On Jul 10, 2009, at 04.37, Arjen de Korte wrote:
Citeren ben thielsen <[email protected]>:
[...]
some additional information - i've since added another smart-ups
1500 (not xlm), connected via usb to this same server, and it draws
the voltage graph without incident.
The latter is useful information, since it means that the problems
is probably in the values reported by the 'apcsmart' and 'usbhid-
ups' drivers that you're using to monitor these devices. Could you
post the 'upsc' output for both?
Chances are that the difference is in the reported values for the
'battery.voltage(.*)' values. It might confuse upsimage.cgi when it
tries to calculate 'battery.voltage.minimum' and
'battery.voltage.maximum' (those are not reported by either driver),
which is needed to draw the scale of the battery voltage graph.
working voltage graph:
[ups2]
driver = usbhid-ups
port = auto
>upsc u...@upsmon
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 50
battery.mfr.date: 2003/07/01
battery.runtime: 1920
battery.runtime.low: 120
battery.temperature: 25.2
battery.type: PbAc
battery.voltage: 27.7
battery.voltage.nominal: 24.0
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.4.1
driver.version.data: APC HID 0.93
driver.version.internal: 0.34
input.voltage: 123.8
output.voltage: 123.8
output.voltage.nominal: 120.0
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.firmware: 617.3.D
ups.firmware.aux: 1.5
ups.load: 46.1
ups.mfr: American Power Conversion
ups.mfr.date: 2003/07/01
ups.model: Smart-UPS 1500 RM
ups.productid: 0002
ups.serial: AS0327210919
ups.status: OL
ups.test.result: No test initiated
ups.timer.reboot: -1
ups.timer.shutdown: -1
ups.vendorid: 051d
non-working voltage graph:
[ups4]
driver = snmp-ups
port = ups4
community = xxxxxxxxxx
snmp_version = v1
pollfreq = 5
>upsc u...@upsmon
ambient.humidity: -1.00
ambient.temperature: 27.8
battery.charge: 100.00
battery.charge.restart: 0
battery.current: 0.00
battery.date: 01/16/07
battery.packs: 0.00
battery.packs.bad: 0.00
battery.runtime: 1380.00
battery.runtime.low: 120
battery.voltage: 55.00
battery.voltage.nominal: 0.00
driver.name: snmp-ups
driver.parameter.pollfreq: 5
driver.parameter.pollinterval: 2
driver.parameter.port: ups4
driver.parameter.snmp_version: v1
driver.version: 2.4.1
driver.version.internal: 0.44
input.frequency: 0.00
input.L1-L2.voltage: 0.00
input.L1-L2.voltage.maximum: 0.00
input.L1-L2.voltage.minimum: 0.00
input.L1.current: 0.00
input.L1.current.maximum: 0.00
input.L1.current.minimum: 0.00
input.phases: 0
input.sensitivity: high
input.transfer.high: 127
input.transfer.low: 106
input.voltage: 120.00
output.current: 6.00
output.frequency: 60.00
output.L1-L2.voltage: 0.00
output.L1.current: 0.00
output.L1.current.maximum: 0.00
output.L1.current.minimum: 0.00
output.L1.power: 0.00
output.L1.power.maximum: 0.00
output.L1.power.maximum.percent: 0.00
output.L1.power.minimum: 0.00
output.L1.power.minimum.percent: 0.00
output.L1.power.percent: 0.00
output.phases: 0
output.voltage: 120.00
output.voltage.nominal: 120
ups.delay.shutdown: 90
ups.delay.start: 0
ups.firmware: 716.3.D
ups.id: ups4
ups.load: 54.00
ups.mfr: APC
ups.mfr.date: 01/16/07
ups.model: Smart-UPS 1500 XLM
ups.serial: QS0703121476
ups.status: OL
ups.temperature: 25.00
ups.test.result: Ok
-ben