quick question: do you have the 0.7 delay on EVERY module after the
/presence time elapsed?
It is strange that I do not experience that.

No, the CRC16_errors and CRC16_tries should not increase every loop

CRC errors and tries are part of the Dallas (now Maxim) 1wire specification.
It ensures data integrity.
Here is the page on Maxim's website:

https://www.maximintegrated.com/en/design/technical-documents/app-notes/2/27.html

The way I understood it years ago when I was tinkering with it- and I
hope I remember right -, was:

If a low level 16 bit read (e.g. reading a temperature) - or write -
fails because the data on the bus is not correct, then the CRC16 error
gets increased by 1, and the operation gets retried.
An operation will be retried three times - resulting in an increased
operation time - which will be logged in /statistics/*read*/tries.x -
where 0 is the first re-try or /statistics/*write*/tries.x respectively
hence /tries.0 will be always greater than /tries.1 and /tries.2

 
you could read /statistics/CRC16_errors after every read or write and
print when the value increases to find out which module gives you the errors


On 08.08.20 19:07, Mick Sulley wrote:
>
> I have just run it again, sleep for 3 seconds after the
> simultaneous/temperature write and sleep 25 seconds at the end of the
> loop.  Presence is at 120 and I see a delay every 130 seconds or so. 
> The delay is on reading whichever parameter is first, so if I read
> present first then that is the 0.7 scan, the other parameters are <
> 0.1, but If I read type first then that is 0.7 sec, etc
>
> I am also reading CR16_errors and CR16_tries, these are the same and
> both increase by 8 each loop.  Is that normal?  Is there any
> documentation on this stuff, I can't find anything.
>
> Mick
>
> On 08/08/2020 08:46, Martin Patzak wrote:
>> Thanks Mick, great summary.
>>
>> Let me add to 4), that you only see the 0.7 sec delay, because you
>> read in a busy loop.
>> I read only every 30 seconds and I never see a delay.
>>
>> But timing your reads is a good practice because this way you catch
>> retries and maybe bus or sensor problems.
>> Additionally you can have a look in /statistics for retries and errors
>>
>> On 08.08.20 01:04, Mick Sulley wrote:
>>> Update on test findings.  Test setup was 19 - DS18B20 temperature, 2
>>> - DS2413 IO and 1 - DS2437 Voltage, Raspberry Pi4 with Sheepwalk
>>> RPi3 Adapter
>>>
>>> 1) /simultaneous/temperature does work, best to read latesttemp.
>>>
>>> 2) /settings/timeout/presence cannot be set or read via the owhttpd
>>> web page, you must use owwrite & owread
>>>
>>> 3) Reading values (after setting simultaneous) normally takes < 0.1
>>> seconds
>>>
>>> 4) After the /settings/timeout/presence interval the next read for
>>> every device will take around 0.7 seconds.  Note if you read
>>> multiple fields it is only the first one which takes the increased
>>> time.
>>>
>>> 5) The increased time after /settings/timeout/presence interval
>>> applies to all devices, not just temperature
>>>
>>>
>>> Mick
>>