How amazing! It's working now!!!(/usr/local/ups/bin/usbhid-ups -DDDD -a UPS -k)
I will test this more deeply.

15.05.2025 17:26, Jim Klimov:
You wanted fixed code, so you should download what was proposed for the PR that may fix or not fix the problem. It was not merged yet.

TBH I've never tried to download archives prepared by GitHub on its own, but assuming from your earlier examples that this way of code delivery is usable, you need to get this:

https://github.com/networkupstools/nut/pull/2955
=> jimklimov <https://github.com/jimklimov> wants to merge 5 commits into networkupstools:master <https://github.com/networkupstools/nut/tree/master>from jimklimov:sdcommands-args <https://github.com/jimklimov/nut/tree/sdcommands-args>
=> https://github.com/jimklimov/nut/tree/sdcommands-args
=> Code => ZIP => https://github.com/jimklimov/nut/archive/refs/heads/sdcommands-args.zip

But why would you not just use git? :)

:; git clone https://github.com/jimklimov/nut -b sdcommands-args
:; cd nut
...

Hope this helps,
Jim Klimov

PS: Inspired by that specific change, a bigger PR was also proposed at https://github.com/networkupstools/nut/pull/2957 to also consistently log the processing of instcmd and setvar operations. Previously all drivers tended to do this differently, which made troubleshooting harder. Now they would all follow the same logic and message structure, at least in broad strokes, and specifically would try to syslog any operations that can impact power delivery to the useful load.


On Thu, May 15, 2025 at 3:44 PM Alexey Korobeinikov <[email protected]> wrote:

    I downlod this:
    https://github.com/networkupstools/nut
    Code->Download ZIP.


    15.05.2025 16:17, Jim Klimov:
    Seems you did not build the PR source branch, usbhid-ups version
    there should be 0.64.

    Jim

    On Thu, May 15, 2025, 13:04 Alexey Korobeinikov
    <[email protected]> wrote:

        After reseting usb (usbreset 0d9f:0004), I can connect to
        UPS. But still have problem to shuting down the UPS:

        /usr/local/ups/bin/usbhid-ups -DDDD -a UPS -k
        Network UPS Tools 2.8.3.1 (development iteration after 2.8.3)
        - Generic HID driver 0.63
        USB communication driver (libusb 1.0) 0.50
          0.000000     [D1] upsdrv_makevartable...
          0.000078     [D1] Using USB implementation: libusb-1.0.26
        (API: 0x01000109)
          0.000238     [D3] main_arg: var='driver' val='usbhid-ups'
          0.000253     [D3] main_arg: var='vendorid' val='0d9f'
          0.000272     [D3] main_arg: var='productid' val='0004'
          0.000289     [D3] main_arg: var='port' val='auto'
          0.000310     [D3] main_arg: var='pollinterval' val='2'
        ...
          0.004914     [D2] Checking device 4 of 10 (0D9F/0004)
          0.019235     [D2] - VendorID: 0d9f
          0.019276     [D2] - ProductID: 0004
          0.019282     [D2] - Manufacturer: POWERCOM Co.,LTD
          0.019288     [D2] - Product: HID UPS Battery
          0.019293     [D2] - Serial Number: 004-0D9F-000
          0.019298     [D2] - Bus: 006
          0.019303     [D2] - Bus Port: 002
          0.019308     [D2] - Device: 003
          0.019313     [D2] - Device release number: 0002
          0.019318     [D2] Trying to match device
          0.019327     [D2] match_function_subdriver (non-SHUT mode):
        matching a device...
          0.019347     [D3] match_function_regex: matching a device...
          0.019420     [D2] Device matches
          0.019438     [D2] Reading configuration descriptor 1 of 1
          0.019479     [D3] libusb_kernel_driver_active() returned 0:
        Success
          0.019516     [D2] Claimed interface 0 successfully
          0.019533     [D3] nut_libusb_set_altinterface: skipped
        libusb_set_interface_alt_setting(udev, 0, 0)
          0.021265     [D2] Retrieved HID descriptor (expected 9, got 9)
          0.021306     [D3] HID descriptor, method 1: (9 bytes) => 09
        21 00 01 00 01 22 e4 03
          0.021314     [D3] HID descriptor length (method 1) 996
          0.021330     [D4] i=0, extra[i]=09, extra[i+1]=21
          0.021344     [D3] HID descriptor, method 2: (9 bytes) => 09
        21 00 01 00 01 22 e4 03
          0.021369     [D3] HID descriptor length (method 2) 996
          0.021381     [D2] HID descriptor length 996
          0.062245     [D2] Report Descriptor size = 996
          0.062294     [D3] Report Descriptor: (996 bytes) => 05 84
        09 04 a1 01 09 24 a1 02 85 01 09 fe
          0.062308     [D3]  79 01 75 08 95 01 15 00 26 ff 00 b1 22
        85 02 09 ff 79 02 b1 22 05 85 85 05
          0.062322     [D3]  09 89 79 04 b1 22 85 07 09 8b b1 22 85
        08 09 2c 25 03 b1 22 85 09 09 83 25
          0.062335     [D3]  64 b1 22 09 67 b1 22 85 0e 09 66 81 22
        09 66 b1 a2 85 0b 09 8c b1 22 85 0c
          0.062347     [D3]  09 29 b1 a2 85 0d 09 85 75 10 27 ff ff
        00 00 b1 a2 85 37 09 68 81 22 09 68
          0.062363     [D3]  b1 a2 05 84 85 0f 09 57 75 10 16 00 00
        27 ff ff 00 00 b1 a2 85 10 09 56 75
          0.062380     [D3]  20 16 00 00 27 9f 86 01 00 b1 a2 85 11
        09 40 75 10 16 64 00 26 f0 00 b1 22
          0.062395     [D3]  85 12 09 30 75 10 16 00 00 26 40 01 b1
        a2 85 2c 09 36 75 08 25 5a b1 a2 85
          0.062410     [D3]  13 09 5a 75 08 15 00 25 03 b1 a2 09 02
        a1 02 05 85 85 0a 09 44 75 01 15 00
          0.062437     [D3]  25 01 81 a2 09 44 b1 a2 09 45 81 a2 09
        45 b1 a2 09 d0 81 a2 09 d0 b1 a2 09
          0.062455     [D3]  d1 81 a2 09 d1 b1 a2 09 42 81 a2 09 42
        b1 a2 09 43 81 a2 09 43 b1 a2 09 4b
          0.062474     [D3]  81 a2 09 4b b1 a2 09 db 81 a2 09 db b1
        a2 05 84 09 68 81 a2 09 68 b1 a2 09
          0.062491     [D3]  69 81 a2 09 69 b1 a2 09 73 81 a2 09 73
        b1 a2 09 65 81 a2 09 65 b1 a2 95 03
          0.062510     [D3]  81 01 b1 01 95 01 06 86 ff 09 80 81 a2
        09 80 b1 a2 c0 c0 05 84 09 12 a1 00
          0.062526     [D3]  85 15 09 58 75 08 25 66 b1 a2 85 16 09
        70 75 08 25 03 b1 a2 05 85 85 17 09
          0.062544     [D3]  85 75 10 27 ff ff 00 00 b1 a2 85 18 09
        66 75 08 15 00 25 64 b1 a2 05 84 85
          0.062559     [D3]  19 09 40 75 10 16 00 0c 26 00 30 b1 22
        85 1a 09 30 75 10 16 00 09 26 00 24
          0.062577     [D3]  b1 a2 85 1b 09 56 75 20 16 00 00 27 9f
        86 01 00 b1 a2 85 2d 09 36 75 08 25
          0.062594     [D3]  5a b1 a2 c0 05 84 09 1a a1 00 85 1c 09
        40 75 10 16 64 00 26 f0 00 b1 22 85
          0.062612     [D3]  1d 09 30 75 10 16 00 00 26 40 01 b1 a2
        85 2e 09 30 75 10 16 00 00 26 40 01
          0.062627     [D3]  b1 a2 85 1e 09 32 75 08 15 00 25 46 b1
        a2 c0 05 84 09 1c a1 00 85 2f 09 41
          0.062645     [D3]  75 08 15 01 25 0c b1 22 85 1f 09 35 75
        08 15 00 25 64 b1 a2 85 20 09 40 75
          0.062664     [D3]  10 16 64 00 26 f0 00 b1 22 85 21 09 30
        75 10 16 00 00 26 40 01 b1 a2 85 30
          0.062681     [D3]  09 42 75 08 15 32 25 3c b1 22 85 22 09
        32 75 08 15 00 25 46 b1 a2 85 23 09
          0.062699     [D3]  57 75 08 15 00 25 12 b1 a2 85 24 09 56
        75 20 16 00 00 27 9f 86 01 00 b1 a2
          0.062716     [D3]  c0 05 84 85 06 09 01 79 05 b1 a2 85 25
        09 5a 75 08 15 00 25 03 b1 a2 09 02
          0.062736     [D3]  a1 02 05 85 85 26 09 44 75 01 15 00 25
        01 b1 a2 09 45 b1 a2 09 d0 b1 a2 09
          0.062752     [D3]  d1 b1 a2 09 42 b1 a2 09 43 b1 a2 09 4b
        b1 a2 09 db b1 a2 05 84 09 68 b1 a2
          0.062768     [D3]  09 69 b1 a2 09 73 b1 a2 09 65 b1 a2 09
        6e b1 a2 09 6f b1 a2 09 71 b1 a2 06
          0.062791     [D3]  86 ff 09 80 b1 a2 c0 85 27 05 84 09 69
        75 08 15 00 25 01 b1 a2 09 1e a1 00
          0.062807     [D3]  85 a0 09 01 75 08 95 07 15 00 26 ff 00
        b1 03 85 a1 09 01 75 08 95 07 15 00
          0.062835     [D3]  26 ff 00 b1 03 85 a2 09 01 75 08 95 07
        15 00 26 ff 00 b1 03 85 a3 09 01 75
          0.062853     [D3]  08 95 07 15 00 26 ff 00 b1 03 85 a4 09
        01 75 08 95 07 15 00 26 ff 00 b1 03
          0.062871     [D3]  85 a5 09 01 75 08 95 07 15 00 26 ff 00
        b1 03 85 a6 09 01 75 08 95 07 15 00
          0.062889     [D3]  26 ff 00 b1 03 85 a7 09 01 75 08 95 07
        15 00 26 ff 00 b1 03 85 a8 09 01 75
          0.062905     [D3]  08 95 07 15 00 26 ff 00 b1 03 85 a9 09
        01 75 08 95 07 15 00 26 ff 00 b1 03
          0.062923     [D3]  85 aa 09 01 75 08 95 07 15 00 26 ff 00
        b1 03 85 ab 09 01 75 08 95 07 15 00
          0.062940     [D3]  26 ff 00 b1 03 85 ac 09 01 75 08 95 07
        15 00 26 ff 00 b1 03 85 ad 09 01 75
          0.062960     [D3]  08 95 07 15 00 26 ff 00 b1 03 85 ae 09
        01 75 08 95 07 15 00 26 ff 00 b1 03
          0.062977     [D3]  85 31 09 01 75 08 95 01 15 00 26 ff 00
        b1 03 85 32 09 01 75 08 95 01 15 00
          0.062990     [D3]  26 ff 00 b1 03 c0 c0
          0.063197     Using subdriver: PowerCOM HID 0.71
          0.063214     [D1] 102 HID objects found
          0.063229     [D4] Entering libusb_get_report
          0.064157     [D3] Report[get]: (2 bytes) => 01 01
          0.064197     [D1] Path: UPS.PowerSummary.iProduct, Type:
        Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1
          0.064209     [D4] Entering libusb_get_report
          0.066271     [D3] Report[get]: (2 bytes) => 02 02
          0.066311     [D1] Path: UPS.PowerSummary.iSerialNumber,
        Type: Feature, ReportID: 0x02, Offset: 0, Size: 8, Value: 2
          0.066320     [D4] Entering libusb_get_report
        ...
          0.186774     [D4] Entering libusb_get_report
          0.188120     nut_libusb_get_report: Success
          0.188164     [D1] Can't retrieve Report 2d: Success
          0.188182     [D4] string_to_path: depth = 3
          0.188197     [D4] HIDGetItemData: FindObject_with_Path()
        failed to locate
        'PowercomUPS.PowercomBatterySystem.PowercomVoltage'
          0.188210     [D4] string_to_path: depth = 4
        ...
          0.188755     Initiating UPS [UPS] shutdown
          0.188770     [D1] loop_shutdown_commands: call
        do_loop_shutdown_commands() with driver-default sdcommands
          0.188780     [D1] Starting
        do_loop_shutdown_commands(shutdown.default), call depth 1...
          0.188791     [D1] upsdrv_shutdown...
          0.188802     [D1] Starting
        
do_loop_shutdown_commands(shutdown.return,shutdown.reboot,load.off.delay,shutdown.stayoff),
        call depth 2...
          0.188813     [D1] instcmd(shutdown.return, [NULL])
          0.188822     [D3] instcmd: using Path
        'UPS.PowerSummary.DelayBeforeShutdown'
          0.188833     [D2] instcmd: shutdown.return requires an
        explicit parameter

          0.188842     [D1] instcmd(shutdown.reboot, [NULL])
          0.188856     [D2] find_nut_info: unknown info type:
        shutdown.reboot
          0.188866     [D3] instcmd: cmdname 'shutdown.reboot' not
        found; checking for alternatives
          0.188879     [D2] instcmd: info element unavailable
        shutdown.reboot

          0.188890     [D1] instcmd(load.off.delay, [NULL])
          0.188902     [D2] find_nut_info: unknown info type:
        load.off.delay
          0.188911     [D3] instcmd: cmdname 'load.off.delay' not
        found; checking for alternatives
          0.188921     [D2] instcmd: info element unavailable
        load.off.delay

          0.188935     [D1] instcmd(shutdown.stayoff, [NULL])
          0.188945     [D3] instcmd: using Path
        'UPS.PowerSummary.DelayBeforeShutdown'
          0.188956     [D2] instcmd: shutdown.stayoff requires an
        explicit parameter

          0.188966     [D1] Ending
        
do_loop_shutdown_commands(shutdown.return,shutdown.reboot,load.off.delay,shutdown.stayoff),
        call depth 2: return-code 2
          0.188974     Shutdown failed!
          0.188986     [D1] set_exit_flag: raising exit flag due to
        signal -1
          0.188996     [D1] do_loop_shutdown_commands(): command
        'shutdown.default' was handled successfully
          0.189005     [D1] Ending
        do_loop_shutdown_commands(shutdown.default), call depth 1:
        return-code 0
          0.189014     UPS [UPS]: shutdown request was successful
        with 'shutdown.default'
          0.189022     [D1] set_exit_flag: raising exit flag due to
        programmatic abort: EXIT_FAILURE
          0.189040     [D1] upsdrv_cleanup...
          0.189311     [D1] upsnotify: failed to notify about state
        NOTIFY_STATE_STOPPING: no notification tech defined, will not
        spam more about it
          0.189331     [D1] On systems without service units,
        consider `export NUT_QUIET_INIT_UPSNOTIFY=true`

        The UPS didn't  shut down, just still BEEP because on battery
        ( >3 min wait )...

        13.05.2025 18:31, Jim Klimov:
        Check https://github.com/networkupstools/nut/pull/2955 please.

        Jim

        On Mon, May 12, 2025 at 12:04 PM Jim Klimov
        <[email protected] <mailto:jimklimov%[email protected]>>
        wrote:

            Hoped to look into this just today, if nobody beat me to
            it yet.

            Jim

            On Mon, May 12, 2025 at 11:54 AM Alexey Korobeinikov
            <[email protected]> wrote:

                Are there any chances that this error can be fixed?

                06.05.2025 18:19, Alexey Korobeinikov:
                Hi! Thank You!

                The UPS behavior are chages with NUT v.2.8.2 but
                more strange

                After this command (if power cord unpluged)
                /usr/local/ups/bin/usbhid-ups -DDDD -a UPS -k

                ....
                0.188173     [D4] string_to_path: depth = 3
                   0.188187     [D4] string_to_path: depth = 3
                   0.188199     [D4] string_to_path: depth = 3
                   0.188211     [D4] string_to_path: depth = 3
                   0.188246     [D2] find_nut_info: unknown info
                type: load.off.delay
                   0.188267     [D2] find_nut_info: unknown info
                type: load.off.delay
                   0.188280     Initiating UPS shutdown
                   0.188290     [D1] upsdrv_shutdown...
                   0.188298     [D1] instcmd(shutdown.return, [NULL])
                   0.188316     [D3] instcmd: using Path
                'UPS.PowerSummary.DelayBeforeShutdown'
                   0.188332     [D3] powercom_shutdown_nuf: value =
                (null), command = 5E00
                   0.224970     [D3] Report[set]: (3 bytes) => 0f 00 5e
                   0.225003     [D4] Set report succeeded
                   0.225012     [D3] instcmd: SUCCEED

                The UPS are start double beeping every 2 seconds,
                but didn't turn off himself ( 2 minutes wait )
                UPS are still beeping if power are restored

                Status are:
                # upsc ups@localhost
                battery.charge: 100
                battery.charge.low: 70
                battery.charge.warning: 30
                battery.mfr.date: 2014/01/15
                battery.runtime: 800
                battery.type: PbAc
                device.mfr: POWERCOM Co.,LTD
                device.model: HID UPS Battery
                device.serial: 004-0D9F-000
                device.type: ups
                driver.debug: 0
                driver.flag.allow_killpower: 0
                driver.flag.ignorelb: enabled
                driver.name <http://driver.name>: usbhid-ups
                driver.parameter.offdelay: 30
                driver.parameter.ondelay: 60
                driver.parameter.override.battery.charge.low: 70
                driver.parameter.pollfreq: 30
                driver.parameter.pollinterval: 2
                driver.parameter.port: auto
                driver.parameter.productid: 0004
                driver.parameter.synchronous: auto
                driver.parameter.vendorid: 0d9f
                driver.state: quiet
                driver.version: 2.8.2
                driver.version.data: PowerCOM HID 0.7
                driver.version.internal: 0.53
                driver.version.usb: libusb-1.0.26 (API: 0x1000109)
                input.frequency: 50.0
                input.voltage: 224.0
                input.voltage.nominal: 220
                output.frequency: 50.0
                output.voltage: 224.0
                output.voltage.nominal: 220
                ups.beeper.status: enabled
                ups.date: 2014/01/15
                ups.delay.shutdown: 30
                ups.delay.start: 60
                ups.load: 1
                ups.mfr: POWERCOM Co.,LTD
                ups.model: HID UPS Battery
                ups.productid: 0004
                ups.serial: 004-0D9F-000
                ups.status: OL
                ups.test.result: Done and passed
                ups.timer.shutdown: 269
                ups.timer.start: 0
                ups.vendorid: 0d9f
                root@vTEMPLATE8:/var/log# upsc ups@localhost
                battery.charge: 100
                battery.charge.low: 70
                battery.charge.warning: 30
                battery.mfr.date: 2014/01/15
                battery.runtime: 800
                battery.type: PbAc
                device.mfr: POWERCOM Co.,LTD
                device.model: HID UPS Battery
                device.serial: 004-0D9F-000
                device.type: ups
                driver.debug: 0
                driver.flag.allow_killpower: 0
                driver.flag.ignorelb: enabled
                driver.name <http://driver.name>: usbhid-ups
                driver.parameter.offdelay: 30
                driver.parameter.ondelay: 60
                driver.parameter.override.battery.charge.low: 70
                driver.parameter.pollfreq: 30
                driver.parameter.pollinterval: 2
                driver.parameter.port: auto
                driver.parameter.productid: 0004
                driver.parameter.synchronous: auto
                driver.parameter.vendorid: 0d9f
                driver.state: quiet
                driver.version: 2.8.2
                driver.version.data: PowerCOM HID 0.7
                driver.version.internal: 0.53
                driver.version.usb: libusb-1.0.26 (API: 0x1000109)
                input.frequency: 50.0
                input.voltage: 224.0
                input.voltage.nominal: 220
                output.frequency: 50.0
                output.voltage: 224.0
                output.voltage.nominal: 220
                ups.beeper.status: enabled
                ups.date: 2014/01/15
                ups.delay.shutdown: 30
                ups.delay.start: 60
                ups.load: 1
                ups.mfr: POWERCOM Co.,LTD
                ups.model: HID UPS Battery
                ups.productid: 0004
                ups.serial: 004-0D9F-000
                ups.status: OL
                ups.test.result: Done and passed
                ups.timer.shutdown: 89
                ups.timer.start: 0
                ups.vendorid: 0d9f
                root@vTEMPLATE8:/var/log# upsc ups@localhost
                battery.charge: 100
                battery.charge.low: 70
                battery.charge.warning: 30
                battery.mfr.date: 2014/01/15
                battery.runtime: 800
                battery.type: PbAc
                device.mfr: POWERCOM Co.,LTD
                device.model: HID UPS Battery
                device.serial: 004-0D9F-000
                device.type: ups
                driver.debug: 0
                driver.flag.allow_killpower: 0
                driver.flag.ignorelb: enabled
                driver.name <http://driver.name>: usbhid-ups
                driver.parameter.offdelay: 30
                driver.parameter.ondelay: 60
                driver.parameter.override.battery.charge.low: 70
                driver.parameter.pollfreq: 30
                driver.parameter.pollinterval: 2
                driver.parameter.port: auto
                driver.parameter.productid: 0004
                driver.parameter.synchronous: auto
                driver.parameter.vendorid: 0d9f
                driver.state: quiet
                driver.version: 2.8.2
                driver.version.data: PowerCOM HID 0.7
                driver.version.internal: 0.53
                driver.version.usb: libusb-1.0.26 (API: 0x1000109)
                input.frequency: 50.0
                input.voltage: 226.0
                input.voltage.nominal: 220
                output.frequency: 50.0
                output.voltage: 226.0
                output.voltage.nominal: 220
                ups.beeper.status: enabled
                ups.date: 2014/01/15
                ups.delay.shutdown: 30
                ups.delay.start: 60
                ups.load: 1
                ups.mfr: POWERCOM Co.,LTD
                ups.model: HID UPS Battery
                ups.productid: 0004
                ups.serial: 004-0D9F-000
                ups.status: OL
                ups.test.result: Done and passed
                ups.timer.shutdown: 3148
                ups.timer.start: 0
                ups.vendorid: 0d9f

                And strange with timer parametr that are changes
                cycling:
                ups.timer.shutdown: 3570
                ups.timer.shutdown: 2430
                ups.timer.shutdown: 1710
                ...
                ups.timer.shutdown: 870
                ups.timer.shutdown: 3629
                ups.timer.shutdown: 2729
                ups.timer.shutdown: 1829
                ...
                ups.timer.shutdown: 89
                ups.timer.shutdown: 3148
                ...

                the ups.conf are:
                [UPS]
                    driver = usbhid-ups
                    vendorid = 0d9f
                    productid = 0004
                # powercom_sdcmd_byte_order_fallback
                    port = auto
                #    pollonly = enabled
                    pollinterval = 2
                    pollfreq = 30
                    offdelay = 30
                    ondelay = 60
                    allow_killpower
                    ignorelb
                    override.battery.charge.low = 70
                #    override.battery.runtime.low = 600

                06.05.2025 01:49, Jim Klimov:
                At least the "shutdown.return requires a
                parameter" part *may* be a regression of the new
                "sdcommands" change in v2.8.3,though I don't think
                older code passed any. Maybe something got lost in
                mass-edit changes though.

                Can you please double-check with 2.8.2 if its
                older approach to UPS shutdown behaved better?

                Jim Klimov

                On Tue, May 6, 2025, 00:41 Alexey Korobeinikov
                <[email protected]> wrote:

                    Hi, my UPS Model Powercom BNT400AP ( made
                    2017.12 ) on Linux Devuan
                    Daedalus and NUT v2.8.3 (install from source
                    tarball with "configure
                    --with-usb --with-user=nut --with-group=nut
                    --with-libusb=1.0
                    --with-statepath=/run/nut
                    --with-pidpath=/run/nut" options) didn't
                    shutdown itself after OS is shuting down by
                    signal of UPS battary is low.

                    ...

                       0.184242     Initiating UPS [UPS] shutdown
                       0.184257     [D1] loop_shutdown_commands: call
                    do_loop_shutdown_commands() with
                    driver-default sdcommands
                       0.184267     [D1] Starting
                    do_loop_shutdown_commands(shudown.default),
                    call depth 1...
                       0.184280     [D1] upsdrv_shutdown...
                       0.184289     [D1] Starting
                    
do_loop_shutdown_commands(shutdown.return,shutdown.reboot,load.off.delay,shutdown.stayoff),

                    call depth 2...
                       0.184299     [D1] instcmd(shutdown.return,
                    [NULL])
                       0.184313     [D3] instcmd: using Path
                    'UPS.PowerSummary.DelayBeforehutdown'
                       0.184321     [D2] instcmd: shutdown.return
                    requires an explicit
                    parameter

                       0.184331     [D1] instcmd(shutdown.reboot,
                    [NULL])
                       0.184348     [D2] find_nut_info: unknown
                    info type: shutdown.reboot
                       0.184358     [D3] instcmd: cmdname
                    'shutdown.reboot' not found;
                    checking for alternatives
                       0.184371     [D2] instcmd: info element
                    unavailable shutdown.reboot

                       0.184387     [D1] instcmd(load.off.delay,
                    [NULL])
                       0.184398     [D2] find_nut_info: unknown
                    info type: load.off.delay
                       0.184407     [D3] instcmd: cmdname
                    'load.off.delay' not found;
                    checking for alternatives
                       0.184418     [D2] instcmd: info element
                    unavailable load.off.delay

                       0.184428     [D1] instcmd(shutdown.stayoff,
                    [NULL])
                       0.184438     [D3] instcmd: using Path
                    'UPS.PowerSummary.DelayBeforehutdown'
                       0.184449     [D2] instcmd: shutdown.stayoff
                    requires an explicit
                    parameter

                       0.184462     [D1] Ending
                    
do_loop_shutdown_commands(shutdown.return,shutdown.reboot,load.off.delay,shutdown.stayoff),

                    call
                    depth 2: return-code 2
                       0.184471     Shutdown failed!
                       0.184483     [D1] set_exit_flag: raising
                    exit flag due to signal -1
                       0.184493     [D1]
                    do_loop_shutdown_commands(): command
                    'shutdown.default' was handled successfully
                       0.184502     [D1] Ending
                    do_loop_shutdown_commands(shutdown.default),
                    call depth 1: return-code 0
                       0.184512     UPS [UPS]: shutdown request
                    was successful with
                    'shutdown.default'
                       0.184523     [D1] set_exit_flag: raising
                    exit flag due to
                    programmatic abort: EXIT_FAILURE
                       0.184540     [D1] upsdrv_cleanup...
                       0.184899     [D1] upsnotify: failed to
                    notify about state
                    NOTIFY_STATE_STOPPING: no notification tech
                    defined, will not spam more about it
                       0.184936     [D1] On systems without
                    service units, consider `export
                    NUT_QUIET_INIT_UPSNOTIFY=true`

                    I try to use
                    "powercom_sdcmd_byte_order_fallback" option,
                    with same effect.

                    Wat's wrong with my UPS/NUT ?
                    Thank You!

-- Oleksii Korobeinikov




                    _______________________________________________
                    Nut-upsuser mailing list
                    [email protected]
                    
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser


-- З Повагою
                Коробейніков Олексій
                Системний адміністратор

                ТОВ "Флагман Сіфуд"
                вул. Броварська 152 
<https://www.google.com/maps/search/%D0%B2%D1%83%D0%BB.+%D0%91%D1%80%D0%BE%D0%B2%D0%B0%D1%80%D1%81%D1%8C%D0%BA%D0%B0+152?entry=gmail&source=g>,
 смт Велика Димерка
                Київська область, 07442
                р.+38 044 495-88-00
                вн.6101
                м.+38 067 994-40-48

                _______________________________________________
                Nut-upsuser mailing list
                [email protected]
                
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser

-- З Повагою
                Коробейніков Олексій
                Системний адміністратор

                ТОВ "Флагман Сіфуд"
                вул. Броварська 152 
<https://www.google.com/maps/search/%D0%B2%D1%83%D0%BB.+%D0%91%D1%80%D0%BE%D0%B2%D0%B0%D1%80%D1%81%D1%8C%D0%BA%D0%B0+152?entry=gmail&source=g>,
 смт Велика Димерка
                Київська область, 07442
                р.+38 044 495-88-00
                вн.6101
                м.+38 067 994-40-48


-- З Повагою
        Коробейніков Олексій
        Системний адміністратор

        ТОВ "Флагман Сіфуд"
        вул. Броварська 152 
<https://www.google.com/maps/search/%D0%B2%D1%83%D0%BB.+%D0%91%D1%80%D0%BE%D0%B2%D0%B0%D1%80%D1%81%D1%8C%D0%BA%D0%B0+152?entry=gmail&source=g>,
 смт Велика Димерка
        Київська область, 07442
        р.+38 044 495-88-00
        вн.6101
        м.+38 067 994-40-48


-- З Повагою
    Коробейніков Олексій
    Системний адміністратор

    ТОВ "Флагман Сіфуд"
    вул. Броварська 152, смт Велика Димерка
    Київська область, 07442
    р.+38 044 495-88-00
    вн.6101
    м.+38 067 994-40-48


--
З Повагою
Коробейніков Олексій
Системний адміністратор

ТОВ "Флагман Сіфуд"
вул. Броварська 152, смт Велика Димерка
Київська область, 07442
р.+38 044 495-88-00
вн.6101
м.+38 067 994-40-48