OK Steve,

I spotted the bug. 

You don't have the Battery_low alarm.
This trigger a bug in the driver. During some cleanup of the
code, the numbers was changed to unsigned int. That was not so smart
for this. -1 indicate not present alarm. But -1 is more than 0 if
it is read as unsigned so it trigger to set the alarm flag.  

-001    SHUTDOWN_IMMINENT    No
-001    BATTERY_LOW     No
0012    UTILITY_FAIL    Yes
-001    OUTPUT_SHORT_CIRCUIT    No

Try this. Change the unsigned int to int in bcmxcp.h
----------------------------------------------------
typedef struct { /* Entry in BCM/XCP - UPS mapping table */
        unsigned int alarm_block_index;         /* Index of this alarm in alarm 
block. -1 = not existing */
        char *alarm_desc;                       /* Description of this alarm */
}       BCMXCP_ALARM_MAP_ENTRY_t;
--------------------------------------------------------

And see if it make any difference.

About the build of svn. I think it should run OK on debian.
 
Regards
Kjell

lör 2007-05-19 klockan 19:25 +0100 skrev [EMAIL PROTECTED]:
> Hi, Kjell,
> 
> Kjell Claesson wrote:
> > Can you upgrade to 2.0.5, or any better if you can use the svn trunk. 
> 
> Thanks very much for your pointer. I'm currently trying to compile but
> it appears to be broken on my Debian (stable) system.
> 
> The issue here is that the configure script appears to assume that both
> libgd and libXpm will be in the same place, but here libgd is indeed in
> /usr/lib, but libXpm is in /usr/X11R6/lib. I know how to fix that in a
> plain makefile (adding -L/usr/X11R6/lib just before -lXpm) but I'm not
> very good on autoconf stuff.
> 
> Anyway, here's the list of alarms you asked about:
> 
> ommunications with UPS re-established
> Shutdown delay =  120 seconds
> Index Offset  Format  NUT
> 
> 0015  0000    61      None
> 0021  0004    61      None
> 0023  0008    61      None
> 0027  0012    61      output.frequency
> 0028  0016    61      input.frequency
> 0029  0020    61      None
> 0033  0024    61      battery.voltage
> 0034  0028    f0      battery.charge
> 0035  0032    f0      battery.runtime
> 0036  0036    f0      None
> 0056  0040    61      input.voltage
> 0059  0044    61      None
> 0062  0048    61      ambient.temperature
> 0071  0052    61      None
> 0074  0056    61      None
> 0075  0060    61      None
> 
> 
> Length of alarm map: 25
> 
> Index Alarm   Supported
> 
> 0000  INVERTER_AC_OVER_VOLTAGE        Yes
> 0001  INVERTER_AC_UNDER_VOLTAGE       Yes
> -001  INVERTER_OVER_OR_UNDER_FREQ     No
> -001  BYPASS_AC_OVER_VOLTAGE  No
> -001  BYPASS_AC_UNDER_VOLTAGE No
> -001  BYPASS_OVER_OR_UNDER_FREQ       No
> 0002  INPUT_AC_OVER_VOLTAGE   Yes
> 0003  INPUT_AC_UNDER_VOLTAGE  Yes
> -001  INPUT_UNDER_OR_OVER_FREQ        No
> -001  OUTPUT_OVER_VOLTAGE     No
> -001  OUTPUT_UNDER_VOLTAGE    No
> -001  OUTPUT_UNDER_OR_OVER_FREQ       No
> -001  REMOTE_EMERGENCY_PWR_OFF        No
> -001  REMOTE_GO_TO_BYPASS     No
> -001  BUILDING_ALARM_6        No
> -001  BUILDING_ALARM_5        No
> -001  BUILDING_ALARM_4        No
> -001  BUILDING_ALARM_3        No
> -001  BUILDING_ALARM_2        No
> -001  BUILDING_ALARM_1        No
> -001  STATIC_SWITCH_OVER_TEMP No
> -001  CHARGER_OVER_TEMP       No
> -001  CHARGER_LOGIC_PWR_FAIL  No
> -001  CHARGER_OVER_VOLTAGE_OR_CURRENT No
> 0004  INVERTER_OVER_TEMP      Yes
> 0005  OUTPUT_OVERLOAD Yes
> 0006  RECTIFIER_INPUT_OVER_CURRENT    Yes
> -001  INVERTER_OUTPUT_OVER_CURRENT    No
> 0007  DC_LINK_OVER_VOLTAGE    Yes
> 0008  DC_LINK_UNDER_VOLTAGE   Yes
> -001  RECTIFIER_FAILED        No
> -001  INVERTER_FAULT  No
> -001  BATTERY_CONNECTOR_FAIL  No
> -001  BYPASS_BREAKER_FAIL     No
> 0009  CHARGER_FAIL    Yes
> -001  RAMP_UP_FAILED  No
> -001  STATIC_SWITCH_FAILED    No
> -001  ANALOG_AD_REF_FAIL      No
> -001  BYPASS_UNCALIBRATED     No
> -001  RECTIFIER_UNCALIBRATED  No
> -001  OUTPUT_UNCALIBRATED     No
> -001  INVERTER_UNCALIBRATED   No
> -001  DC_VOLT_UNCALIBRATED    No
> -001  OUTPUT_CURRENT_UNCALIBRATED     No
> -001  RECTIFIER_CURRENT_UNCALIBRATED  No
> -001  BATTERY_CURRENT_UNCALIBRATED    No
> -001  INVERTER_ON_OFF_STAT_FAIL       No
> -001  BATTERY_CURRENT_LIMIT   No
> 0010  INVERTER_STARTUP_FAIL   Yes
> -001  ANALOG_BOARD_AD_STAT_FAIL       No
> 0011  OUTPUT_CURRENT_OVER_100 Yes
> -001  BATTERY_GROUND_FAULT    No
> -001  WAITING_FOR_CHARGER_SYNC        No
> -001  NV_RAM_FAIL     No
> -001  ANALOG_BOARD_AD_TIMEOUT No
> -001  SHUTDOWN_IMMINENT       No
> -001  BATTERY_LOW     No
> 0012  UTILITY_FAIL    Yes
> -001  OUTPUT_SHORT_CIRCUIT    No
> -001  UTILITY_NOT_PRESENT     No
> -001  FULL_TIME_CHARGING      No
> -001  FAST_BYPASS_COMMAND     No
> -001  AD_ERROR        No
> -001  INTERNAL_COM_FAIL       No
> -001  RECTIFIER_SELFTEST_FAIL No
> -001  RECTIFIER_EEPROM_FAIL   No
> -001  RECTIFIER_EPROM_FAIL    No
> -001  INPUT_LINE_VOLTAGE_LOSS No
> -001  BATTERY_DC_OVER_VOLTAGE No
> -001  POWER_SUPPLY_OVER_TEMP  No
> -001  POWER_SUPPLY_FAIL       No
> -001  POWER_SUPPLY_5V_FAIL    No
> -001  POWER_SUPPLY_12V_FAIL   No
> -001  HEATSINK_OVER_TEMP      No
> -001  HEATSINK_TEMP_SENSOR_FAIL       No
> -001  RECTIFIER_CURRENT_OVER_125      No
> -001  RECTIFIER_FAULT_INTERRUPT_FAIL  No
> -001  RECTIFIER_POWER_CAPASITOR_FAIL  No
> -001  INVERTER_PROGRAM_STACK_ERROR    No
> -001  INVERTER_BOARD_SELFTEST_FAIL    No
> -001  INVERTER_AD_SELFTEST_FAIL       No
> -001  INVERTER_RAM_SELFTEST_FAIL      No
> -001  NV_MEMORY_CHECKSUM_FAIL No
> -001  PROGRAM_CHECKSUM_FAIL   No
> -001  INVERTER_CPU_SELFTEST_FAIL      No
> -001  NETWORK_NOT_RESPONDING  No
> -001  FRONT_PANEL_SELFTEST_FAIL       No
> -001  NODE_EEPROM_VERIFICATION_ERROR  No
> -001  OUTPUT_AC_OVER_VOLT_TEST_FAIL   No
> -001  OUTPUT_DC_OVER_VOLTAGE  No
> 0013  INPUT_PHASE_ROTATION_ERROR      Yes
> -001  INVERTER_RAMP_UP_TEST_FAILED    No
> -001  INVERTER_OFF_COMMAND    No
> -001  INVERTER_ON_COMMAND     No
> -001  TO_BYPASS_COMMAND       No
> -001  FROM_BYPASS_COMMAND     No
> -001  AUTO_MODE_COMMAND       No
> -001  EMERGENCY_SHUTDOWN_COMMAND      No
> -001  SETUP_SWITCH_OPEN       No
> -001  INVERTER_OVER_VOLT_INT  No
> -001  INVERTER_UNDER_VOLT_INT No
> -001  ABSOLUTE_DCOV_ACOV      No
> -001  PHASE_A_CURRENT_LIMIT   No
> -001  PHASE_B_CURRENT_LIMIT   No
> -001  PHASE_C_CURRENT_LIMIT   No
> 0014  BYPASS_NOT_AVAILABLE    Yes
> -001  RECTIFIER_BREAKER_OPEN  No
> -001  BATTERY_CONTACTOR_OPEN  No
> -001  INVERTER_CONTACTOR_OPEN No
> -001  BYPASS_BREAKER_OPEN     No
> -001  INV_BOARD_ACOV_INT_TEST_FAIL    No
> -001  INVERTER_OVER_TEMP_TRIP No
> -001  INV_BOARD_ACUV_INT_TEST_FAIL    No
> -001  INVERTER_VOLTAGE_FEEDBACK_ERROR No
> -001  DC_UNDER_VOLTAGE_TIMEOUT        No
> -001  AC_UNDER_VOLTAGE_TIMEOUT        No
> -001  DC_UNDER_VOLTAGE_WHILE_CHARGE   No
> -001  INVERTER_VOLTAGE_BIAS_ERROR     No
> -001  RECTIFIER_PHASE_ROTATION        No
> -001  BYPASS_PHASER_ROTATION  No
> -001  SYSTEM_INTERFACE_BOARD_FAIL     No
> -001  PARALLEL_BOARD_FAIL     No
> -001  LOST_LOAD_SHARING_PHASE_A       No
> -001  LOST_LOAD_SHARING_PHASE_B       No
> -001  LOST_LOAD_SHARING_PHASE_C       No
> -001  DC_OVER_VOLTAGE_TIMEOUT No
> 0015  BATTERY_TOTALLY_DISCHARGED      Yes
> -001  INVERTER_PHASE_BIAS_ERROR       No
> -001  INVERTER_VOLTAGE_BIAS_ERROR_2   No
> -001  DC_LINK_BLEED_COMPLETE  No
> -001  LARGE_CHARGER_INPUT_CURRENT     No
> -001  INV_VOLT_TOO_LOW_FOR_RAMP_LEVEL No
> -001  LOSS_OF_REDUNDANCY      No
> -001  LOSS_OF_SYNC_BUS        No
> -001  RECTIFIER_BREAKER_SHUNT_TRIP    No
> -001  LOSS_OF_CHARGER_SYNC    No
> -001  INVERTER_LOW_LEVEL_TEST_TIMEOUT No
> -001  OUTPUT_BREAKER_OPEN     No
> -001  CONTROL_POWER_ON        No
> -001  INVERTER_ON     No
> -001  CHARGER_ON      No
> -001  BYPASS_ON       No
> -001  BYPASS_POWER_LOSS       No
> -001  ON_MANUAL_BYPASS        No
> -001  BYPASS_MANUAL_TURN_OFF  No
> -001  INVERTER_BLEEDING_DC_LINK_VOLT  No
> -001  CPU_ISR_ERROR   No
> -001  SYSTEM_ISR_RESTART      No
> -001  PARALLEL_DC     No
> -001  BATTERY_NEEDS_SERVICE   No
> -001  BATTERY_CHARGING        No
> -001  BATTERY_NOT_CHARGED     No
> -001  DISABLED_BATTERY_TIME   No
> -001  SERIES_7000_ENABLE      No
> -001  OTHER_UPS_ON    No
> -001  PARALLEL_INVERTER       No
> -001  UPS_IN_PARALLEL No
> -001  OUTPUT_BREAKER_REALY_FAIL       No
> -001  CONTROL_POWER_OFF       No
> -001  LEVEL_2_OVERLOAD_PHASE_A        No
> -001  LEVEL_2_OVERLOAD_PHASE_B        No
> -001  LEVEL_2_OVERLOAD_PHASE_C        No
> -001  LEVEL_3_OVERLOAD_PHASE_A        No
> -001  LEVEL_3_OVERLOAD_PHASE_B        No
> -001  LEVEL_3_OVERLOAD_PHASE_C        No
> -001  LEVEL_4_OVERLOAD_PHASE_A        No
> -001  LEVEL_4_OVERLOAD_PHASE_B        No
> -001  LEVEL_4_OVERLOAD_PHASE_C        No
> 0016  UPS_ON_BATTERY  Yes
> 0017  UPS_ON_BYPASS   Yes
> -001  LOAD_DUMPED     No
> -001  LOAD_ON_INVERTER        No
> -001  UPS_ON_COMMAND  No
> -001  UPS_OFF_COMMAND No
> -001  LOW_BATTERY_SHUTDOWN    No
> -001  AUTO_ON_ENABLED No
> -001  SOFTWARE_INCOMPABILITY_DETECTED No
> -001  INVERTER_TEMP_SENSOR_FAILED     No
> -001  DC_START_OCCURED        No
> -001  IN_PARALLEL_OPERATION   No
> -001  SYNCING_TO_BYPASS       No
> -001  RAMPING_UPS_UP  No
> -001  INVERTER_ON_DELAY       No
> -001  CHARGER_ON_DELAY        No
> -001  WAITING_FOR_UTIL_INPUT  No
> -001  CLOSE_BYPASS_BREAKER    No
> -001  TEMPORARY_BYPASS_OPERATION      No
> -001  SYNCING_TO_OUTPUT       No
> -001  BYPASS_FAILURE  No
> -001  AUTO_OFF_COMMAND_EXECUTED       No
> -001  AUTO_ON_COMMAND_EXECUTED        No
> -001  BATTERY_TEST_FAILED     No
> 0018  FUSE_FAIL       Yes
> -001  FAN_FAIL        No
> -001  SITE_WIRING_FAULT       No
> -001  BACKFEED_CONTACTOR_FAIL No
> -001  ON_BUCK No
> -001  ON_BOOST        No
> -001  ON_DOUBLE_BOOST No
> -001  BATTERIES_DISCONNECTED  No
> 
> 
> -Steve
> 


_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser