On 02/27/2012 06:38 AM, Arnaud Quette wrote:
> 2012/2/21 Zach La Celle <[email protected]>:
>> I figured out the cause of this problem: incorrect permissions on the
>> USB device.  At least, this seemed to fix the problem I had when I
>> manually tried to run upsdrvctl and got a permission denied.  The other
>> problems may have been solved simply by reinstalling nut, not sure.
>>
>> It no longer returns the temperature, line frequency, or load
>> percentage, but this is fine for now.
>>
>> In case anybody needs to fix their permissions in Debian-based system,
>> run lsusb to get your vendorId, productId, and usb bus address, then
>> check /dev/bus/usb/<bus number>/<device number> to see its permissions.
>>  Mine were 664: changing them to 666 worked for me.  To give an example
>> of my udev rule in /etc/udev/rules.d/90-APCUps.rules:
>>
>> # APC USB device
>> SUBSYSTEM=="usb", ATTR{idVendor}=="051d", ATTR{idProduct}="0003",
>> MODE="0666"
> 
> this (udev support) is automatically included in for version that
> supports the device (generated automatically).
> Ie, in your case, as of nut 2.6.0.
> 
>> Hope this helps.  Still not sure what was happening at first.  Also, if
>> there's any ways to get upsc to read more values from the UPS, let me know.
> 
> can you please post an output of "/path/to/usbhid-ups -D -a ..."
> just to see if there is more data to retrieve.
> 
> cheers,
> Arnaud

Here's some more data for you.  I'm not sure if it's better to post
files somewhere on the web or just paste text in: for now, I'm pasting text.

Notably missing from upsc (versus when using the other driver with my
other, older APC UPS') are line frequency, load percentage, and temperature.

Output of upsc rack1ups:

battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 50
battery.runtime: 5220
battery.runtime.low: 120
battery.type: PbAc
battery.voltage: 54.8
battery.voltage.nominal: 24.0
device.mfr: American Power Conversion
device.model: Smart-UPS 3000
device.serial: ################
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.productid: 0003
driver.parameter.vendorid: 051d
driver.version: 2.4.3
driver.version.data: APC HID 0.95
driver.version.internal: 0.34
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.firmware: UPS 06.5 / ID=18
ups.mfr: American Power Conversion
ups.mfr.date: 2011/08/19
ups.model: Smart-UPS 3000
ups.productid: 0003
ups.serial: #################
ups.status: OL
ups.timer.reboot: -1
ups.timer.shutdown: -1
ups.vendorid: 051d

Output of /lib/nut/usbhid-ups -D -a rack1ups:

   0.000000     debug level is '1'
   0.014536     upsdrv_initups...
   0.213175     Using subdriver: APC HID 0.95
   0.214015     Path: UPS.PowerSummary.iProduct, Type: Feature, ReportID:
0x01, Offset: 0, Size: 8, Value: 2.000000
   0.215007     Path: UPS.PowerSummary.iSerialNumber, Type: Feature,
ReportID: 0x02, Offset: 0, Size: 8, Value: 3.000000
   0.216004     Path: UPS.PowerSummary.iManufacturer, Type: Feature,
ReportID: 0x03, Offset: 0, Size: 8, Value: 1.000000
   0.217008     Path: UPS.PowerSummary.iOEMInformation, Type: Feature,
ReportID: 0x04, Offset: 0, Size: 8, Value: 1.000000
   0.217976     Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature,
ReportID: 0x05, Offset: 0, Size: 8, Value: 4.000000
   0.218980     Path: UPS.PowerSummary.Rechargeable, Type: Feature,
ReportID: 0x06, Offset: 0, Size: 8, Value: 1.000000
   0.219003     Path: UPS.PowerSummary.CapacityMode, Type: Feature,
ReportID: 0x06, Offset: 8, Size: 8, Value: 2.000000
   0.220011     Path: UPS.PowerSummary.DesignCapacity, Type: Feature,
ReportID: 0x0e, Offset: 0, Size: 8, Value: 100.000000
   0.220040     Path: UPS.PowerSummary.FullChargeCapacity, Type: Feature,
ReportID: 0x0e, Offset: 8, Size: 8, Value: 100.000000
   0.221016     Path: UPS.PowerSummary.RemainingCapacity, Type: Input,
ReportID: 0x0c, Offset: 0, Size: 8, Value: 100.000000
   0.221044     Path: UPS.PowerSummary.RemainingCapacity, Type: Feature,
ReportID: 0x0c, Offset: 0, Size: 8, Value: 100.000000
   0.222009     Path: UPS.PowerSummary.CapacityGranularity1, Type: Feature,
ReportID: 0x10, Offset: 0, Size: 8, Value: 1.000000
   0.222036     Path: UPS.PowerSummary.CapacityGranularity2, Type: Feature,
ReportID: 0x10, Offset: 8, Size: 8, Value: 1.000000
   0.223006     Path: UPS.PowerSummary.WarningCapacityLimit, Type: Feature,
ReportID: 0x0f, Offset: 0, Size: 8, Value: 50.000000
   0.224009     Path: UPS.PowerSummary.RemainingCapacityLimit, Type:
Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 10.000000
   0.225006     Path: UPS.PowerSummary.ManufacturerDate, Type: Feature,
ReportID: 0x09, Offset: 0, Size: 16, Value: 16147.000000
   0.225983     Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input,
ReportID: 0x0d, Offset: 0, Size: 16, Value: 5220.000000
   0.226008     Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature,
ReportID: 0x0d, Offset: 0, Size: 16, Value: 5220.000000
   0.226979     Path: UPS.PowerSummary.DelayBeforeShutdown, Type: Feature,
ReportID: 0x12, Offset: 0, Size: 16, Value: -1.000000
   0.227979     Path: UPS.PowerSummary.DelayBeforeReboot, Type: Feature,
ReportID: 0x13, Offset: 0, Size: 24, Value: -1.000000
   0.228977     Path: UPS.PowerSummary.RemainingTimeLimit, Type: Input,
ReportID: 0x08, Offset: 0, Size: 24, Value: 120.000000
   0.229001     Path: UPS.PowerSummary.RemainingTimeLimit, Type: Feature,
ReportID: 0x08, Offset: 0, Size: 24, Value: 120.000000
   0.230007     Path: UPS.PowerSummary.ConfigVoltage, Type: Feature,
ReportID: 0x0a, Offset: 0, Size: 16, Value: 24.000000
   0.231010     Path: UPS.PowerSummary.Voltage, Type: Feature, ReportID:
0x0b, Offset: 0, Size: 16, Value: 54.800000
   0.232004     Path: UPS.PowerSummary.AudibleAlarmControl, Type: Input,
ReportID: 0x14, Offset: 0, Size: 8, Value: 2.000000
   0.232031     Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature,
ReportID: 0x14, Offset: 0, Size: 8, Value: 2.000000
   0.232980     Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input,
ReportID: 0x07, Offset: 0, Size: 1, Value: 0.000000
   0.233004     Path: UPS.PowerSummary.PresentStatus.Charging, Type:
Feature, ReportID: 0x07, Offset: 0, Size: 1, Value: 0.000000
   0.233019     Path: UPS.PowerSummary.PresentStatus.Discharging, Type:
Input, ReportID: 0x07, Offset: 1, Size: 1, Value: 0.000000
   0.233031     Path: UPS.PowerSummary.PresentStatus.Discharging, Type:
Feature, ReportID: 0x07, Offset: 1, Size: 1, Value: 0.000000
   0.233044     Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input,
ReportID: 0x07, Offset: 2, Size: 1, Value: 1.000000
   0.233057     Path: UPS.PowerSummary.PresentStatus.ACPresent, Type:
Feature, ReportID: 0x07, Offset: 2, Size: 1, Value: 1.000000
   0.233073     Path: UPS.PowerSummary.PresentStatus.BatteryPresent, Type:
Input, ReportID: 0x07, Offset: 3, Size: 1, Value: 1.000000
   0.233100     Path: UPS.PowerSummary.PresentStatus.BatteryPresent, Type:
Feature, ReportID: 0x07, Offset: 3, Size: 1, Value: 1.000000
   0.233112     Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input,
ReportID: 0x07, Offset: 4, Size: 1, Value: 0.000000
   0.233122     Path:
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type:
Feature, ReportID: 0x07, Offset: 4, Size: 1, Value: 0.000000
   0.233133     Path: UPS.PowerSummary.PresentStatus.ShutdownRequested,
Type: Input, ReportID: 0x07, Offset: 5, Size: 1, Value: 0.000000
   0.233143     Path: UPS.PowerSummary.PresentStatus.ShutdownRequested,
Type: Feature, ReportID: 0x07, Offset: 5, Size: 1, Value: 0.000000
   0.233154     Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type:
Input, ReportID: 0x07, Offset: 6, Size: 1, Value: 0.000000
   0.233164     Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type:
Feature, ReportID: 0x07, Offset: 6, Size: 1, Value: 0.000000
   0.233175     Path:
UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Input,
ReportID: 0x07, Offset: 7, Size: 1, Value: 0.000000
   0.233185     Path:
UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Feature,
ReportID: 0x07, Offset: 7, Size: 1, Value: 0.000000
   0.233196     Path: UPS.PowerSummary.PresentStatus.CommunicationLost,
Type: Input, ReportID: 0x07, Offset: 8, Size: 1, Value: 0.000000
   0.233206     Path: UPS.PowerSummary.PresentStatus.CommunicationLost,
Type: Feature, ReportID: 0x07, Offset: 8, Size: 1, Value: 0.000000
   0.233217     Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type:
Input, ReportID: 0x07, Offset: 9, Size: 1, Value: 0.000000
   0.233228     Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type:
Feature, ReportID: 0x07, Offset: 9, Size: 1, Value: 0.000000
   0.233238     Path: UPS.PowerSummary.PresentStatus.Overload, Type: Input,
ReportID: 0x07, Offset: 10, Size: 1, Value: 0.000000
   0.233248     Path: UPS.PowerSummary.PresentStatus.Overload, Type:
Feature, ReportID: 0x07, Offset: 10, Size: 1, Value: 0.000000
   0.233259     Path: UPS.PowerSummary.PresentStatus.VoltageNotRegulated,
Type: Input, ReportID: 0x07, Offset: 11, Size: 1, Value: 0.000000
   0.233270     Path: UPS.PowerSummary.PresentStatus.VoltageNotRegulated,
Type: Feature, ReportID: 0x07, Offset: 11, Size: 1, Value: 0.000000
   0.233280     Path: UPS.PowerSummary.PresentStatus.ff860080, Type: Input,
ReportID: 0x07, Offset: 12, Size: 1, Value: 0.000000
   0.233291     Path: UPS.PowerSummary.PresentStatus.ff860080, Type:
Feature, ReportID: 0x07, Offset: 12, Size: 1, Value: 0.000000
   0.233980     Can't retrieve Report 89: Broken pipe
   0.234002     Path: UPS.ff8600fd, Type: Input, ReportID: 0x89, Offset: 0,
Size: 8
   0.234975     Can't retrieve Report 90: Broken pipe
   0.234997     Path: UPS.ff8600fc, Type: Output, ReportID: 0x90, Offset: 0,
Size: 8
Network UPS Tools - Generic HID driver 0.34 (2.4.3)
USB communication driver 0.31
   0.235030     Detected a UPS: American Power Conversion/Smart-UPS 3000
FW:UPS 06.5 / ID=18
   0.239247     upsdrv_initinfo...
   0.239265     upsdrv_updateinfo...
   0.491006     Got 0 HID objects...
   0.491032     Quick update...
   0.491116     upsdrv_updateinfo...
   0.744021     Got 0 HID objects...
   0.744045     Quick update...
   2.492938     upsdrv_updateinfo...
   2.745105     Got 0 HID objects...
   2.745129     Quick update...
   4.494748     upsdrv_updateinfo...
   4.747183     Got 0 HID objects...
   4.747206     Quick update...
   6.496560     upsdrv_updateinfo...
   6.748274     Got 0 HID objects...
   6.748299     Quick update...
   8.328686     Signal 2: exiting
   8.328728     upsdrv_cleanup...

Hope this helps you.  I'm complaining to APC about not releasing the
MicroLink protocol, but somehow I don't think it will change their mind...

Thanks.  Let me know if there's anything I can do.

-Zach