Yes, I can test on trunk or on a patched version, but I cannot shut down or restart this particular UPS during the day. Hopefully we won't need to do that to figure out the Report 89 / Report 90 stuff.
Would you like me to run off of stable or devel? Also, can I check out stable with subversion/git, or should I just download it manually? -Zach On 03/05/2012 09:58 AM, Arnaud Quette wrote: > Hi Zach, > > 2012/2/29 Zach La Celle <[email protected]>: >> On 02/27/2012 06:38 AM, Arnaud Quette wrote: >>> 2012/2/21 Zach La Celle <[email protected]>: >>>> I figured out the cause of this problem: incorrect permissions on the >>>> USB device. At least, this seemed to fix the problem I had when I >>>> manually tried to run upsdrvctl and got a permission denied. The other >>>> problems may have been solved simply by reinstalling nut, not sure. >>>> >>>> It no longer returns the temperature, line frequency, or load >>>> percentage, but this is fine for now. >>>> >>>> In case anybody needs to fix their permissions in Debian-based system, >>>> run lsusb to get your vendorId, productId, and usb bus address, then >>>> check /dev/bus/usb/<bus number>/<device number> to see its permissions. >>>> Mine were 664: changing them to 666 worked for me. To give an example >>>> of my udev rule in /etc/udev/rules.d/90-APCUps.rules: >>>> >>>> # APC USB device >>>> SUBSYSTEM=="usb", ATTR{idVendor}=="051d", ATTR{idProduct}="0003", >>>> MODE="0666" >>> >>> this (udev support) is automatically included in for version that >>> supports the device (generated automatically). >>> Ie, in your case, as of nut 2.6.0. >>> >>>> Hope this helps. Still not sure what was happening at first. Also, if >>>> there's any ways to get upsc to read more values from the UPS, let me know. >>> >>> can you please post an output of "/path/to/usbhid-ups -D -a ..." >>> just to see if there is more data to retrieve. >>> >>> cheers, >>> Arnaud >> >> Here's some more data for you. I'm not sure if it's better to post >> files somewhere on the web or just paste text in: for now, I'm pasting text. >> >> Notably missing from upsc (versus when using the other driver with my >> other, older APC UPS') are line frequency, load percentage, and temperature. >> >> Output of upsc rack1ups: >> >> battery.charge: 100 >> battery.charge.low: 10 >> battery.charge.warning: 50 >> battery.runtime: 5220 >> battery.runtime.low: 120 >> battery.type: PbAc >> battery.voltage: 54.8 >> battery.voltage.nominal: 24.0 >> device.mfr: American Power Conversion >> device.model: Smart-UPS 3000 >> device.serial: ################ >> device.type: ups >> driver.name: usbhid-ups >> driver.parameter.pollfreq: 30 >> driver.parameter.pollinterval: 2 >> driver.parameter.port: auto >> driver.parameter.productid: 0003 >> driver.parameter.vendorid: 051d >> driver.version: 2.4.3 >> driver.version.data: APC HID 0.95 >> driver.version.internal: 0.34 >> ups.beeper.status: enabled >> ups.delay.shutdown: 20 >> ups.firmware: UPS 06.5 / ID=18 >> ups.mfr: American Power Conversion >> ups.mfr.date: 2011/08/19 >> ups.model: Smart-UPS 3000 >> ups.productid: 0003 >> ups.serial: ################# >> ups.status: OL >> ups.timer.reboot: -1 >> ups.timer.shutdown: -1 >> ups.vendorid: 051d >> >> Output of /lib/nut/usbhid-ups -D -a rack1ups: >> >> 0.000000 debug level is '1' >> 0.014536 upsdrv_initups... >> 0.213175 Using subdriver: APC HID 0.95 >> 0.214015 Path: UPS.PowerSummary.iProduct, Type: Feature, ReportID: >> 0x01, Offset: 0, Size: 8, Value: 2.000000 >> 0.215007 Path: UPS.PowerSummary.iSerialNumber, Type: Feature, >> ReportID: 0x02, Offset: 0, Size: 8, Value: 3.000000 >> 0.216004 Path: UPS.PowerSummary.iManufacturer, Type: Feature, >> ReportID: 0x03, Offset: 0, Size: 8, Value: 1.000000 >> 0.217008 Path: UPS.PowerSummary.iOEMInformation, Type: Feature, >> ReportID: 0x04, Offset: 0, Size: 8, Value: 1.000000 >> 0.217976 Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, >> ReportID: 0x05, Offset: 0, Size: 8, Value: 4.000000 >> 0.218980 Path: UPS.PowerSummary.Rechargeable, Type: Feature, >> ReportID: 0x06, Offset: 0, Size: 8, Value: 1.000000 >> 0.219003 Path: UPS.PowerSummary.CapacityMode, Type: Feature, >> ReportID: 0x06, Offset: 8, Size: 8, Value: 2.000000 >> 0.220011 Path: UPS.PowerSummary.DesignCapacity, Type: Feature, >> ReportID: 0x0e, Offset: 0, Size: 8, Value: 100.000000 >> 0.220040 Path: UPS.PowerSummary.FullChargeCapacity, Type: Feature, >> ReportID: 0x0e, Offset: 8, Size: 8, Value: 100.000000 >> 0.221016 Path: UPS.PowerSummary.RemainingCapacity, Type: Input, >> ReportID: 0x0c, Offset: 0, Size: 8, Value: 100.000000 >> 0.221044 Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, >> ReportID: 0x0c, Offset: 0, Size: 8, Value: 100.000000 >> 0.222009 Path: UPS.PowerSummary.CapacityGranularity1, Type: Feature, >> ReportID: 0x10, Offset: 0, Size: 8, Value: 1.000000 >> 0.222036 Path: UPS.PowerSummary.CapacityGranularity2, Type: Feature, >> ReportID: 0x10, Offset: 8, Size: 8, Value: 1.000000 >> 0.223006 Path: UPS.PowerSummary.WarningCapacityLimit, Type: Feature, >> ReportID: 0x0f, Offset: 0, Size: 8, Value: 50.000000 >> 0.224009 Path: UPS.PowerSummary.RemainingCapacityLimit, Type: >> Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 10.000000 >> 0.225006 Path: UPS.PowerSummary.ManufacturerDate, Type: Feature, >> ReportID: 0x09, Offset: 0, Size: 16, Value: 16147.000000 >> 0.225983 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, >> ReportID: 0x0d, Offset: 0, Size: 16, Value: 5220.000000 >> 0.226008 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, >> ReportID: 0x0d, Offset: 0, Size: 16, Value: 5220.000000 >> 0.226979 Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature, >> ReportID: 0x12, Offset: 0, Size: 16, Value: -1.000000 >> 0.227979 Path: UPS.PowerSummary.DelayBeforeReboot, Type: Feature, >> ReportID: 0x13, Offset: 0, Size: 24, Value: -1.000000 >> 0.228977 Path: UPS.PowerSummary.RemainingTimeLimit, Type: Input, >> ReportID: 0x08, Offset: 0, Size: 24, Value: 120.000000 >> 0.229001 Path: UPS.PowerSummary.RemainingTimeLimit, Type: Feature, >> ReportID: 0x08, Offset: 0, Size: 24, Value: 120.000000 >> 0.230007 Path: UPS.PowerSummary.ConfigVoltage, Type: Feature, >> ReportID: 0x0a, Offset: 0, Size: 16, Value: 24.000000 >> 0.231010 Path: UPS.PowerSummary.Voltage, Type: Feature, ReportID: >> 0x0b, Offset: 0, Size: 16, Value: 54.800000 >> 0.232004 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Input, >> ReportID: 0x14, Offset: 0, Size: 8, Value: 2.000000 >> 0.232031 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, >> ReportID: 0x14, Offset: 0, Size: 8, Value: 2.000000 >> 0.232980 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input, >> ReportID: 0x07, Offset: 0, Size: 1, Value: 0.000000 >> 0.233004 Path: UPS.PowerSummary.PresentStatus.Charging, Type: >> Feature, ReportID: 0x07, Offset: 0, Size: 1, Value: 0.000000 >> 0.233019 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: >> Input, ReportID: 0x07, Offset: 1, Size: 1, Value: 0.000000 >> 0.233031 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: >> Feature, ReportID: 0x07, Offset: 1, Size: 1, Value: 0.000000 >> 0.233044 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input, >> ReportID: 0x07, Offset: 2, Size: 1, Value: 1.000000 >> 0.233057 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: >> Feature, ReportID: 0x07, Offset: 2, Size: 1, Value: 1.000000 >> 0.233073 Path: UPS.PowerSummary.PresentStatus.BatteryPresent, Type: >> Input, ReportID: 0x07, Offset: 3, Size: 1, Value: 1.000000 >> 0.233100 Path: UPS.PowerSummary.PresentStatus.BatteryPresent, Type: >> Feature, ReportID: 0x07, Offset: 3, Size: 1, Value: 1.000000 >> 0.233112 Path: >> UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input, >> ReportID: 0x07, Offset: 4, Size: 1, Value: 0.000000 >> 0.233122 Path: >> UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: >> Feature, ReportID: 0x07, Offset: 4, Size: 1, Value: 0.000000 >> 0.233133 Path: UPS.PowerSummary.PresentStatus.ShutdownRequested, >> Type: Input, ReportID: 0x07, Offset: 5, Size: 1, Value: 0.000000 >> 0.233143 Path: UPS.PowerSummary.PresentStatus.ShutdownRequested, >> Type: Feature, ReportID: 0x07, Offset: 5, Size: 1, Value: 0.000000 >> 0.233154 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: >> Input, ReportID: 0x07, Offset: 6, Size: 1, Value: 0.000000 >> 0.233164 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: >> Feature, ReportID: 0x07, Offset: 6, Size: 1, Value: 0.000000 >> 0.233175 Path: >> UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Input, >> ReportID: 0x07, Offset: 7, Size: 1, Value: 0.000000 >> 0.233185 Path: >> UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Feature, >> ReportID: 0x07, Offset: 7, Size: 1, Value: 0.000000 >> 0.233196 Path: UPS.PowerSummary.PresentStatus.CommunicationLost, >> Type: Input, ReportID: 0x07, Offset: 8, Size: 1, Value: 0.000000 >> 0.233206 Path: UPS.PowerSummary.PresentStatus.CommunicationLost, >> Type: Feature, ReportID: 0x07, Offset: 8, Size: 1, Value: 0.000000 >> 0.233217 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: >> Input, ReportID: 0x07, Offset: 9, Size: 1, Value: 0.000000 >> 0.233228 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: >> Feature, ReportID: 0x07, Offset: 9, Size: 1, Value: 0.000000 >> 0.233238 Path: UPS.PowerSummary.PresentStatus.Overload, Type: Input, >> ReportID: 0x07, Offset: 10, Size: 1, Value: 0.000000 >> 0.233248 Path: UPS.PowerSummary.PresentStatus.Overload, Type: >> Feature, ReportID: 0x07, Offset: 10, Size: 1, Value: 0.000000 >> 0.233259 Path: UPS.PowerSummary.PresentStatus.VoltageNotRegulated, >> Type: Input, ReportID: 0x07, Offset: 11, Size: 1, Value: 0.000000 >> 0.233270 Path: UPS.PowerSummary.PresentStatus.VoltageNotRegulated, >> Type: Feature, ReportID: 0x07, Offset: 11, Size: 1, Value: 0.000000 >> 0.233280 Path: UPS.PowerSummary.PresentStatus.ff860080, Type: Input, >> ReportID: 0x07, Offset: 12, Size: 1, Value: 0.000000 >> 0.233291 Path: UPS.PowerSummary.PresentStatus.ff860080, Type: >> Feature, ReportID: 0x07, Offset: 12, Size: 1, Value: 0.000000 >> 0.233980 Can't retrieve Report 89: Broken pipe >> 0.234002 Path: UPS.ff8600fd, Type: Input, ReportID: 0x89, Offset: 0, >> Size: 8 >> 0.234975 Can't retrieve Report 90: Broken pipe >> 0.234997 Path: UPS.ff8600fc, Type: Output, ReportID: 0x90, Offset: 0, >> Size: 8 >> Network UPS Tools - Generic HID driver 0.34 (2.4.3) >> USB communication driver 0.31 >> 0.235030 Detected a UPS: American Power Conversion/Smart-UPS 3000 >> FW:UPS 06.5 / ID=18 >> 0.239247 upsdrv_initinfo... >> 0.239265 upsdrv_updateinfo... >> 0.491006 Got 0 HID objects... >> 0.491032 Quick update... >> 0.491116 upsdrv_updateinfo... >> 0.744021 Got 0 HID objects... >> 0.744045 Quick update... >> 2.492938 upsdrv_updateinfo... >> 2.745105 Got 0 HID objects... >> 2.745129 Quick update... >> 4.494748 upsdrv_updateinfo... >> 4.747183 Got 0 HID objects... >> 4.747206 Quick update... >> 6.496560 upsdrv_updateinfo... >> 6.748274 Got 0 HID objects... >> 6.748299 Quick update... >> 8.328686 Signal 2: exiting >> 8.328728 upsdrv_cleanup... >> >> Hope this helps you. I'm complaining to APC about not releasing the >> MicroLink protocol, but somehow I don't think it will change their mind... > > a good try, but I'm inclined in thinking that they won't move! > >> Thanks. Let me know if there's anything I can do. > > yeah, I'd like to check what's beyond " Can't retrieve Report..." for > report 89 and 90. > would you be able to compile and test it on the trunk, possibly with > an additional patch? > > cheers, > Arnaud _______________________________________________ Nut-upsuser mailing list [email protected] http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser