Braidwood - we have not messed with the failed fuel yet.  Maybe in 10
years we will get to them.

 

________________________________

From: [email protected] [mailto:[email protected]] On Behalf
Of Erik P Simon
Sent: Wednesday, August 17, 2011 6:46 AM
To: [email protected]
Subject: Powernet: NUHOMS loading failed fuel

 

Surry Power Station wants to know if anyone has had to deal with loading
failed fuel into NUHOMS casks specifically the 32-PTH metal matrix type?
We have recently loaded 4 of 32 assemblies with known leakers and are
experiencing difficulties in vacuum drying the DSC due to high levels of
Kr-85. Our current configuration has the vacuum drying system directly
discharging to the Vent Stack 2 ( Vent Vent), there is no let down or
delay prior to the radiation monitor.

Thanks,

Erik

 

Erik Simon

Health Physics Shift Supervisor

Radiation Protection, Surry Power Station

 

Dominion Generation

Phone:  757-365-2672; Internal: 8-798-2672

Pager:  800-272-5643-3299; E-mail: [email protected]
<mailto:[email protected]> 

 

 


CONFIDENTIALITY NOTICE: This electronic message contains information
which may be legally confidential and/or privileged and does not in any
case represent a firm ENERGY COMMODITY bid or offer relating thereto
which binds the sender without an additional express written
confirmation to that effect. The information is intended solely for the
individual or entity named above and access by anyone else is
unauthorized. If you are not the intended recipient, any disclosure,
copying, distribution, or use of the contents of this information is
prohibited and may be unlawful. If you have received this electronic
transmission in error, please reply immediately to the sender that you
have received the message in error, and delete it. Thank you.




-----------------------------------------
**************************************************
This e-mail and any of its attachments may contain Exelon
Corporation proprietary information, which is privileged,
confidential, or subject to copyright belonging to the Exelon
Corporation family of Companies. 
This e-mail is intended solely for the use of the individual or
entity to which it is addressed.  If you are not the intended
recipient of this e-mail, you are hereby notified that any
dissemination, distribution, copying, or action taken in relation
to the contents of and attachments to this e-mail is strictly
prohibited and may be unlawful.  If you have received this e-mail
in error, please notify the sender immediately and permanently
delete the original and any copy of this e-mail and any printout.
Thank You.
**************************************************

Reply via email to