of the new "sdcommands" change in v2.8.3,though I don't
think older code passed any. Maybe something got lost in mass-edit
changes though.
Can you please double-check with 2.8.2 if its older approach to UPS
shutdown behaved better?
Jim Klimov
On Tue, May 6, 2025, 00:41 Alexey Korobeinikov <[email protected]>
wrote:
Hi, my UPS Model Powercom BNT400AP ( made 2017.12 ) on Linux Devuan
Daedalus and NUT v2.8.3 (install from source tarball with "configure
--with-usb --with-user=nut --with-group=nut --with-libusb=1.0
--with-statepath=/run/nut --with-pidpath=/run/nut" options) didn't
shutdown itself after OS is shuting down by signal of UPS battary
is low.
...
0.184242 Initiating UPS [UPS] shutdown
0.184257 [D1] loop_shutdown_commands: call
do_loop_shutdown_commands() with driver-default sdcommands
0.184267 [D1] Starting
do_loop_shutdown_commands(shudown.default), call depth 1...
0.184280 [D1] upsdrv_shutdown...
0.184289 [D1] Starting
do_loop_shutdown_commands(shutdown.return,shutdown.reboot,load.off.delay,shutdown.stayoff),
call depth 2...
0.184299 [D1] instcmd(shutdown.return, [NULL])
0.184313 [D3] instcmd: using Path
'UPS.PowerSummary.DelayBeforehutdown'
0.184321 [D2] instcmd: shutdown.return requires an explicit
parameter
0.184331 [D1] instcmd(shutdown.reboot, [NULL])
0.184348 [D2] find_nut_info: unknown info type: shutdown.reboot
0.184358 [D3] instcmd: cmdname 'shutdown.reboot' not found;
checking for alternatives
0.184371 [D2] instcmd: info element unavailable shutdown.reboot
0.184387 [D1] instcmd(load.off.delay, [NULL])
0.184398 [D2] find_nut_info: unknown info type: load.off.delay
0.184407 [D3] instcmd: cmdname 'load.off.delay' not found;
checking for alternatives
0.184418 [D2] instcmd: info element unavailable load.off.delay
0.184428 [D1] instcmd(shutdown.stayoff, [NULL])
0.184438 [D3] instcmd: using Path
'UPS.PowerSummary.DelayBeforehutdown'
0.184449 [D2] instcmd: shutdown.stayoff requires an explicit
parameter
0.184462 [D1] Ending
do_loop_shutdown_commands(shutdown.return,shutdown.reboot,load.off.delay,shutdown.stayoff),
call
depth 2: return-code 2
0.184471 Shutdown failed!
0.184483 [D1] set_exit_flag: raising exit flag due to signal -1
0.184493 [D1] do_loop_shutdown_commands(): command
'shutdown.default' was handled successfully
0.184502 [D1] Ending
do_loop_shutdown_commands(shutdown.default),
call depth 1: return-code 0
0.184512 UPS [UPS]: shutdown request was successful with
'shutdown.default'
0.184523 [D1] set_exit_flag: raising exit flag due to
programmatic abort: EXIT_FAILURE
0.184540 [D1] upsdrv_cleanup...
0.184899 [D1] upsnotify: failed to notify about state
NOTIFY_STATE_STOPPING: no notification tech defined, will not spam
more about it
0.184936 [D1] On systems without service units, consider
`export
NUT_QUIET_INIT_UPSNOTIFY=true`
I try to use "powercom_sdcmd_byte_order_fallback" option, with
same effect.
Wat's wrong with my UPS/NUT ?
Thank You!
--
Oleksii Korobeinikov
_______________________________________________
Nut-upsuser mailing list
[email protected]
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
--
З Повагою
Коробейніков Олексій
Системний адміністратор
ТОВ "Флагман Сіфуд"
вул. Броварська 152, смт Велика Димерка
Київська область, 07442
р.+38 044 495-88-00
вн.6101
м.+38 067 994-40-48
_______________________________________________
Nut-upsuser mailing list
[email protected]
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser