Citeren benjamin thielsen <[email protected]>:
aha - thank you, that seems to have done the trick. i suppose that
dividing by zero would also explain the floating point error.
Yes. That tipped me off that there might be something wrong in the
values reported by the UPS.
regarding the values you've specified above for the override and
defaults - how are those determined?
Your UPS reports a battery voltage of 55 V. Assuming this is correct,
this would be right what you'd expect for a 48 V nominal lead acid
battery (24 cells) that is fully charged (depending on the vendor,
2.27 - 2.30 V per cell). The minimum cell voltage is where the UPS
shuts down to protect the batteries for deep discharge (1.60 - 1.80 V
per cell). If 'battery.voltage.nominal' is provided, both will be
calculated automatically if not reported by the driver, but I'd rather
make this explicit in the configuration.
What remains is the question if this is a problem in the snmp-ups
driver or the UPS. I honestly don't know.
well, if the output of snmpwalk is any indication, it appears that
snmp-ups is accurately passing on values:
snmpwalk -v1 -c xxxxxxxxxx -m '/usr/share/snmp/mibs/powernet391.mib'
ups4 .1.3.6.1.4.1 | grep -i nominal
PowerNet-MIB::upsAdvBatteryNominalVoltage.0 = INTEGER: 0
That sucks, but this also explains the other weird values that are
reported. I noticed quite a couple of firmware updates for this UPS on
the APC site. It might be worthwhile to check if this fixes things.
Best regards, Arjen
--
Please keep list traffic on the list
_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser