On Jul 31, 2013, at 3:36 AM, Pavel Potcheptsov (EKTOS) wrote:

> Does it looks good?

I think so - 40.8 volts with a nominal of 36 volts is 13.6 V/cell, which agrees 
with the 100% charge value. Hopefully the line voltages and frequency make 
sense for your region.

> Another question what does riello experimental driver warning mean?

We add that to all new drivers. This driver was written by Elio Parisi of 
Riello, and they have published the protocol documents, so it is probably less 
experimental than the drivers which have been developed without that sort of 
help.

That said, this driver hasn't had as much testing as the others, and a lot of 
the code appears to have special cases for certain models.

> Does it affect shutdown procedure?

It shouldn't. However, I would recommend testing the shutdown procedure to be 
sure.

> Should I install riello driver on Slave computers, which powered from same 
> UPS or just setup their as usual slave (just upsmon.conf)?

No, the drivers are only necessary on the computer(s) which are communicating 
directly with the UPS.

-- 