Seems you did not build the PR source branch, usbhid-ups version
there should be 0.64.
Jim
On Thu, May 15, 2025, 13:04 Alexey Korobeinikov
<[email protected]> wrote:
After reseting usb (usbreset 0d9f:0004), I can connect to
UPS. But still have problem to shuting down the UPS:
/usr/local/ups/bin/usbhid-ups -DDDD -a UPS -k
Network UPS Tools 2.8.3.1 (development iteration after 2.8.3)
- Generic HID driver 0.63
USB communication driver (libusb 1.0) 0.50
0.000000 [D1] upsdrv_makevartable...
0.000078 [D1] Using USB implementation: libusb-1.0.26
(API: 0x01000109)
0.000238 [D3] main_arg: var='driver' val='usbhid-ups'
0.000253 [D3] main_arg: var='vendorid' val='0d9f'
0.000272 [D3] main_arg: var='productid' val='0004'
0.000289 [D3] main_arg: var='port' val='auto'
0.000310 [D3] main_arg: var='pollinterval' val='2'
...
0.004914 [D2] Checking device 4 of 10 (0D9F/0004)
0.019235 [D2] - VendorID: 0d9f
0.019276 [D2] - ProductID: 0004
0.019282 [D2] - Manufacturer: POWERCOM Co.,LTD
0.019288 [D2] - Product: HID UPS Battery
0.019293 [D2] - Serial Number: 004-0D9F-000
0.019298 [D2] - Bus: 006
0.019303 [D2] - Bus Port: 002
0.019308 [D2] - Device: 003
0.019313 [D2] - Device release number: 0002
0.019318 [D2] Trying to match device
0.019327 [D2] match_function_subdriver (non-SHUT mode):
matching a device...
0.019347 [D3] match_function_regex: matching a device...
0.019420 [D2] Device matches
0.019438 [D2] Reading configuration descriptor 1 of 1
0.019479 [D3] libusb_kernel_driver_active() returned 0:
Success
0.019516 [D2] Claimed interface 0 successfully
0.019533 [D3] nut_libusb_set_altinterface: skipped
libusb_set_interface_alt_setting(udev, 0, 0)
0.021265 [D2] Retrieved HID descriptor (expected 9, got 9)
0.021306 [D3] HID descriptor, method 1: (9 bytes) => 09
21 00 01 00 01 22 e4 03
0.021314 [D3] HID descriptor length (method 1) 996
0.021330 [D4] i=0, extra[i]=09, extra[i+1]=21
0.021344 [D3] HID descriptor, method 2: (9 bytes) => 09
21 00 01 00 01 22 e4 03
0.021369 [D3] HID descriptor length (method 2) 996
0.021381 [D2] HID descriptor length 996
0.062245 [D2] Report Descriptor size = 996
0.062294 [D3] Report Descriptor: (996 bytes) => 05 84
09 04 a1 01 09 24 a1 02 85 01 09 fe
0.062308 [D3] 79 01 75 08 95 01 15 00 26 ff 00 b1 22
85 02 09 ff 79 02 b1 22 05 85 85 05
0.062322 [D3] 09 89 79 04 b1 22 85 07 09 8b b1 22 85
08 09 2c 25 03 b1 22 85 09 09 83 25
0.062335 [D3] 64 b1 22 09 67 b1 22 85 0e 09 66 81 22
09 66 b1 a2 85 0b 09 8c b1 22 85 0c
0.062347 [D3] 09 29 b1 a2 85 0d 09 85 75 10 27 ff ff
00 00 b1 a2 85 37 09 68 81 22 09 68
0.062363 [D3] b1 a2 05 84 85 0f 09 57 75 10 16 00 00
27 ff ff 00 00 b1 a2 85 10 09 56 75
0.062380 [D3] 20 16 00 00 27 9f 86 01 00 b1 a2 85 11
09 40 75 10 16 64 00 26 f0 00 b1 22
0.062395 [D3] 85 12 09 30 75 10 16 00 00 26 40 01 b1
a2 85 2c 09 36 75 08 25 5a b1 a2 85
0.062410 [D3] 13 09 5a 75 08 15 00 25 03 b1 a2 09 02
a1 02 05 85 85 0a 09 44 75 01 15 00
0.062437 [D3] 25 01 81 a2 09 44 b1 a2 09 45 81 a2 09
45 b1 a2 09 d0 81 a2 09 d0 b1 a2 09
0.062455 [D3] d1 81 a2 09 d1 b1 a2 09 42 81 a2 09 42
b1 a2 09 43 81 a2 09 43 b1 a2 09 4b
0.062474 [D3] 81 a2 09 4b b1 a2 09 db 81 a2 09 db b1
a2 05 84 09 68 81 a2 09 68 b1 a2 09
0.062491 [D3] 69 81 a2 09 69 b1 a2 09 73 81 a2 09 73
b1 a2 09 65 81 a2 09 65 b1 a2 95 03
0.062510 [D3] 81 01 b1 01 95 01 06 86 ff 09 80 81 a2
09 80 b1 a2 c0 c0 05 84 09 12 a1 00
0.062526 [D3] 85 15 09 58 75 08 25 66 b1 a2 85 16 09
70 75 08 25 03 b1 a2 05 85 85 17 09
0.062544 [D3] 85 75 10 27 ff ff 00 00 b1 a2 85 18 09
66 75 08 15 00 25 64 b1 a2 05 84 85
0.062559 [D3] 19 09 40 75 10 16 00 0c 26 00 30 b1 22
85 1a 09 30 75 10 16 00 09 26 00 24
0.062577 [D3] b1 a2 85 1b 09 56 75 20 16 00 00 27 9f
86 01 00 b1 a2 85 2d 09 36 75 08 25
0.062594 [D3] 5a b1 a2 c0 05 84 09 1a a1 00 85 1c 09
40 75 10 16 64 00 26 f0 00 b1 22 85
0.062612 [D3] 1d 09 30 75 10 16 00 00 26 40 01 b1 a2
85 2e 09 30 75 10 16 00 00 26 40 01
0.062627 [D3] b1 a2 85 1e 09 32 75 08 15 00 25 46 b1
a2 c0 05 84 09 1c a1 00 85 2f 09 41
0.062645 [D3] 75 08 15 01 25 0c b1 22 85 1f 09 35 75
08 15 00 25 64 b1 a2 85 20 09 40 75
0.062664 [D3] 10 16 64 00 26 f0 00 b1 22 85 21 09 30
75 10 16 00 00 26 40 01 b1 a2 85 30
0.062681 [D3] 09 42 75 08 15 32 25 3c b1 22 85 22 09
32 75 08 15 00 25 46 b1 a2 85 23 09
0.062699 [D3] 57 75 08 15 00 25 12 b1 a2 85 24 09 56
75 20 16 00 00 27 9f 86 01 00 b1 a2
0.062716 [D3] c0 05 84 85 06 09 01 79 05 b1 a2 85 25
09 5a 75 08 15 00 25 03 b1 a2 09 02
0.062736 [D3] a1 02 05 85 85 26 09 44 75 01 15 00 25
01 b1 a2 09 45 b1 a2 09 d0 b1 a2 09
0.062752 [D3] d1 b1 a2 09 42 b1 a2 09 43 b1 a2 09 4b
b1 a2 09 db b1 a2 05 84 09 68 b1 a2
0.062768 [D3] 09 69 b1 a2 09 73 b1 a2 09 65 b1 a2 09
6e b1 a2 09 6f b1 a2 09 71 b1 a2 06
0.062791 [D3] 86 ff 09 80 b1 a2 c0 85 27 05 84 09 69
75 08 15 00 25 01 b1 a2 09 1e a1 00
0.062807 [D3] 85 a0 09 01 75 08 95 07 15 00 26 ff 00
b1 03 85 a1 09 01 75 08 95 07 15 00
0.062835 [D3] 26 ff 00 b1 03 85 a2 09 01 75 08 95 07
15 00 26 ff 00 b1 03 85 a3 09 01 75
0.062853 [D3] 08 95 07 15 00 26 ff 00 b1 03 85 a4 09
01 75 08 95 07 15 00 26 ff 00 b1 03
0.062871 [D3] 85 a5 09 01 75 08 95 07 15 00 26 ff 00
b1 03 85 a6 09 01 75 08 95 07 15 00
0.062889 [D3] 26 ff 00 b1 03 85 a7 09 01 75 08 95 07
15 00 26 ff 00 b1 03 85 a8 09 01 75
0.062905 [D3] 08 95 07 15 00 26 ff 00 b1 03 85 a9 09
01 75 08 95 07 15 00 26 ff 00 b1 03
0.062923 [D3] 85 aa 09 01 75 08 95 07 15 00 26 ff 00
b1 03 85 ab 09 01 75 08 95 07 15 00
0.062940 [D3] 26 ff 00 b1 03 85 ac 09 01 75 08 95 07
15 00 26 ff 00 b1 03 85 ad 09 01 75
0.062960 [D3] 08 95 07 15 00 26 ff 00 b1 03 85 ae 09
01 75 08 95 07 15 00 26 ff 00 b1 03
0.062977 [D3] 85 31 09 01 75 08 95 01 15 00 26 ff 00
b1 03 85 32 09 01 75 08 95 01 15 00
0.062990 [D3] 26 ff 00 b1 03 c0 c0
0.063197 Using subdriver: PowerCOM HID 0.71
0.063214 [D1] 102 HID objects found
0.063229 [D4] Entering libusb_get_report
0.064157 [D3] Report[get]: (2 bytes) => 01 01
0.064197 [D1] Path: UPS.PowerSummary.iProduct, Type:
Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 1
0.064209 [D4] Entering libusb_get_report
0.066271 [D3] Report[get]: (2 bytes) => 02 02
0.066311 [D1] Path: UPS.PowerSummary.iSerialNumber,
Type: Feature, ReportID: 0x02, Offset: 0, Size: 8, Value: 2
0.066320 [D4] Entering libusb_get_report
...
0.186774 [D4] Entering libusb_get_report
0.188120 nut_libusb_get_report: Success
0.188164 [D1] Can't retrieve Report 2d: Success
0.188182 [D4] string_to_path: depth = 3
0.188197 [D4] HIDGetItemData: FindObject_with_Path()
failed to locate
'PowercomUPS.PowercomBatterySystem.PowercomVoltage'
0.188210 [D4] string_to_path: depth = 4
...
0.188755 Initiating UPS [UPS] shutdown
0.188770 [D1] loop_shutdown_commands: call
do_loop_shutdown_commands() with driver-default sdcommands
0.188780 [D1] Starting
do_loop_shutdown_commands(shutdown.default), call depth 1...
0.188791 [D1] upsdrv_shutdown...
0.188802 [D1] Starting
do_loop_shutdown_commands(shutdown.return,shutdown.reboot,load.off.delay,shutdown.stayoff),
call depth 2...
0.188813 [D1] instcmd(shutdown.return, [NULL])
0.188822 [D3] instcmd: using Path
'UPS.PowerSummary.DelayBeforeShutdown'
0.188833 [D2] instcmd: shutdown.return requires an
explicit parameter
0.188842 [D1] instcmd(shutdown.reboot, [NULL])
0.188856 [D2] find_nut_info: unknown info type:
shutdown.reboot
0.188866 [D3] instcmd: cmdname 'shutdown.reboot' not
found; checking for alternatives
0.188879 [D2] instcmd: info element unavailable
shutdown.reboot
0.188890 [D1] instcmd(load.off.delay, [NULL])
0.188902 [D2] find_nut_info: unknown info type:
load.off.delay
0.188911 [D3] instcmd: cmdname 'load.off.delay' not
found; checking for alternatives
0.188921 [D2] instcmd: info element unavailable
load.off.delay
0.188935 [D1] instcmd(shutdown.stayoff, [NULL])
0.188945 [D3] instcmd: using Path
'UPS.PowerSummary.DelayBeforeShutdown'
0.188956 [D2] instcmd: shutdown.stayoff requires an
explicit parameter
0.188966 [D1] Ending
do_loop_shutdown_commands(shutdown.return,shutdown.reboot,load.off.delay,shutdown.stayoff),
call depth 2: return-code 2
0.188974 Shutdown failed!
0.188986 [D1] set_exit_flag: raising exit flag due to
signal -1
0.188996 [D1] do_loop_shutdown_commands(): command
'shutdown.default' was handled successfully
0.189005 [D1] Ending
do_loop_shutdown_commands(shutdown.default), call depth 1:
return-code 0
0.189014 UPS [UPS]: shutdown request was successful
with 'shutdown.default'
0.189022 [D1] set_exit_flag: raising exit flag due to
programmatic abort: EXIT_FAILURE
0.189040 [D1] upsdrv_cleanup...
0.189311 [D1] upsnotify: failed to notify about state
NOTIFY_STATE_STOPPING: no notification tech defined, will not
spam more about it
0.189331 [D1] On systems without service units,
consider `export NUT_QUIET_INIT_UPSNOTIFY=true`
The UPS didn't shut down, just still BEEP because on battery
( >3 min wait )...
13.05.2025 18:31, Jim Klimov:
Check https://github.com/networkupstools/nut/pull/2955 please.
Jim
On Mon, May 12, 2025 at 12:04 PM Jim Klimov
<[email protected] <mailto:jimklimov%[email protected]>>
wrote:
Hoped to look into this just today, if nobody beat me to
it yet.
Jim
On Mon, May 12, 2025 at 11:54 AM Alexey Korobeinikov
<[email protected]> wrote:
Are there any chances that this error can be fixed?
06.05.2025 18:19, Alexey Korobeinikov:
Hi! Thank You!
The UPS behavior are chages with NUT v.2.8.2 but
more strange
After this command (if power cord unpluged)
/usr/local/ups/bin/usbhid-ups -DDDD -a UPS -k
....
0.188173 [D4] string_to_path: depth = 3
0.188187 [D4] string_to_path: depth = 3
0.188199 [D4] string_to_path: depth = 3
0.188211 [D4] string_to_path: depth = 3
0.188246 [D2] find_nut_info: unknown info
type: load.off.delay
0.188267 [D2] find_nut_info: unknown info
type: load.off.delay
0.188280 Initiating UPS shutdown
0.188290 [D1] upsdrv_shutdown...
0.188298 [D1] instcmd(shutdown.return, [NULL])
0.188316 [D3] instcmd: using Path
'UPS.PowerSummary.DelayBeforeShutdown'
0.188332 [D3] powercom_shutdown_nuf: value =
(null), command = 5E00
0.224970 [D3] Report[set]: (3 bytes) => 0f 00 5e
0.225003 [D4] Set report succeeded
0.225012 [D3] instcmd: SUCCEED
The UPS are start double beeping every 2 seconds,
but didn't turn off himself ( 2 minutes wait )
UPS are still beeping if power are restored
Status are:
# upsc ups@localhost
battery.charge: 100
battery.charge.low: 70
battery.charge.warning: 30
battery.mfr.date: 2014/01/15
battery.runtime: 800
battery.type: PbAc
device.mfr: POWERCOM Co.,LTD
device.model: HID UPS Battery
device.serial: 004-0D9F-000
device.type: ups
driver.debug: 0
driver.flag.allow_killpower: 0
driver.flag.ignorelb: enabled
driver.name <http://driver.name>: usbhid-ups
driver.parameter.offdelay: 30
driver.parameter.ondelay: 60
driver.parameter.override.battery.charge.low: 70
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.productid: 0004
driver.parameter.synchronous: auto
driver.parameter.vendorid: 0d9f
driver.state: quiet
driver.version: 2.8.2
driver.version.data: PowerCOM HID 0.7
driver.version.internal: 0.53
driver.version.usb: libusb-1.0.26 (API: 0x1000109)
input.frequency: 50.0
input.voltage: 224.0
input.voltage.nominal: 220
output.frequency: 50.0
output.voltage: 224.0
output.voltage.nominal: 220
ups.beeper.status: enabled
ups.date: 2014/01/15
ups.delay.shutdown: 30
ups.delay.start: 60
ups.load: 1
ups.mfr: POWERCOM Co.,LTD
ups.model: HID UPS Battery
ups.productid: 0004
ups.serial: 004-0D9F-000
ups.status: OL
ups.test.result: Done and passed
ups.timer.shutdown: 269
ups.timer.start: 0
ups.vendorid: 0d9f
root@vTEMPLATE8:/var/log# upsc ups@localhost
battery.charge: 100
battery.charge.low: 70
battery.charge.warning: 30
battery.mfr.date: 2014/01/15
battery.runtime: 800
battery.type: PbAc
device.mfr: POWERCOM Co.,LTD
device.model: HID UPS Battery
device.serial: 004-0D9F-000
device.type: ups
driver.debug: 0
driver.flag.allow_killpower: 0
driver.flag.ignorelb: enabled
driver.name <http://driver.name>: usbhid-ups
driver.parameter.offdelay: 30
driver.parameter.ondelay: 60
driver.parameter.override.battery.charge.low: 70
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.productid: 0004
driver.parameter.synchronous: auto
driver.parameter.vendorid: 0d9f
driver.state: quiet
driver.version: 2.8.2
driver.version.data: PowerCOM HID 0.7
driver.version.internal: 0.53
driver.version.usb: libusb-1.0.26 (API: 0x1000109)
input.frequency: 50.0
input.voltage: 224.0
input.voltage.nominal: 220
output.frequency: 50.0
output.voltage: 224.0
output.voltage.nominal: 220
ups.beeper.status: enabled
ups.date: 2014/01/15
ups.delay.shutdown: 30
ups.delay.start: 60
ups.load: 1
ups.mfr: POWERCOM Co.,LTD
ups.model: HID UPS Battery
ups.productid: 0004
ups.serial: 004-0D9F-000
ups.status: OL
ups.test.result: Done and passed
ups.timer.shutdown: 89
ups.timer.start: 0
ups.vendorid: 0d9f
root@vTEMPLATE8:/var/log# upsc ups@localhost
battery.charge: 100
battery.charge.low: 70
battery.charge.warning: 30
battery.mfr.date: 2014/01/15
battery.runtime: 800
battery.type: PbAc
device.mfr: POWERCOM Co.,LTD
device.model: HID UPS Battery
device.serial: 004-0D9F-000
device.type: ups
driver.debug: 0
driver.flag.allow_killpower: 0
driver.flag.ignorelb: enabled
driver.name <http://driver.name>: usbhid-ups
driver.parameter.offdelay: 30
driver.parameter.ondelay: 60
driver.parameter.override.battery.charge.low: 70
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.productid: 0004
driver.parameter.synchronous: auto
driver.parameter.vendorid: 0d9f
driver.state: quiet
driver.version: 2.8.2
driver.version.data: PowerCOM HID 0.7
driver.version.internal: 0.53
driver.version.usb: libusb-1.0.26 (API: 0x1000109)
input.frequency: 50.0
input.voltage: 226.0
input.voltage.nominal: 220
output.frequency: 50.0
output.voltage: 226.0
output.voltage.nominal: 220
ups.beeper.status: enabled
ups.date: 2014/01/15
ups.delay.shutdown: 30
ups.delay.start: 60
ups.load: 1
ups.mfr: POWERCOM Co.,LTD
ups.model: HID UPS Battery
ups.productid: 0004
ups.serial: 004-0D9F-000
ups.status: OL
ups.test.result: Done and passed
ups.timer.shutdown: 3148
ups.timer.start: 0
ups.vendorid: 0d9f
And strange with timer parametr that are changes
cycling:
ups.timer.shutdown: 3570
ups.timer.shutdown: 2430
ups.timer.shutdown: 1710
...
ups.timer.shutdown: 870
ups.timer.shutdown: 3629
ups.timer.shutdown: 2729
ups.timer.shutdown: 1829
...
ups.timer.shutdown: 89
ups.timer.shutdown: 3148
...
the ups.conf are:
[UPS]
driver = usbhid-ups
vendorid = 0d9f
productid = 0004
# powercom_sdcmd_byte_order_fallback
port = auto
# pollonly = enabled
pollinterval = 2
pollfreq = 30
offdelay = 30
ondelay = 60
allow_killpower
ignorelb
override.battery.charge.low = 70
# override.battery.runtime.low = 600
06.05.2025 01:49, Jim Klimov:
At least the "shutdown.return requires a
parameter" part *may* be a regression of the new
"sdcommands" change in v2.8.3,though I don't think
older code passed any. Maybe something got lost in
mass-edit changes though.
Can you please double-check with 2.8.2 if its
older approach to UPS shutdown behaved better?
Jim Klimov
On Tue, May 6, 2025, 00:41 Alexey Korobeinikov
<[email protected]> wrote:
Hi, my UPS Model Powercom BNT400AP ( made
2017.12 ) on Linux Devuan
Daedalus and NUT v2.8.3 (install from source
tarball with "configure
--with-usb --with-user=nut --with-group=nut
--with-libusb=1.0
--with-statepath=/run/nut
--with-pidpath=/run/nut" options) didn't
shutdown itself after OS is shuting down by
signal of UPS battary is low.
...
0.184242 Initiating UPS [UPS] shutdown
0.184257 [D1] loop_shutdown_commands: call
do_loop_shutdown_commands() with
driver-default sdcommands
0.184267 [D1] Starting
do_loop_shutdown_commands(shudown.default),
call depth 1...
0.184280 [D1] upsdrv_shutdown...
0.184289 [D1] Starting
do_loop_shutdown_commands(shutdown.return,shutdown.reboot,load.off.delay,shutdown.stayoff),
call depth 2...
0.184299 [D1] instcmd(shutdown.return,
[NULL])
0.184313 [D3] instcmd: using Path
'UPS.PowerSummary.DelayBeforehutdown'
0.184321 [D2] instcmd: shutdown.return
requires an explicit
parameter
0.184331 [D1] instcmd(shutdown.reboot,
[NULL])
0.184348 [D2] find_nut_info: unknown
info type: shutdown.reboot
0.184358 [D3] instcmd: cmdname
'shutdown.reboot' not found;
checking for alternatives
0.184371 [D2] instcmd: info element
unavailable shutdown.reboot
0.184387 [D1] instcmd(load.off.delay,
[NULL])
0.184398 [D2] find_nut_info: unknown
info type: load.off.delay
0.184407 [D3] instcmd: cmdname
'load.off.delay' not found;
checking for alternatives
0.184418 [D2] instcmd: info element
unavailable load.off.delay
0.184428 [D1] instcmd(shutdown.stayoff,
[NULL])
0.184438 [D3] instcmd: using Path
'UPS.PowerSummary.DelayBeforehutdown'
0.184449 [D2] instcmd: shutdown.stayoff
requires an explicit
parameter
0.184462 [D1] Ending
do_loop_shutdown_commands(shutdown.return,shutdown.reboot,load.off.delay,shutdown.stayoff),
call
depth 2: return-code 2
0.184471 Shutdown failed!
0.184483 [D1] set_exit_flag: raising
exit flag due to signal -1
0.184493 [D1]
do_loop_shutdown_commands(): command
'shutdown.default' was handled successfully
0.184502 [D1] Ending
do_loop_shutdown_commands(shutdown.default),
call depth 1: return-code 0
0.184512 UPS [UPS]: shutdown request
was successful with
'shutdown.default'
0.184523 [D1] set_exit_flag: raising
exit flag due to
programmatic abort: EXIT_FAILURE
0.184540 [D1] upsdrv_cleanup...
0.184899 [D1] upsnotify: failed to
notify about state
NOTIFY_STATE_STOPPING: no notification tech
defined, will not spam more about it
0.184936 [D1] On systems without
service units, consider `export
NUT_QUIET_INIT_UPSNOTIFY=true`
I try to use
"powercom_sdcmd_byte_order_fallback" option,
with same effect.
Wat's wrong with my UPS/NUT ?
Thank You!
--
Oleksii Korobeinikov
_______________________________________________
Nut-upsuser mailing list
[email protected]
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
--
З Повагою
Коробейніков Олексій
Системний адміністратор
ТОВ "Флагман Сіфуд"
вул. Броварська 152
<https://www.google.com/maps/search/%D0%B2%D1%83%D0%BB.+%D0%91%D1%80%D0%BE%D0%B2%D0%B0%D1%80%D1%81%D1%8C%D0%BA%D0%B0+152?entry=gmail&source=g>,
смт Велика Димерка
Київська область, 07442
р.+38 044 495-88-00
вн.6101
м.+38 067 994-40-48
_______________________________________________
Nut-upsuser mailing list
[email protected]
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
--
З Повагою
Коробейніков Олексій
Системний адміністратор
ТОВ "Флагман Сіфуд"
вул. Броварська 152
<https://www.google.com/maps/search/%D0%B2%D1%83%D0%BB.+%D0%91%D1%80%D0%BE%D0%B2%D0%B0%D1%80%D1%81%D1%8C%D0%BA%D0%B0+152?entry=gmail&source=g>,
смт Велика Димерка
Київська область, 07442
р.+38 044 495-88-00
вн.6101
м.+38 067 994-40-48
--
З Повагою
Коробейніков Олексій
Системний адміністратор
ТОВ "Флагман Сіфуд"
вул. Броварська 152
<https://www.google.com/maps/search/%D0%B2%D1%83%D0%BB.+%D0%91%D1%80%D0%BE%D0%B2%D0%B0%D1%80%D1%81%D1%8C%D0%BA%D0%B0+152?entry=gmail&source=g>,
смт Велика Димерка
Київська область, 07442
р.+38 044 495-88-00
вн.6101
м.+38 067 994-40-48