I downlod this:
https://github.com/networkupstools/nut
Code->Download ZIP.


15.05.2025 16:17, Jim Klimov:
Seems you did not build the PR source branch, usbhid-ups version there should be 0.64.

Jim

On Thu, May 15, 2025, 13:04 Alexey Korobeinikov <[email protected]> wrote:

    After reseting usb (usbreset 0d9f:0004), I can connect to UPS. But
    still have problem to shuting down the UPS:

    /usr/local/ups/bin/usbhid-ups -DDDD -a UPS -k
    Network UPS Tools 2.8.3.1 (development iteration after 2.8.3) -
    Generic HID driver 0.63
    USB communication driver (libusb 1.0) 0.50
      0.000000     [D1] upsdrv_makevartable...
      0.000078     [D1] Using USB implementation: libusb-1.0.26 (API:
    0x01000109)
      0.000238     [D3] main_arg: var='driver' val='usbhid-ups'
      0.000253     [D3] main_arg: var='vendorid' val='0d9f'
      0.000272     [D3] main_arg: var='productid' val='0004'
      0.000289     [D3] main_arg: var='port' val='auto'
      0.000310     [D3] main_arg: var='pollinterval' val='2'
    ...
      0.004914     [D2] Checking device 4 of 10 (0D9F/0004)
      0.019235     [D2] - VendorID: 0d9f
      0.019276     [D2] - ProductID: 0004
      0.019282     [D2] - Manufacturer: POWERCOM Co.,LTD
      0.019288     [D2] - Product: HID UPS Battery
      0.019293     [D2] - Serial Number: 004-0D9F-000
      0.019298     [D2] - Bus: 006
      0.019303     [D2] - Bus Port: 002
      0.019308     [D2] - Device: 003
      0.019313     [D2] - Device release number: 0002
      0.019318     [D2] Trying to match device
      0.019327     [D2] match_function_subdriver (non-SHUT mode):
    matching a device...
      0.019347     [D3] match_function_regex: matching a device...
      0.019420     [D2] Device matches
      0.019438     [D2] Reading configuration descriptor 1 of 1
      0.019479     [D3] libusb_kernel_driver_active() returned 0: Success
      0.019516     [D2] Claimed interface 0 successfully
      0.019533     [D3] nut_libusb_set_altinterface: skipped
    libusb_set_interface_alt_setting(udev, 0, 0)
      0.021265     [D2] Retrieved HID descriptor (expected 9, got 9)
      0.021306     [D3] HID descriptor, method 1: (9 bytes) => 09 21
    00 01 00 01 22 e4 03
      0.021314     [D3] HID descriptor length (method 1) 996
      0.021330     [D4] i=0, extra[i]=09, extra[i+1]=21
      0.021344     [D3] HID descriptor, method 2: (9 bytes) => 09 21
    00 01 00 01 22 e4 03
      0.021369     [D3] HID descriptor length (method 2) 996
      0.021381     [D2] HID descriptor length 996
      0.062245     [D2] Report Descriptor size = 996
      0.062294     [D3] Report Descriptor: (996 bytes) => 05 84 09 04
    a1 01 09 24 a1 02 85 01 09 fe
      0.062308     [D3]  79 01 75 08 95 01 15 00 26 ff 00 b1 22 85 02
    09 ff 79 02 b1 22 05 85 85 05
      0.062322     [D3]  09 89 79 04 b1 22 85 07 09 8b b1 22 85 08 09
    2c 25 03 b1 22 85 09 09 83 25
      0.062335     [D3]  64 b1 22 09 67 b1 22 85 0e 09 66 81 22 09 66
    b1 a2 85 0b 09 8c b1 22 85 0c
      0.062347     [D3]  09 29 b1 a2 85 0d 09 85 75 10 27 ff ff 00 00
    b1 a2 85 37 09 68 81 22 09 68
      0.062363     [D3]  b1 a2 05 84 85 0f 09 57 75 10 16 00 00 27 ff
    ff 00 00 b1 a2 85 10 09 56 75
      0.062380     [D3]  20 16 00 00 27 9f 86 01 00 b1 a2 85 11 09 40
    75 10 16 64 00 26 f0 00 b1 22
      0.062395     [D3]  85 12 09 30 75 10 16 00 00 26 40 01 b1 a2 85
    2c 09 36 75 08 25 5a b1 a2 85
      0.062410     [D3]  13 09 5a 75 08 15 00 25 03 b1 a2 09 02 a1 02
    05 85 85 0a 09 44 75 01 15 00
      0.062437     [D3]  25 01 81 a2 09 44 b1 a2 09 45 81 a2 09 45 b1
    a2 09 d0 81 a2 09 d0 b1 a2 09
      0.062455     [D3]  d1 81 a2 09 d1 b1 a2 09 42 81 a2 09 42 b1 a2
    09 43 81 a2 09 43 b1 a2 09 4b
      0.062474     [D3]  81 a2 09 4b b1 a2 09 db 81 a2 09 db b1 a2 05
    84 09 68 81 a2 09 68 b1 a2 09
      0.062491     [D3]  69 81 a2 09 69 b1 a2 09 73 81 a2 09 73 b1 a2
    09 65 81 a2 09 65 b1 a2 95 03
      0.062510     [D3]  81 01 b1 01 95 01 06 86 ff 09 80 81 a2 09 80
    b1 a2 c0 c0 05 84 09 12 a1 00
      0.062526     [D3]  85 15 09 58 75 08 25 66 b1 a2 85 16 09 70 75
    08 25 03 b1 a2 05 85 85 17 09
      0.062544     [D3]  85 75 10 27 ff ff 00 00 b1 a2 85 18 09 66 75
    08 15 00 25 64 b1 a2 05 84 85
      0.062559     [D3]  19 09 40 75 10 16 00 0c 26 00 30 b1 22 85 1a
    09 30 75 10 16 00 09 26 00 24
      0.062577     [D3]  b1 a2 85 1b 09 56 75 20 16 00 00 27 9f 86 01
    00 b1 a2 85 2d 09 36 75 08 25
      0.062594     [D3]  5a b1 a2 c0 05 84 09 1a a1 00 85 1c 09 40 75
    10 16 64 00 26 f0 00 b1 22 85
      0.062612     [D3]  1d 09 30 75 10 16 00 00 26 40 01 b1 a2 85 2e
    09 30 75 10 16 00 00 26 40 01
      0.062627     [D3]  b1 a2 85 1e 09 32 75 08 15 00 25 46 b1 a2 c0
    05 84 09 1c a1 00 85 2f 09 41
      0.062645     [D3]  75 08 15 01 25 0c b1 22 85 1f 09 35 75 08 15
    00 25 64 b1 a2 85 20 09 40 75
      0.062664     [D3]  10 16 64 00 26 f0 00 b1 22 85 21 09 30 75 10
    16 00 00 26 40 01 b1 a2 85 30
      0.062681     [D3]  09 42 75 08 15 32 25 3c b1 22 85 22 09 32 75
    08 15 00 25 46 b1 a2 85 23 09
      0.062699     [D3]  57 75 08 15 00 25 12 b1 a2 85 24 09 56 75 20
    16 00 00 27 9f 86 01 00 b1 a2
      0.062716     [D3]  c0 05 84 85 06 09 01 79 05 b1 a2 85 25 09 5a
    75 08 15 00 25 03 b1 a2 09 02
      0.062736     [D3]  a1 02 05 85 85 26 09 44 75 01 15 00 25 01 b1
    a2 09 45 b1 a2 09 d0 b1 a2 09
      0.062752     [D3]  d1 b1 a2 09 42 b1 a2 09 43 b1 a2 09 4b b1 a2
    09 db b1 a2 05 84 09 68 b1 a2
      0.062768     [D3]  09 69 b1 a2 09 73 b1 a2 09 65 b1 a2 09 6e b1
    a2 09 6f b1 a2 09 71 b1 a2 06
      0.062791     [D3]  86 ff 09 80 b1 a2 c0 85 27 05 84 09 69 75 08
    15 00 25 01 b1 a2 09 1e a1 00
      0.062807     [D3]  85 a0 09 01 75 08 95 07 15 00 26 ff 00 b1 03
    85 a1 09 01 75 08 95 07 15 00
      0.062835     [D3]  26 ff 00 b1 03 85 a2 09 01 75 08 95 07 15 00
    26 ff 00 b1 03 85 a3 09 01 75
      0.062853     [D3]  08 95 07 15 00 26 ff 00 b1 03 85 a4 09 01 75
    08 95 07 15 00 26 ff 00 b1 03
      0.062871     [D3]  85 a5 09 01 75 08 95 07 15 00 26 ff 00 b1 03
    85 a6 09 01 75 08 95 07 15 00
      0.062889     [D3]  26 ff 00 b1 03 85 a7 09 01 75 08 95 07 15 00
    26 ff 00 b1 03 85 a8 09 01 75
      0.062905     [D3]  08 95 07 15 00 26 ff 00 b1 03 85 a9 09 01 75
    08 95 07 15 00 26 ff 00 b1 03
      0.062923     [D3]  85 aa 09 01 75 08 95 07 15 00 26 ff 00 b1 03
    85 ab 09 01 75 08 95 07 15 00
      0.062940     [D3]  26 ff 00 b1 03 85 ac 09 01 75 08 95 07 15 00
    26 ff 00 b1 03 85 ad 09 01 75
      0.062960     [D3]  08 95 07 15 00 26 ff 00 b1 03 85 ae 09 01 75
    08 95 07 15 00 26 ff 00 b1 03
      0.062977     [D3]  85 31 09 01 75 08 95 01 15 00 26 ff 00 b1 03
    85 32 09 01 75 08 95 01 15 00
      0.062990     [D3]  26 ff 00 b1 03 c0 c0
      0.063197     Using subdriver: PowerCOM HID 0.71
      0.063214     [D1] 102 HID objects found
      0.063229     [D4] Entering libusb_get_report
      0.064157     [D3] Report[get]: (2 bytes) => 01 01
      0.064197     [D1] Path: UPS.PowerSummary.iProduct, Type:
    Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1
      0.064209     [D4] Entering libusb_get_report
      0.066271     [D3] Report[get]: (2 bytes) => 02 02
      0.066311     [D1] Path: UPS.PowerSummary.iSerialNumber, Type:
    Feature, ReportID: 0x02, Offset: 0, Size: 8, Value: 2
      0.066320     [D4] Entering libusb_get_report
    ...
      0.186774     [D4] Entering libusb_get_report
      0.188120     nut_libusb_get_report: Success
      0.188164     [D1] Can't retrieve Report 2d: Success
      0.188182     [D4] string_to_path: depth = 3
      0.188197     [D4] HIDGetItemData: FindObject_with_Path() failed
    to locate 'PowercomUPS.PowercomBatterySystem.PowercomVoltage'
      0.188210     [D4] string_to_path: depth = 4
    ...
      0.188755     Initiating UPS [UPS] shutdown
      0.188770     [D1] loop_shutdown_commands: call
    do_loop_shutdown_commands() with driver-default sdcommands
      0.188780     [D1] Starting
    do_loop_shutdown_commands(shutdown.default), call depth 1...
      0.188791     [D1] upsdrv_shutdown...
      0.188802     [D1] Starting
    
do_loop_shutdown_commands(shutdown.return,shutdown.reboot,load.off.delay,shutdown.stayoff),
    call depth 2...
      0.188813     [D1] instcmd(shutdown.return, [NULL])
      0.188822     [D3] instcmd: using Path
    'UPS.PowerSummary.DelayBeforeShutdown'
      0.188833     [D2] instcmd: shutdown.return requires an explicit
    parameter

      0.188842     [D1] instcmd(shutdown.reboot, [NULL])
      0.188856     [D2] find_nut_info: unknown info type: shutdown.reboot
      0.188866     [D3] instcmd: cmdname 'shutdown.reboot' not found;
    checking for alternatives
      0.188879     [D2] instcmd: info element unavailable shutdown.reboot

      0.188890     [D1] instcmd(load.off.delay, [NULL])
      0.188902     [D2] find_nut_info: unknown info type: load.off.delay
      0.188911     [D3] instcmd: cmdname 'load.off.delay' not found;
    checking for alternatives
      0.188921     [D2] instcmd: info element unavailable load.off.delay

      0.188935     [D1] instcmd(shutdown.stayoff, [NULL])
      0.188945     [D3] instcmd: using Path
    'UPS.PowerSummary.DelayBeforeShutdown'
      0.188956     [D2] instcmd: shutdown.stayoff requires an explicit
    parameter

      0.188966     [D1] Ending
    
do_loop_shutdown_commands(shutdown.return,shutdown.reboot,load.off.delay,shutdown.stayoff),
    call depth 2: return-code 2
      0.188974     Shutdown failed!
      0.188986     [D1] set_exit_flag: raising exit flag due to signal -1
      0.188996     [D1] do_loop_shutdown_commands(): command
    'shutdown.default' was handled successfully
      0.189005     [D1] Ending
    do_loop_shutdown_commands(shutdown.default), call depth 1:
    return-code 0
      0.189014     UPS [UPS]: shutdown request was successful with
    'shutdown.default'
      0.189022     [D1] set_exit_flag: raising exit flag due to
    programmatic abort: EXIT_FAILURE
      0.189040     [D1] upsdrv_cleanup...
      0.189311     [D1] upsnotify: failed to notify about state
    NOTIFY_STATE_STOPPING: no notification tech defined, will not spam
    more about it
      0.189331     [D1] On systems without service units, consider
    `export NUT_QUIET_INIT_UPSNOTIFY=true`

    The UPS didn't  shut down, just still BEEP because on battery ( >3
    min wait )...

    13.05.2025 18:31, Jim Klimov:
    Check https://github.com/networkupstools/nut/pull/2955 please.

    Jim

    On Mon, May 12, 2025 at 12:04 PM Jim Klimov
    <[email protected] <mailto:jimklimov%[email protected]>> wrote:

        Hoped to look into this just today, if nobody beat me to it yet.

        Jim

        On Mon, May 12, 2025 at 11:54 AM Alexey Korobeinikov
        <[email protected]> wrote:

            Are there any chances that this error can be fixed?

            06.05.2025 18:19, Alexey Korobeinikov:
            Hi! Thank You!

            The UPS behavior are chages with NUT v.2.8.2 but more
            strange

            After this command (if power cord unpluged)
            /usr/local/ups/bin/usbhid-ups -DDDD -a UPS -k

            ....
            0.188173     [D4] string_to_path: depth = 3
               0.188187     [D4] string_to_path: depth = 3
               0.188199     [D4] string_to_path: depth = 3
               0.188211     [D4] string_to_path: depth = 3
               0.188246     [D2] find_nut_info: unknown info type:
            load.off.delay
               0.188267     [D2] find_nut_info: unknown info type:
            load.off.delay
               0.188280     Initiating UPS shutdown
               0.188290     [D1] upsdrv_shutdown...
               0.188298     [D1] instcmd(shutdown.return, [NULL])
               0.188316     [D3] instcmd: using Path
            'UPS.PowerSummary.DelayBeforeShutdown'
               0.188332     [D3] powercom_shutdown_nuf: value =
            (null), command = 5E00
               0.224970     [D3] Report[set]: (3 bytes) => 0f 00 5e
               0.225003     [D4] Set report succeeded
               0.225012     [D3] instcmd: SUCCEED

            The UPS are start double beeping every 2 seconds, but
            didn't turn off himself ( 2 minutes wait )
            UPS are still beeping if power are restored

            Status are:
            # upsc ups@localhost
            battery.charge: 100
            battery.charge.low: 70
            battery.charge.warning: 30
            battery.mfr.date: 2014/01/15
            battery.runtime: 800
            battery.type: PbAc
            device.mfr: POWERCOM Co.,LTD
            device.model: HID UPS Battery
            device.serial: 004-0D9F-000
            device.type: ups
            driver.debug: 0
            driver.flag.allow_killpower: 0
            driver.flag.ignorelb: enabled
            driver.name <http://driver.name>: usbhid-ups
            driver.parameter.offdelay: 30
            driver.parameter.ondelay: 60
            driver.parameter.override.battery.charge.low: 70
            driver.parameter.pollfreq: 30
            driver.parameter.pollinterval: 2
            driver.parameter.port: auto
            driver.parameter.productid: 0004
            driver.parameter.synchronous: auto
            driver.parameter.vendorid: 0d9f
            driver.state: quiet
            driver.version: 2.8.2
            driver.version.data: PowerCOM HID 0.7
            driver.version.internal: 0.53
            driver.version.usb: libusb-1.0.26 (API: 0x1000109)
            input.frequency: 50.0
            input.voltage: 224.0
            input.voltage.nominal: 220
            output.frequency: 50.0
            output.voltage: 224.0
            output.voltage.nominal: 220
            ups.beeper.status: enabled
            ups.date: 2014/01/15
            ups.delay.shutdown: 30
            ups.delay.start: 60
            ups.load: 1
            ups.mfr: POWERCOM Co.,LTD
            ups.model: HID UPS Battery
            ups.productid: 0004
            ups.serial: 004-0D9F-000
            ups.status: OL
            ups.test.result: Done and passed
            ups.timer.shutdown: 269
            ups.timer.start: 0
            ups.vendorid: 0d9f
            root@vTEMPLATE8:/var/log# upsc ups@localhost
            battery.charge: 100
            battery.charge.low: 70
            battery.charge.warning: 30
            battery.mfr.date: 2014/01/15
            battery.runtime: 800
            battery.type: PbAc
            device.mfr: POWERCOM Co.,LTD
            device.model: HID UPS Battery
            device.serial: 004-0D9F-000
            device.type: ups
            driver.debug: 0
            driver.flag.allow_killpower: 0
            driver.flag.ignorelb: enabled
            driver.name <http://driver.name>: usbhid-ups
            driver.parameter.offdelay: 30
            driver.parameter.ondelay: 60
            driver.parameter.override.battery.charge.low: 70
            driver.parameter.pollfreq: 30
            driver.parameter.pollinterval: 2
            driver.parameter.port: auto
            driver.parameter.productid: 0004
            driver.parameter.synchronous: auto
            driver.parameter.vendorid: 0d9f
            driver.state: quiet
            driver.version: 2.8.2
            driver.version.data: PowerCOM HID 0.7
            driver.version.internal: 0.53
            driver.version.usb: libusb-1.0.26 (API: 0x1000109)
            input.frequency: 50.0
            input.voltage: 224.0
            input.voltage.nominal: 220
            output.frequency: 50.0
            output.voltage: 224.0
            output.voltage.nominal: 220
            ups.beeper.status: enabled
            ups.date: 2014/01/15
            ups.delay.shutdown: 30
            ups.delay.start: 60
            ups.load: 1
            ups.mfr: POWERCOM Co.,LTD
            ups.model: HID UPS Battery
            ups.productid: 0004
            ups.serial: 004-0D9F-000
            ups.status: OL
            ups.test.result: Done and passed
            ups.timer.shutdown: 89
            ups.timer.start: 0
            ups.vendorid: 0d9f
            root@vTEMPLATE8:/var/log# upsc ups@localhost
            battery.charge: 100
            battery.charge.low: 70
            battery.charge.warning: 30
            battery.mfr.date: 2014/01/15
            battery.runtime: 800
            battery.type: PbAc
            device.mfr: POWERCOM Co.,LTD
            device.model: HID UPS Battery
            device.serial: 004-0D9F-000
            device.type: ups
            driver.debug: 0
            driver.flag.allow_killpower: 0
            driver.flag.ignorelb: enabled
            driver.name <http://driver.name>: usbhid-ups
            driver.parameter.offdelay: 30
            driver.parameter.ondelay: 60
            driver.parameter.override.battery.charge.low: 70
            driver.parameter.pollfreq: 30
            driver.parameter.pollinterval: 2
            driver.parameter.port: auto
            driver.parameter.productid: 0004
            driver.parameter.synchronous: auto
            driver.parameter.vendorid: 0d9f
            driver.state: quiet
            driver.version: 2.8.2
            driver.version.data: PowerCOM HID 0.7
            driver.version.internal: 0.53
            driver.version.usb: libusb-1.0.26 (API: 0x1000109)
            input.frequency: 50.0
            input.voltage: 226.0
            input.voltage.nominal: 220
            output.frequency: 50.0
            output.voltage: 226.0
            output.voltage.nominal: 220
            ups.beeper.status: enabled
            ups.date: 2014/01/15
            ups.delay.shutdown: 30
            ups.delay.start: 60
            ups.load: 1
            ups.mfr: POWERCOM Co.,LTD
            ups.model: HID UPS Battery
            ups.productid: 0004
            ups.serial: 004-0D9F-000
            ups.status: OL
            ups.test.result: Done and passed
            ups.timer.shutdown: 3148
            ups.timer.start: 0
            ups.vendorid: 0d9f

            And strange with timer parametr that are changes cycling:
            ups.timer.shutdown: 3570
            ups.timer.shutdown: 2430
            ups.timer.shutdown: 1710
            ...
            ups.timer.shutdown: 870
            ups.timer.shutdown: 3629
            ups.timer.shutdown: 2729
            ups.timer.shutdown: 1829
            ...
            ups.timer.shutdown: 89
            ups.timer.shutdown: 3148
            ...

            the ups.conf are:
            [UPS]
                driver = usbhid-ups
                vendorid = 0d9f
                productid = 0004
            #    powercom_sdcmd_byte_order_fallback
                port = auto
            #    pollonly = enabled
                pollinterval = 2
                pollfreq = 30
                offdelay = 30
                ondelay = 60
                allow_killpower
                ignorelb
                override.battery.charge.low = 70
            #    override.battery.runtime.low = 600

            06.05.2025 01:49, Jim Klimov:
            At least the "shutdown.return requires a parameter"
            part *may* be a regression of the new "sdcommands"
            change in v2.8.3,though I don't think older code passed
            any. Maybe something got lost in mass-edit changes though.

            Can you please double-check with 2.8.2 if its older
            approach to UPS shutdown behaved better?

            Jim Klimov

            On Tue, May 6, 2025, 00:41 Alexey Korobeinikov
            <[email protected]> wrote:

                Hi, my UPS Model Powercom BNT400AP ( made 2017.12 )
                on Linux Devuan
                Daedalus and NUT v2.8.3 (install from source
                tarball with "configure
                --with-usb --with-user=nut --with-group=nut
                --with-libusb=1.0
                --with-statepath=/run/nut --with-pidpath=/run/nut"
                options) didn't
                shutdown itself after OS is shuting down by signal
                of UPS battary is low.

                ...

                   0.184242     Initiating UPS [UPS] shutdown
                   0.184257     [D1] loop_shutdown_commands: call
                do_loop_shutdown_commands() with driver-default
                sdcommands
                   0.184267     [D1] Starting
                do_loop_shutdown_commands(shudown.default), call
                depth 1...
                   0.184280     [D1] upsdrv_shutdown...
                   0.184289     [D1] Starting
                
do_loop_shutdown_commands(shutdown.return,shutdown.reboot,load.off.delay,shutdown.stayoff),

                call depth 2...
                   0.184299     [D1] instcmd(shutdown.return, [NULL])
                   0.184313     [D3] instcmd: using Path
                'UPS.PowerSummary.DelayBeforehutdown'
                   0.184321     [D2] instcmd: shutdown.return
                requires an explicit
                parameter

                   0.184331     [D1] instcmd(shutdown.reboot, [NULL])
                   0.184348     [D2] find_nut_info: unknown info
                type: shutdown.reboot
                   0.184358     [D3] instcmd: cmdname
                'shutdown.reboot' not found;
                checking for alternatives
                   0.184371     [D2] instcmd: info element
                unavailable shutdown.reboot

                   0.184387     [D1] instcmd(load.off.delay, [NULL])
                   0.184398     [D2] find_nut_info: unknown info
                type: load.off.delay
                   0.184407     [D3] instcmd: cmdname
                'load.off.delay' not found;
                checking for alternatives
                   0.184418     [D2] instcmd: info element
                unavailable load.off.delay

                   0.184428     [D1] instcmd(shutdown.stayoff, [NULL])
                   0.184438     [D3] instcmd: using Path
                'UPS.PowerSummary.DelayBeforehutdown'
                   0.184449     [D2] instcmd: shutdown.stayoff
                requires an explicit
                parameter

                   0.184462     [D1] Ending
                
do_loop_shutdown_commands(shutdown.return,shutdown.reboot,load.off.delay,shutdown.stayoff),

                call
                depth 2: return-code 2
                   0.184471     Shutdown failed!
                   0.184483     [D1] set_exit_flag: raising exit
                flag due to signal -1
                   0.184493     [D1] do_loop_shutdown_commands():
                command
                'shutdown.default' was handled successfully
                   0.184502     [D1] Ending
                do_loop_shutdown_commands(shutdown.default),
                call depth 1: return-code 0
                   0.184512     UPS [UPS]: shutdown request was
                successful with
                'shutdown.default'
                   0.184523     [D1] set_exit_flag: raising exit
                flag due to
                programmatic abort: EXIT_FAILURE
                   0.184540     [D1] upsdrv_cleanup...
                   0.184899     [D1] upsnotify: failed to notify
                about state
                NOTIFY_STATE_STOPPING: no notification tech
                defined, will not spam more about it
                   0.184936     [D1] On systems without service
                units, consider `export
                NUT_QUIET_INIT_UPSNOTIFY=true`

                I try to use "powercom_sdcmd_byte_order_fallback"
                option, with same effect.

                Wat's wrong with my UPS/NUT ?
                Thank You!

-- Oleksii Korobeinikov




                _______________________________________________
                Nut-upsuser mailing list
                [email protected]
                
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser


-- З Повагою
            Коробейніков Олексій
            Системний адміністратор

            ТОВ "Флагман Сіфуд"
            вул. Броварська 152 
<https://www.google.com/maps/search/%D0%B2%D1%83%D0%BB.+%D0%91%D1%80%D0%BE%D0%B2%D0%B0%D1%80%D1%81%D1%8C%D0%BA%D0%B0+152?entry=gmail&source=g>,
 смт Велика Димерка
            Київська область, 07442
            р.+38 044 495-88-00
            вн.6101
            м.+38 067 994-40-48

            _______________________________________________
            Nut-upsuser mailing list
            [email protected]
            https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser

-- З Повагою
            Коробейніков Олексій
            Системний адміністратор

            ТОВ "Флагман Сіфуд"
            вул. Броварська 152 
<https://www.google.com/maps/search/%D0%B2%D1%83%D0%BB.+%D0%91%D1%80%D0%BE%D0%B2%D0%B0%D1%80%D1%81%D1%8C%D0%BA%D0%B0+152?entry=gmail&source=g>,
 смт Велика Димерка
            Київська область, 07442
            р.+38 044 495-88-00
            вн.6101
            м.+38 067 994-40-48


-- З Повагою
    Коробейніков Олексій
    Системний адміністратор

    ТОВ "Флагман Сіфуд"
    вул. Броварська 152 
<https://www.google.com/maps/search/%D0%B2%D1%83%D0%BB.+%D0%91%D1%80%D0%BE%D0%B2%D0%B0%D1%80%D1%81%D1%8C%D0%BA%D0%B0+152?entry=gmail&source=g>,
 смт Велика Димерка
    Київська область, 07442
    р.+38 044 495-88-00
    вн.6101
    м.+38 067 994-40-48


--
З Повагою
Коробейніков Олексій
Системний адміністратор

ТОВ "Флагман Сіфуд"
вул. Броварська 152, смт Велика Димерка
Київська область, 07442
р.+38 044 495-88-00
вн.6101
м.+38 067 994-40-48