Hi Steve.
sön 2007-02-04 klockan 03:30 +1100 skrev Steve Simeonidis:
> I have an FC5 system with a powerware 5110 usb ups.
>
> The system seems to find the UPS
>
> ------------------------------
> [EMAIL PROTECTED] src]# lsusb
> Bus 004 Device 001: ID 0000:0000
> Bus 003 Device 002: ID 0592:0002 Powerware Corp.
> Bus 003 Device 001: ID 0000:0000
> Bus 002 Device 001: ID 0000:0000
> Bus 005 Device 001: ID 0000:0000
> Bus 001 Device 001: ID 0000:0000
> -------------------------------
>
> [EMAIL PROTECTED] src]# cat /proc/bus/usb/devices
> ......
>
> T: Bus=03 Lev=01 Prnt=01 Port=00 Cnt=01 Dev#= 2 Spd=1.5 MxCh= 0
> D: Ver= 2.00 Cls=00(>ifc ) Sub=00 Prot=00 MxPS= 8 #Cfgs= 1
> P: Vendor=0592 ProdID=0002 Rev= 0.50
> S: Manufacturer=Powerware
> S: Product=Powerware UPS
> C:* #Ifs= 1 Cfg#= 1 Atr=80 MxPwr=100mA
> I: If#= 0 Alt= 0 #EPs= 1 Cls=ff(vend.) Sub=00 Prot=00 Driver=(none)
> E: Ad=81(I) Atr=03(Int.) MxPS= 8 Ivl=20ms
>
> -----------------------------
Yep that looks OK.
>
> I have set the port to auto but I can not make it work
>
> What do I need to set the port to?
>
The ups.conf should look something like this.
[pw5110]
driver = bcmxcp_usb
port = auto
shutdown_delay = 60
desc = "USB ups"
Now try to start the driver like this.
/sbin/bcmxcp_usb -a pw5110
If it spit out something like this
--------
Network UPS Tools - BCMXCP UPS driver 0.11 (2.0.5)
Model = POWERWARE UPS 500VA
Firmware = Cont:00.80 Inve:00.60
Shutdown delay = 60 seconds
--------
Then it is ok. If not then check the you have the right
udev rules installed.
Kjell
_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser