Ran with gdb:

gdb /lib/nut/usbhid-ups

run -u nut -a nailbunny -x bus=010 -x vendorid=0764 -x productid=0501 -DDDDD


Same result as when I ran normally.  Driver just stops communicating with no 
errors or messages in the logs.  Not sure where to go from here as I'm not 
seeing anything to follow up on.


________________________________
From: Daniel Shields <[email protected]>
Sent: Friday, October 14, 2016 12:02 AM
To: Charles Lepple
Cc: nut-upsuser@lists. alioth. debian. org
Subject: Re: [Nut-upsuser] Data Stale at random intervals


Just an update, these messages are in the syslog when nut is no longer able to 
communicate with the server:


Oct 14 01:41:59 golgotha upsmon[1300]: Poll UPS [nailbunny@localhost] failed - 
Data stale
Oct 14 01:42:04 golgotha upsmon[1300]: Poll UPS [nailbunny@localhost] failed - 
Data stale
Oct 14 01:42:09 golgotha upsmon[1300]: Poll UPS [nailbunny@localhost] failed - 
Data stale
Oct 14 01:42:14 golgotha upsmon[1300]: Poll UPS [nailbunny@localhost] failed - 
Data stale
Oct 14 01:42:19 golgotha upsmon[1300]: Poll UPS [nailbunny@localhost] failed - 
Data stale
Oct 14 01:42:19 golgotha upsmon[1300]: UPS nailbunny@localhost is unavailable
Oct 14 01:42:24 golgotha upsmon[1300]: Poll UPS [nailbunny@localhost] failed - 
Data stale
Oct 14 01:42:29 golgotha upsmon[1300]: Poll UPS [nailbunny@localhost] failed - 
Data stale
Oct 14 01:42:34 golgotha upsmon[1300]: Poll UPS [nailbunny@localhost] failed - 
Data stale
Oct 14 01:42:39 golgotha upsmon[1300]: Poll UPS [nailbunny@localhost] failed - 
Data stale
Oct 14 01:42:41 golgotha upsd[1267]: Send ping to UPS [nailbunny] failed: 
Resource temporarily unavailable
Oct 14 01:42:43 golgotha upsd[1267]: Connected to UPS [nailbunny]: 
usbhid-ups-nailbunny
Oct 14 01:42:44 golgotha upsmon[1300]: Communications with UPS 
nailbunny@localhost established
Oct 14 01:42:59 golgotha upsd[1267]: Data for UPS [nailbunny] is stale - check 
driver
Oct 14 01:43:04 golgotha upsmon[1300]: Poll UPS [nailbunny@localhost] failed - 
Data stale
Oct 14 01:43:04 golgotha upsmon[1300]: Communications with UPS 
nailbunny@localhost lost
Oct 14 01:43:09 golgotha upsmon[1300]: Poll UPS [nailbunny@localhost] failed - 
Data stale
Oct 14 01:43:14 golgotha upsmon[1300]: Poll UPS [nailbunny@localhost] failed - 
Data stale
Oct 14 01:43:19 golgotha upsmon[1300]: Poll UPS [nailbunny@localhost] failed - 
Data stale


The server reconnects, but can't communicate due to the Data Stale.  I get the 
same result from trying to restart the nut-server service manually.  I have to 
stop and restart the service and it will work for a couple hours up to ~ 24 
sometimes.


________________________________
From: Daniel Shields <[email protected]>
Sent: Thursday, October 13, 2016 2:19 PM
To: Charles Lepple
Cc: nut-upsuser@lists. alioth. debian. org
Subject: Re: [Nut-upsuser] Data Stale at random intervals



Here are the results of a restart as well as a stop/start.  Seems like it may 
be the server?  I tried to run the nut-server service with gdb, but no luck 
getting it to work so far.  Thanks!

________________________________
From: Charles Lepple <[email protected]>
Sent: Wednesday, October 12, 2016 8:20 PM
To: Daniel Shields
Cc: nut-upsuser@lists. alioth. debian. org
Subject: Re: [Nut-upsuser] Data Stale at random intervals

On Oct 12, 2016, at 8:13 PM, Daniel Shields <[email protected]> wrote:
>
> Wow.  Okay, well I let the debug run all day.  Nothing in the logs even with 
> debug cranked to level 5.  Attached are the last 1000 lines before it quit.  
> I'm really stumped now.

gzipped and resent for the rest of the list.

Can you elaborate on how it quit? I don't see any error messages to that effect.

_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to